Allen Bradley
Bulletin 1882
copyright 1982
WARNING: A PC system should not be
operated without a hard-wired Master Con-
trol Relay and Emergency Stop Switches to
provide emergency I/O power shut down.
Emergency Stops can br moni-
tored but should NOT be controlled by the
User Program. These devices should be
wired as describe in tle PLC-2/20 As-
sembly and Instruction Manual (Publica-
tion 1772-801).
This is direct quote from manual page 7-1
CAPITALS and all
Being said it was ignored for years.
One of my fathers quotes:
If carpenters build houses the way some programmers wrote programs,
the first woodpecker that came along, would destroy civilization as we know it
QUOTE(TWControls @ May 20 2006, 03:33 PM) [snapback]34238[/snapback]
Been Around pretty much covered everything. Great job.
Just to add a few things.
QUOTE
e-stops will still stop or shut everything down dead in its tracks
If the PLC works perfectly and the programmer writes a perfect program this would be close to true. Flaws can pop up in the chip sets that are in the PLCs. It is possible however highly unlikely that a PLC could have a flaw that would compromise the Estop circuit. Some PLCs have relay outputs, what if a relay was to stick closed? This is not unusual.
The following is straight out of the RsLogix5000 Help
QUOTE
The MCR instruction is not a substitute for a hard-wired master control relay that provides emergency-stop capability. You should still install a hard-wired master control relay to provide emergency I/O power shutdown.
I really with they would just take the MCR instruction out of the software. I guess it is kept for compatibility with older processors that are replaced. The only place I hear of it used now is by instructors in classes
I wish I could type as good as I reed!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!1