jeffersm

MrPLC Member
  • Content count

    24
  • Joined

  • Last visited

Everything posted by jeffersm

  1. Hello I am in charge of a project to put a new solution mixing tank in service and we would like to have a report of time stamps and temperatures automatically generated and saved to a file (preferably PDF) at the end of its 2 hour cycle. This unit has RSView Studio SE HMI software Version 5.00 which is logging the the temperature and time stamp to an SQL database. Unfortunately our programmer is not familiar with writing scripts for performing this function. Does anyone have sample code using SQL querries that you could share with us? Any code samples or recommendations would be greatly appreciated.
  2. I am seeing intermittent problems with a process that is using ControlNet on a ControlLogix5000 system. The problem started happening about 1 month ago and there have been no program changes since 5 months ago. The system has the following: 1) 1756-L61 CPU 2) 1756-CNB/D Master ControlNet card 3) 1756-ENBT/A Ethernet Card (Only used for VFD, HMI and remote access) 4) 3 1794-ACN15/C FlexIO ControlNet interfaces for nodes 2, 3 and 4 on RG-6 bus We were seeing intermittent stopping of the process related to node 4. When the process stops, the technician can sometimes restart by stopping and starting the process. If that doesn't work, then he unpluggs the bus tap from node 4 and then it works. The following steps were taken to try to correct the problem: 1) replaced the FlexI/O on node 4 (just 1 high speed counter) 2) replace the 1794-ACN15/C on node 4 3) replaced the RG-6 cable (had measured high resistance from one of the cables to a tab and had another cable whose connector fell off during troubleshooting process. decided to change all as a preventive measure.) 4) replaced the 3 taps connected to the 1794-ACN15/C as corrosion was noticed on some. 5) replaced the bus/terminal block of the 1794-ACN15/C used on node 4 and the 75 ohm terminator I have checked the CPU fault history, but none were recorded. The technician mentioned that when the process stopped a watchdog timer fault message on HMI. My next step will be to get the exact wording of the fault to trace it back from the HMI to the related logic in the PLC. Last night the process stopped on all the nodes. I don't have the details yet of what happened or how it was corrected. Seems like the problem may be getting worse. Any recommendations on where to look to identify the problem? I have the RSNetworx for ControlNet installed on my computer, but I don't know if we have an interface to connect a PC for configuring ControlNet. If I swap out the 1756-CNB/D Master ControlNet card will I need to use RSNetworx for ControlNet to configure it? Was RSNetworx for ControlNet required when swapping out the 1794-ACN15/C node interface?
  3. I just requested a quote from our local AB supplier for the following: 200 ft 1786-RG6 Standard PVC CM-CL2 1 pk 1786-TNCLXT4 TNC Terminating resistor TNC plug 4 ea 1786-TCT2BD1 TNC T-tap with straight BNC drop connector 1 pk 1786-TNCL10 TNC Plug No barrels or bulkhead adapters at any point in the installation. After reading the installation manual I noticed that there is something else that is wrong. All of the cabling (120 VAC, 24VDC, and ControlNet) are run through the same 1-1/2" sanitary pipe that is about 40 feet long. The 120 VAC is used mostly for some input modules and prox switches, but also powers the vibratory bowls which draw about 5 to 10 amps each and like most bowls are run on half wave with a thyrister type current level control. The 24 VDC powers several solenoid valves. Not a good environment for the ControlNet cable. I will be requesting quotes for installing a new pipe (with generously radiused elbows) just for the ControlNet cable. This is a clean room so that complicates the installation a little. Even though I had tried testing another cable that ran outside the pipe and still got the same results, I recognize that this needs to be corrected. There might be multiple factors at play here. I think we were just lucky that it worked well for so long. On another topic:Can anyone recommend a protective cover for 15" touch screen monitors in a washdown environment? We are using AB6186M15SSTR and would like protective covering for them to prevent water from getting into them.
  4. Will I need new tooling to install the 1786-TNC? Also are there taps with TNC connectors or will I need adapters to go from the TNC to the BNCs on the taps?
  5. Thanks for the recommendation. I don't see High Flex written on it any where, but it does see more flexible than I expected although this is the first time I have worked with quad shield cable. I did notice that the center conductor is made up of very fine strands and the outer braid strands also seem fine compared with coaxial cables that I have worked with in the past. I think it is held in place with wire ties in several locations for neatness. We will have to make sure to avoid that in the future. Do you recommend the AB or any other particular brand of ControlNet cable?
  6. After running less than an hour the fault is still occurring. Our engineering group up in headquarters is recommending to switch to Ethernet IP. Based on the noise warning errors from the CNB, it seems that there is some kind of sporadic noise even though the measurements this past Saturday found nothing. Even with very little running in the plant I was still getting the fault on Saturday and Sunday. The only auxiliary equipment that I was running then were three vibratory feeding bowls. All the local motors were shutoff. I'm starting to think that a 120 VAC bowl coil could be arcing. A couple of weeks ago we started having a problem with one of them blowing its 10 Amp fuse. These bowls run continuously and are not controlled by the PLC but have their wiring running through the same cabinet as Nodes 2 to 4 are located in. I will try to check the current draw on the bowls to see if the problem one is drawing more current, check with the bowl supplier to find out how to get at the coils individually to measure them. It would be nice to have an oscilloscope now to try to capture this event. Has anyone tried the Pico Scopes or anything similar that are PC based scopes?
  7. The connections are as follows: Origional configuration when problems first started occuring: Node 1: CNet Bridge (NUT = 5 mS) Node 2: CNet adapter, 2 VHSC, 5 discrete I/O (all RPI= 5mS) Node 3: CNet adapter, 2 VHSC (all RPI= 5mS) Node 1: CNet adapter(RPI= 20mS) , 1 VHSC (RPI= 5mS) I tried the following configuration since the above seemed odd : Node 1: CNet Bridge (NUT = 5 mS) Node 2: CNet adapter, 2 VHSC, 5 discrete I/O (all RPI= 5mS) Node 3: CNet adapter, 2 VHSC (all RPI= 5mS) Node 1: CNet adapter, 1 VHSC (all RPI= 5mS) (band width usage was about 20%) The Rockwell Field engineer changed the speeds to the following on Saturday, April 16: Node 1: CNet Bridge (NUT = 3 mS) Node 2: CNet adapter, 2 VHSC, 5 discrete I/O (all RPI= 5mS) Node 3: CNet adapter, 2 VHSC (all RPI= 5mS) Node 1: CNet adapter, 1 VHSC (all RPI= 3mS) (band width usage was about 37%): Today we had 2 Rockwell Field engineer troubleshooting and they found that the bridge CPU utilization was at 95% to 100% so we rescheduled to: Node 1: CNet Bridge (NUT = 5 mS) Node 2: CNet adapter, 2 VHSC, 5 discrete I/O (all RPI= 5mS) Node 3: CNet adapter, 2 VHSC (all RPI= 20mS) Node 1: CNet adapter, 1 VHSC (all RPI= 20mS) Now the bridge CPU utilization is at 52% (band width usage was about 10%) Timing is very critical in this application as to the relationship between opening and closing a valve to inject a precise amout of solution into IV bags at 10 independat stations, but the VHSC controls those vales directly and measures the volume by counting turbine pulses. This is done independant of the network, I don't think there is a problem with increasing the RPI for precision. I just have to make sure that the production capacity is not affected by this change. (see attached before and after bridge cpu utilization) We also observed that although the noise measurements said everthing was OK, whaen a fault occured, the network complained about noise. (See attached)
  8. A Rockwell Field Service Engineer was here this past Saturday. He checked the signals on the Control Net and found them to be normal. He inspected the connections of the cabling and saw some problems with the way they were installed and replaced all the connectors. Also in the process of replacing them, he noticed that there was some oxidation on the center conductors of some of the cables, but didn’t think that it would cause a problem especially since the signals look good. We will be replacing them all just to make sure. Also he had said the replacements must be AB or Belden ControlNet cable. What is currently installed is another brand of RG6 quadshield that is labeled as ControlNet cable. The cable that I had tried as areplacement when we first started seeing this problem was regular RG6 which didn't solve the problems we were seeing, so I switched back to using the origionally installed ControlNet cabling after repairing one of the cable ends. Next he upgraded the firmware of the ControlNet bridge from 10.7 to 11.4. Also when he checked the AB firmware compatibility table he found that the firmware of the 1794-ACN15/C node adapters which were at 5.1, 5.2 and 5.2 were not compatible with the firmware in the PLC CPU which is 16.7. He downgraded all of them to 4.3. We cycled the system for about 30 to 40 minutes and we got a fault on node 4 which is the origional problem. Next he change the network schedule from 5 mS to 3 mS and the problem node interface and high speed counter also to 3 mS. Prior to that, everything was at 5 mS. We cycled the machine for about 1.5 to 2 hours and we got a fault. (I can’t say for sure if the problem is better as the amount of time between faults has always been highly variable.) I notice that all the status lights were green after a fault, but in the ladder logic that is checking the status word of the 1794-ACN15/C node adapters a 255 is being recorded and the fault counter incremented. Today I did some additional cycling of the machine and again it faulted after about 1.5 to 2 hours. This time I saved the program when the fault occurred to save the tag values. Also I checked the 1794-ACN15/C node adapters and high speed counter properties after the fault occurred. The node adapter says: it has a minor fault that was recoverable, and that there was a mismatch. I went and changed the version in RSLogix from 10.7 to 11.4 to match the new firmware. The High speed counter listed an “Unexpected Module” fault. This may be related to the problem, but I don’t know what it means. Attached are the screen captures of what I saw today. Any recommendations on what we should try next?
  9. Origionally it was set to Compatible Keying, but I received a recommendation to change it to Disable Keying to try to avoid the fault. Changing the keying did not prevent further faulting. I will put it back to the origional setting this weekend.
  10. Hi dmargineau, Sorry for taking so long to get back to you. Attached are some RSLogix screen shots of what I see related to the mismatch: In the general tab of the 1794-ACN properties, the revision is listed as 3.1 and I can only change the minor (.1) and not the major number. In the module info tab of the 1794-ACN properties, the revision is listed as 5.2 and also says mismatch.
  11. I do have version 16.03 of RXLogix installed on the PC and that is what starts up when I load the software for this PLC. I just meant that I have upto version 17.01 on the same PC.
  12. Correction: The project running on the CPU is V16.03.00 (CPR 9) The RSLogix installed on my PC is V17.01.00 (CPR 9 SR 1)
  13. Hi dmargineau, The RSLogix is V16.03.00 (CPR 9) The CPU is a 1756-L61 with revision 16.7 The RSNetworx for ControlNet is 9.00.00 (CPR 9) Flashing the CNet bridge didn't correct the problem
  14. Hi Shiner, That sounds like a great idea. We have a lot of places where we could use them. Where can I find them and how are they called. I have seen many coolers, but never driers. How do you seal the wireway or conduit entrances to create a positive pressure?
  15. Thanks dmargineau, I tried your recommendation but in reverse. I switched the trouble node flex io adapter with its neighboring node which has been trouble free. I went to the site you recommended, but din't find a ver 5.2 which is what one of the nodes is and the other 2 are 5.1. I was able to download the 5.1 though. I then used the EDS wizard with the find an download option and update the EDSs. Checked that all said they were updated with 5.1 file. Then updated EDS on all flex io. The mismatch I am seeing is actually in all the flex io adapters and is only reported in RSLogix. RSNetworx does not report any problems except when I run diagnostics. It complains about a minor watch dog fault in the cpu execution. The problem continued after this change. I just changed the CNet bridge from one with ver 5.001 FW to 10.007 FW and reoptimized. I will wait and see if it gives better results.
  16. Hi all. Today when I saw the problem happen again I noticed that the status light on the last 1794-ACN15/C in the chain had changed from green to red. I was able to reset it by disconnecting the tap. Our expert in headquarters is recommending to reflash the firmware of the ControlNet card. When I check the properties of the various interfaces, this is what I see: According to the report that RSNetworx produces, the revisions are: Node 1(1756-CNB/D): 5.038 Node 2(1794-ACN15/C): 5.001 Node 3(1794-ACN15/C): 5.002 Node 4(1794-ACN15/C): 5.001 According to RSLogix the revisions are: Node 1(1756-CNB/D): 5.38 Node 2(1794-ACN15/C): 5.1 Node 3(1794-ACN15/C): 5.2 Node 4(1794-ACN15/C): 5.1 According to RSLogix the versions are: Node 1(1756-CNB/D): 5.1 Node 2(1794-ACN15/C): 3.1 Node 3(1794-ACN15/C): 3.1 Node 4(1794-ACN15/C): 4.1 Also in the device properties module in the module identity field, all of the 1794-ACN15/C are listed as mismatch. Checking with the area Technicians, this node has always been problematic for years, not just the month or so that I thought it was. Lately it seems to be worse though. Any recommendations?
  17. We have many installation with Iconics Genesis 32 versions 8 to 10 and have the problem that it becomes unresponsive or looses communication with PLC. When this happens the operators will perform a hard reset to reboot windows since their security level doesn't give them access to the start menu to perform a soft restart start. Our development expert in headquarters is telling us that that the unresponsiveness and loss of communication is probably due insufficient number of tags and that we need to upgrade the licenses to solve the problem. I don't have enough of the details behind his reasoning to be able to judge if it makes sense or not. One thing that I have noticed is that in the PLC ladder logic were the HMI tags are updated, there are no conditionals to perform the writes only if the tag value in the PLC is changed. This means that all tags look like they are written to the HMI on each PLC scan. Could this be overloading the HMI? Also is there a way to add a button to Iconics that will restart the HMI application or windows?
  18. You are right daba. The root cause of the problems is the wetness in the control cabinet. That is what lead to modules being changed, wiring being handled and corrosion issues. This cabinet is in an area that receives daily wash downs and the cabinet seals are deficient. I am in the process of upgrading the seals to prevent water intrusion during the washdown process.
  19. I re-compressed all of the BNC connectors and in the process found a loose power connection to the Node 3 ControlNet interface. Later I reconfigured the Node 4 ControlNet interface. That was the one that was most recently replaced. I saw that the network update time for that unit was set to 20 mS and all the other nodes were 5mS yet all nodes basically perform the same functions. Also the high speed counter that was on that node was set to 5 mS. It didn't make sense to me that an I/O would be configured for a faster rate than the node interface it was connected to. Now everything is set to 5 mS. The node interface that was recently installed was version 4.1, while the other 2 were 3.1. Probably they were alll origionally 3.1
  20. I reconfigured the ControlNet chain about 2 hours ago and so far so good. Although sometimes things would be fine for about 8 hours or so. The configuration was was easier to perform than I expected. Also I replaced a BNC connector that on of the technicians found to be loose. I am using compression type connectors as I saw that they were recommended for humid areas and this area has gotten wet at times although we are working to prevent that. I will be recompessing the rest of the connections as I found that the instrucions that came with the compression tool don't yield the best results. Attached are some screen shots of how the configuration was when first starting out. This was the first time that I ran RSNetWorx. It came as part of RSLogix5000 Standard and the RSNetWorx portion is not activated. Is this supposed to activate with RSLogix or do I need to purchase a separtae activation for that? Do you know how the taps on the ControlNet work? They remind me somewhat of the AUIs that were used with Thick Ethernet. Can they be replaced with Tees (75 ohm version) like was used in Thin Ethernet?
  21. Thanks dmargineau and Steve G. I will try your recommendations.
  22. Series One JR to Logicmaster

    I have a Siemens TI315 which is the same as the Series 1 JR. We want to be able to pull out the program in ladder logic to facilitate support and upgrading to another PLC. We recently purchased the DCU from Automation Direct (the RS-232 version). When I contacted Qualitrol to purchase Logicmaster 1JR they told me they no longer have the IC610CMM100 which is the correct DCU for this and the basic Series One. I didn't realize that this CPU required a different DCU. I thought that I had used this same DCU with the original Series One once and that it had worked, just that I couldn't do on line monitoring. Does any one know if the Automation Direct DCU will work with the Series One JR? Also If I got Logicmaster 1F, can that be made to work with it also?
  23. Series One JR to Logicmaster

    Thanks for the recommendation. Since I already have the DCU I might as well get the Logicmaster Software. Qualitrol sells the L1F for $100 and I expect the L1JR will be the same price. I have already started to copy the program out from the handheld programmer, although its longer than what I realized as I already have 3 pages in long hand and looks like I am 2/3 done. Our validation department had been after us to supply them with a software back up. We were able to make one using the handheld and the built in Windows sound recorder on a laptop. The verify operation checked OK. Surprisingly it worked the first time. The validation engineer was a bit surprised when he put the CD into his computer to copy the file to the server and heard modem type tones. The only difficulty we had in the process was that the key for the handheld programmer switch was lost so we had to use a paper clip and screw driver to get to the load position and back. Do you have a key that you could scan and then upload image file so we can cut a new one?
  24. Does any one know where I might be able to find sample energy management code for Cimplicity HMI. In my facility we have extra licenses for HMI and some under used Genius PowerTraks (Genius bus modules for power monitoring) and Multilin PQMs (Power Quality Meters). With the way that enery prices have been climbing lately, this would be a great project for us to implement at a realively low cost since we already have most of the hardware and development software. All we need is a jump start on the applications.