
Simo99
MrPLC Member-
Content count
48 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by Simo99
-
In fact, the problem was nothing more than the previous one, because after changing the words from unsigned to signed (they were already this way before) the program started working again.
-
Hi guys, I have a problem in a FB of GX Works 3, I am trying to do a subtraction of two variables that have Double Words Signed as type. These two variables increment, the second variable is lower than the first, but the result is always high and this is strange. So there is an error I have not understood, who can help me?
-
I solved the problem, thanks a lot
-
I did the test but the values are negative. The values became negative after the correction of the FB call. I don't know how this is possible
-
I'm trying to explain myself better, I'm using a function called "D-" in an FB, the first value of the subtraction should be 500 larger than the second one, because these numbers are the results of two operations in a Program and they always increase depending on the number of times they enter certain ifs. The variables I am using are labels, specifically the first number is an input variable, the second number is an IN/OUT variable and the result is an internal variable.
-
Thank you very much. I have solved something, but not everything because the subtraction is still wrong. Do you have any other advice please?
-
Hi AndreasW, I am using the "D-" instruction and the results are wrong. I have not found the "DSUB" instruction on GX Works 3, where can I find it? The second value must be less than 500. To get closer to solving the problem by doing this test, should I put "Carry" in parallel with subtraction? How can I select DWord within the monitoring window? Many thanks in andvance
-
Hi experts, i have a problem, i did the upload of my software with GT Desinger 3 on the GOT, but i don't see the PLC variables because my other software did with GX Works3 isn't linked with the uploading. Is there a way to connect both softwares to the uploading withouth a PLC?
-
Why can't i click on it? Can't put the numerical input keyboard in the middle of the base screen/ the window screen?
-
Hi everyone, is there a way to put the numerical input keyboard in a specific position when i click on the numerical input? Thanks a lot.
-
Good morning experts, how can i move a rectangle/JPEG from back layer to front layer? Because if i copy and paste the rectangle from back layer to front layer, the rectangle is invisible
-
Good morning experts, is there any way to create two different Alarm display (System)? So, one with collection mode historical and one with only current alarm? Many thanks in advance
-
Good morning Thiago, thank you very much. No, I have enabled "Use System Alarm" on "System Alarm Observation", I am in the situation of the image attached to this message. Let me explain the problem better. I would like to use the System Alarm Display for only the current alarms and the Alarm Display (System) for the historical, but when I am in run time, I see the same alarms in both the System Alarm Display and the Alarm Display (System) as in the attached image. For example, in the Alarm Display (System) shouldn't I see all of the system alarm history? And the last thing, what does mean this alarm? "G00-307 Monitor Devices are not set"
-
Thank you very much Thiago, you have been very very kind. Thank you very much indeed! I just have one question, I have a GT25**-V type (640x480), so would that mean that even though I have the "System Alarm Display" object in my program, when I load it on my GOT, my current system alarms will not be displayed?
-
Hi Experts, In GT Designer 3 would there be a progressive number of the active window screen? For example, if I am in the window screen 5, the program retrieves in a variable the value 5. Many thanks in advance.
-
Progressive number of the active window screen with GT Designer
Simo99 replied to Simo99's topic in Mitsubishi
Thanks a lot -
Yes, I need the history and only current alarm split into two Alarm Display (System). Is it possible? Thanks a lot, really!
-
Good morning experts, i have a little problem with a Alarm display (user) and i hope with your huge experience you will may help me. Thank you very much in advance Let me explain best. I would like use a slider to control a Alarm display (user), i tried to do it, but the slider doesn't scroll up/ scroll down like i will want. It doesn't scrolling through the pages and it heighlights just some alarm. Could you give me a bit advice, please?
- 1 reply
-
- gt designer 3
- alarm display (user)
-
(and 1 more)
Tagged with:
-
Hi, I have three questions on GT Designer3: 1) Is there a way to exit the simulation by pressing a switch? 2) Do the SP functions "Screen Cleaning" and "Touch panel calibration" only work when the software is loaded on the GOT? 3) The SP functions mentioned above, can only be enabled from the main utility menu?
-
And once time i will do that, will i by-passed this problem @Gambit?
-
Hi everyone, I tried to make a script, but it doesn't work. Let me explain better, I would like to click a button, login and after I enter the correct password I would like to call a window screen or have the same button do other things. Is this possible?
-
Thanks a lot How can i setup a super user and create the accounts?
-
How can I program it with the PLC @JRoss?
-
I don't know what this is. I mean I don't know how I can set the diagnostic function if I want to display it on the GOT as a table like in Tia Portal and see it during the simulation @Gambit May you help me, please?
-
Level Actually i would like use the operator level, but i don't know how can i set the operator name...