sathaporn

MrPLC Member
  • Content count

    10
  • Joined

  • Last visited

Community Reputation

0 Neutral

About sathaporn

  • Rank
    Sparky

Contact Methods

  • ICQ 0
  1. HVAC algorithm

    hello sir i just had finished my project drying paper about 50 loops . I used lcb01 ( 50 loopS) and use software process tool . In process tool, It very easy for do pid loop that seem like you work on DCS . It have more funtion box example pid , spit range , motorise control valve .If you need mornitor system on scada , it can created face plate on tiuch screen or many point on scada . After i finished this project , I start new project about 150 loops , It is stockpreration of pulp and paper .I change lcb01 to lcb05 ( 500 loops) and control by cx-supervisor v2.1 . In cx-programer you will see problem about pid fb. It cannot working complete during change mode from manual to auto and very hard for auto tune. I suggest you chane to lcb 01 and cx-process tool. you will happy. sathaporn srisawat
  2. Labview & Omron PLC

    my understand with your question are , you need to use labview write and read data from omron plc. ok if it correct, now labview is hmi and plc is hardware .what is communition between lapview with plc. in labview v8.5 , it have function opc client that can read and write data from opc server . now i use kepware for opc server and config kepware commu to plc by fin ethernet . it work ok stable and high espeed. result if you need used labview for read and write data any plc then you need to use opc server
  3. Ethernet with CS1-H and CX-Supervisor

    1.first time ,you have to connectd plc by serial cable. 2.goto io table and creat it for plc can see any module 3.in io table go to etn module and click setup 4.at IP address you set 192.168.1. ... ( up to no.of module) 5.subnet set 255.255.255.0 6.select tap tranfer to pc if anything ok software ask for starting module click ok 7.at module you will see lamp run lid , don't show lamp red 8.in io table you need to setup routing network 9.you can see tool menu starting routing and setting click ! 10.softwear will show window for set routing network , you select no.1 and double click , and select insert siou 11.window will show module no.1 and link line with network#1 12.select tap tranfer it to plc , now any think ok lamp run ,100m,link is lid 13.at cx-programmer select connection ethernet and click setting 14. at network goto fin destination and set network(=1) and node(=up your setting module) 15. select tap driver set IP address 192.168.1... ( 2 set last no.up to your setting module) 16 finish your setting in cx-programer test it note 1. IP adress on pc not the same plc example in plc 192.168.1.10 in pc need to 192.168.1.8 ,,, subnet is the same 255.255.255.0 2. cable rj45 you need to used cross type
  4. CX-SUPERVISOR with Allen-Bradley Plc

    I 'm not sure my suggestion but i had tested other plc , it ok. 1. you would to have opc server of ab.plc 2. if you have not opc server ab , can use kepware opc server( you can find it on internet and crack) 3.run opc server ab or kepware after run kepware you can add chanel and device ( during select chanal and device you have to set type and comm of plc. 4. after you select chanel and device successful , you can add new item wheen you click add item , you can see method config point example io area , memory area. 5.back to cx-supervisor , you can add point for ab plc by select dde or opc other. 6. after you click select opc comm. from item list you will see kepware opc server or ab.opc server 7. you need to set name group and item , that the same name on opc server 8.I test my method by used cx-supervisor with unitronic plc , siemens s5 and omron . It can work very well .No problem good luck for you sathaporn from thailand
  5. pid mode auto-manual not complete

    I had used fb-pid for control my process ( pulp & paper) for replace to used lcb-05 because i have loop control about 20 loops ( lcb-05 can use 500 loop).I see problem about fb-pid . It have not bumpless during I change mode manual to auto .Output of PID will swing about 2-3 minute because mv value don't start from mv manual although I will set sp-value equal pv-value . This problem don't appear when i used fb-pid of cx-process tool because it have function bumpless . I try to solve this problem but it is not success. please help me this problem thanks you anyone sathaporn srisawat from thailand
  6. I try to used cx-supervisor for read-write data from plc unitronic by Unitronic OPC server .But i cannot read or write data , i think that i set group,item,path not correct.I see status at opc server , it show that " have new client connect ". When i run cx-supervisor , it show that " fail add item to plc " .If someone have experience about had used cx-supervisor read-write data other plc ( not omron) by OPC server , please advice me. thanks you anyone sathaporn srisawat from thailand
  7. CS1W-ETN21 & Internet ?

    step to connect laptop to plc by ethernet 1. set rotary switch front side of card , upper rotary switch for unit number set 1 ..10 up to you , lower rotary swith have 2 switch ( hex.nuber) set 0,A = 10 for node number result etn21 have unit no.= 1 node number = 10 2. install cs1-etn21 at cpu rack 3. on power 4. now you need to connect to cpu by port rs232 for configu network before used ethernet 5. start cx.programer and set cpu the same hardware , on line cpu 6. go to io table and start create io setup 7. after create already , check detail of cs1w-etn21 about port number and node number now ,it would be port=1 ,node =10 8. if you use cx.programer v6.11 or later promt on ent21 and click right select unit setup 9. program will show dialog first colume you set ip.address and subnet , you can follow my example IP.ADRESS 192.168.1.10 ( 10=node number) SUBNET 255.255.255.0 10. after you set ip.adress and subnet already .under dialog have small menu ,you select tranfer pc to cpu and click tranfer 11. program will tranfer configer to cpu and ask you for restart etn21 note. if anything ok. lamp on module etn21 will show green lamp run,lan, 12. exit io.table to mainpage 13. select menu tool and select network setting 14. select routing and select port no.1 the same like port setting module etn21 click insert siu.. 15. right window will show port 1 link to network no.1 16.the same like step11 ,if anything ok. yellow lamp will flash at rd. 17.step for config lan in your laptop 18. select my network click property and select lan network property 19. select tcp/ip and click for config ip.adress& subnet 20. set ip.adress & subnet , 192.168.1.9 ( last number not same ip.adress of etn21) , 255.255.255.0 21.exit my network go to cx.programmer 22. change connecting of your cpu to ethernet 23. after you select ethernet and click setting , program will show dialog network and driver 24. in window network you select fins destination and set network =1 , node=10 25. in window driver, you checkmark at auto-detct , and set ip.adress 192.168.1.10 is the same ip.adress of etn21 26. exit setting and start online i hope that you will goodluck sathaporn srisawat from thailand
  8. MAD42 analog module

    Dear friends my suggestion to you .for analog output module after you set anything attach manual.It'not to used it . Ok if you set address of analog output module = 2110 and your module are AD008C.It means ,you can use address for 4-20 madc output 2111 -2118.You need to set address 2110=ff by write command mov #ff to 2110 . After you write this command already . You can measure output terminal form 3.2 madc >> 3.9 madc surely.I ever do my project with scada and see this same problem. Goog luck my friends sathaporn ( thailand)
  9. cx-supervisor control pid loop in LCB-01

    Good Spaky thank you for your suggestion. Today in thailand is holiday I don't go to factory .In saturday I will go to factory and test your suggestion.And I will tell the result on sunday. sathaporn srisawat
  10. Dear all Now I am going to write program for controlling dryer section ( paper machine). My hardware are cpu cs1h-h ( cpu63) , lcb01 ,hmi cx-supervisor v1.0 . I have problem about can't control basic pid on LCB01 form my conputor. I write program cx-processtool v.6.1 and complite any item in basic pid to csv.file. I can see its in cx-programer by use em-tranfer block to reg.memory cpu .I cannot change mode pid loop example auto/manual or remote/local .I can set gain,integal or bias from cx-programer . Please help me about how to change mode pid loop in cx-process tool for cx-programer or cx-supervisor . tank you sathapon srisawat