dom33dom

MrPLC Member
  • Content count

    18
  • Joined

  • Last visited

Community Reputation

0 Neutral

About dom33dom

  • Rank
    Sparky

Profile Information

  • Country France
  1. Hello, To be able to communicate with other PLC than AB you need to activate the communication driver ( for example : modbus, fins ..... ) You have to flash the PV+ firmware and you will have access to the communication driver screen. Just select the driver you want and finalize the flash. bye
  2. Hello, There is a new product with PanelView !!! PanelView Component. They are dedicated for Microlgix and SLC / PLC ( serial & ethernet possible ). There is no software to program them. you are directly connected to the PanelView with a web browser. This product start with 2" & 3" & 6" & 10" bye
  3. ControlNet Subnetwork

    Hello, No it's not possible to do this I/O configuration. Your Anybus module should be on the same ControlNet network than the 1756-CNB at adress 1 & 2. Or add another ControlLogix processor in the backplane where the 1756-CNB address 1 is located(the same network as Anybus module). And do communication between the both ControlLogix. bye.
  4. Hello, To configure ethernet port, you have 2 options : Use Rslinx with your serial DF1 driver. Browse on serial driver to reach the ethernet CompactLogix port Right click on the ethernet card and assign the ethernet IP Second one is to use the DCHP - BOOT server Connect your ethernet cable between your PC and CompactLogix The MAC ID address of the compactlogix will appear and you will be able to assign the IP address
  5. PV+600 Application

    Hello, The mer file is not link to you PaneView+ hardware. You can use it either on PanelView+ and you PC ( with Studio Station ). Launch the Station software on you PC and you will find the same launch screen as you have on your PanelView+. If the shortcut has been made for your LOCAL path, it will work on your PC without any modification. bye
  6. MCR Instruction

    You use it correctly. The MCR is designed to avoid to repeat the same conditions on each rung. Take care that you can insert another MCR in an existing one, you have to finish your MCR and start a new one.
  7. PLC 5 Channel 0 serial communication

    You can check in status file ( S:2 ) of RsLogix 5 the type of configuration of the comm port and switch.
  8. Log On to Factory Talk

    Hi, During the installation of ME, you have installed Factory Talk and normally specified User Name and Password. If you don't remember it, launch again the Fatory Talk wizard. You will be able to reset your account.
  9. Hi, You have to test your serial driver under Rslinx Configuration driver. It's not because it's working with one PLC that the serial driver will work all the time !!! You have to check the serial driver each time you want to connect on a new PLC.
  10. RSView ME

    There is a function to do this. Right click on display Add new component .... And you can add display on the your new application.
  11. RSLogix 500 Ladder Printout

    It is normal to have a page break on RsLogix 5/500 if you are using Title Page. Title Page is designed for a "Chapter" in your routine. If you want to add comment on your rung just use Rung Comment and you won't have the break page problem. Take care about the reference ( Rung number or Output ). I used to use Rung Number.
  12. The PCCC format is use by SLC & PLC/5. The Logix and Micrologix 1100 is based on CIP. Maybe a 1761-net-aic will help you but with the serial port ............
  13. Profibus Connectivity

    Hello, You can also try this : http://www.novotek.dk/products/hilscher/Datablad_RIF.pdf Bye.
  14. PID problems in SLC-5/05

    to avoid the bump, just copy your auto value in your manual value when your pid is in Auto mode.
  15. IRDA port in PV+

    Hello, For the moment, there is no possibility or developpment to use the ir port. Bye