technogumbo
Mar 10 2005, 08:24 PM
I am needing to modify the operator interface program on an Allen-Bradley PanelView 1000 that talks DH+ to a PLC-5/25. The operators need some additional features. I can easily upload the program out of the PanelView through out DH+ network. However, when I go to download the modified program, PanelBuilder32 stalls and gives an "Error 1030 - No commands received from operator terminal" fault.
I tried uploading the existing program and then re-downloading the same program, but have the same fault error come back. I remember with the older PanelView 1200's that you had to turn a key switch to enable the download and upload. I could find no tech notes or knowledgebase articles on AB's website to point me in the right direction.
HalBishop
Mar 10 2005, 11:27 PM
There is no keyswitch on the PV1000.
This is from the Rockwell Knowledgebase:
Problem:
Error 1030 - No Commands Received From Operator Terminal
Explanation:
This error can occur during a DH+ to DF1 passthru (PC - DH+ - SLC 5/04 - DF1 - PV) if the PV is not set to the default node of 1. Since PV is point-to-point only, it serves no purpose to ever change the default DF1 node on the PV. However, the software will ALLOW this change if 'USE NETWORKING' is checked in the communications settings in PB32. Unfortunately, once you change the node to something other than 1, passthru downloads cease working. Often times, the upload functionality will still be working, making it seem like everything is ok.
Resolution:
Change the node number on the PV to node 1 (and then remove the check from the 'USE NETWORKING' checkbox). The passthru download should then complete normally.
and:
The customer was running a software package from Trend Micro
called PC Cillin which prevented PanelBuilder32 from dowloading
to the DH485 Panelview terminal via the SLC5/05 Ethernet
controller.
The firewall protection software must be disable from within
PC Cillin before the download can proceed.
Ensure the following bits are set correctly on the SLC5/05 - Status File,
Chan 1 tab:
DH485 Gateway Disable Bit S:34/0 = 0
DF1 Gateway Enable Bit S:34/5 = 0
and:
This tech note attempts to qualify all passthru download combinations for PanelBuilder ND3 and END1.
See also the passthru tables in the PB32 online help under contents, transferring applications, for the latest combinations.
IMPORTANT:
Passthru has occasionally been seen to crash/fault and/or clear memory on some processors (5/40,5/60,5/80) during the passthru operation. Make sure the PLC has not maxed out resources or block transfers. Make sure that the block transfer queue in the PLC is not full and that any BTs are not erring out. Keep all block transfers in the PLC as non-continuous if possible to minimize resource timeouts. Passthru only during non-peak times. With the PV1200/1000e/1200e/1400e, use the Inhibit, Request and Status bits in the PanelView to regulate the passthru operation for downloading; they do not apply to uploading. (the Standard PV's do not have these control bits).
Upload/Download Summary:
ND3 2.60 w/ RSlinx 2.0 and PB32 3.61 w/ RSLinx 2.20.02 (now PB32 3.70 as of June 2001):
Remember to "configure client application" for the driver in RSlinx with PB 2.60!
SLC 5/04
DF1 channel 0 to RIO YES
DH+ channel 1 to RIO YES
DF1 channel 0 to DH+ NO (YES if PB32 and PV f/w 3.30 and RSLinx DF1 set to KE/KF2 and bits S34/0 and 5 set to 1)
DH+ channel 1 to chan 0 YES DH485 or DF1
Anything to 1747SDN NO
SLC 5/03
DF1 channel 0 to RIO YES, ND3 2.60 Jan 99 will support this. Requires 5/03 OS302.
DH485 channel 1 to RIO YES
DF1 channel 0 to DH485 NO
DH485 chan 1 to chan 0 NO SLC does not support Chan 1 to Chan 0 bridging
DF1 1747KE to DH485 YES
DF1 1770KF3 to DH485 YES
Anything to 1747SDN NO
PLC5
DF1 channel 0 to RIO YES, internal DF1 failed with "cannot guarantee delivery, link layer timed out or rec'd a NAK".
DF1 channel 0 to DH+ NO, not supported by PLC
DH+ to RIO YES
PLC5C
DF1 to Cnet NO
DF1 to RIO YES
Cnet to RIO YES
Cnet to DH+ NO
PLC5E
DF1 to Enet NO
DF1 to RIO YES
Enet to RIO YES PB32
Enet to DH+ NO
Anything to 1771SDN NO
Direct
DF1 1785KE to DH+ YES
DF1 1770KF2 to DH+ YES
DF1 1747KE to DH485 YES
DF1 1770KF3 to DH485 YES
PIC to DH485 YES
PCMK DH485 to PV YES
KTX DH485 to AIC to PV YES
1785KA5 DH485 to DH+ YES
KT/KTX to DH+ direct YES
KT/KTX DH+ to 1785KA5 to DH485 YES, PB 2.60; NO PB32 upload, but not download, error 1030
DH+ to KA to DH to KA to DH+ YES
PCMK DH+ to 5/04 to chan 0 YES
PCC to Cnet YES PB32
KFC to Cnet NO KFC does not support Cnet 1.5
KTCX15 to Cnet YES
PCD/KFD to Dnet YES PB32
DF1 to SLC CH0 to SDN NO
Enet direct to PLC/SLC YES PB32
ANY RSlinx Gateway NO (cannot download via RSlinx gateway, but upload works)
May get "Error [1030] : No commands received from operator terminal" when downloading.
This includes ETH to DH+ or DH+ to DH+
SLC 5/05
DF1 channel 0 to RIO YES
Ethernet channel 1 to RIO NO (YES w/ PB32)
DF1 channel 0 to Ethernet ?
Ethernet chan 1 to chan 0 NO (YES w/ PB32)
Anything to 1747SDN NO
ControlLogix
DF1 to Anything: YES to CNB, ENET and DNB
ENET or CNB to DNET: YES, except DNB to DNB
ENET to CNET: YES, except CNB to CNB
CNB or ENET to DH+: YES, download requires PB32 3.61, RSlinx 2.20.01 (SP1), ENET/A 1.18, DHRIO 2.17, DH+ PV 4.10 f/w. See KB 12810. Must also populate all link ID's.
RSLinx 2.20.01 added support for configuring the DHRIO routing table and assigning link id's. This was needed to support the unsolicited reads from the PV terminal.
Anything to RIO: YES, except DF1
Anything to DF1: NO, L1/L2 does not support serial port passthru
CNB to ENET ?
ENET to ENET ?
END1 4.0, RSLinx 2.0 or END1 5.13, RSLinx 2.1:
Now at END1 5.15, RSLinx 2.20.02 as of 2001.
Note: on channel 0 downloads, RSlinx DF1 must be set to KF2, NOT SLC or PLC CH0
Do not do a superwho with the DF1 set to KF2 when connected to Channel 0 of a PLC/SLC, it will show multiple duplicate devices on the who.
Just do the download, then change it back to PLC CH0 for the programming software.
NOTE: DF1 is using Serial driver in PBe, not RSlinx DF1 driver. Must remove the DF1 driver in RSlinx to prevent a conflict.
To use DF1 driver in RSlinx, it must be setup as a KF2, then in PBe, use 'network' and 'AB_DF1' selection.
SLC 5/04
DH+ to RIO YES
DF1 channel 0 to RIO NO
DF1 channel 0 to DH+ NO ; Error 4209 Host PC failed to communicate with the PanelView Terminal RDM 0x5
SLC 5/03, OS302
DF1 channel 0 to RIO NO
PLC5
DF1 channel 0 to RIO YES, internal DF1 also worked
DF1 channel 0 to DH+ NO, not supported by PLC
DH+ to RIO YES
PLC5C
DF1 to Cnet NO
DF1 to RIO YES
Cnet to RIO YES
Cnet to DH+ NO
PLC5E
DF1 to Enet NO not applicable
DF1 to RIO YES
Enet to RIO YES
Enet to DH+ NO
Direct
DF1 1785KE to DH+ YES
KT/KTX DH+ direct YES
DF1 1770KF2 to DH+ YES
DH+ to KA to DH to KA to DH+ YES
PCMK to DH+ YES
PCC to Cnet YES
SLC 5/05
DF1 channel 0 to RIO YES
Ethernet channel 1 to RIO NO
DF1 channel 0 to Ethernet NO
PLC 5/250 or Pyramid Integrator
DH+ to DH+ YES (with PI link ID) (pub 2711E-6.16, pg A-3)
DH+ to RIO ?
Enet to DH+ NO
Enet to RIO NO
ControlLogix
DF1 to Anything: NO
Anything to CNET: YES, Transfer Manual shows DH+ to CNET, page 2-11.
Anything to DH+: NO The PVe xfer utility does not support the DHRIO routing.
This includes ENET to DH+, CNET to DH+ or DH+ to DH+.
Anything to RIO: YES, except DH+ or ENET to RIO
NOTE: The PVe does not support runtime routing via the DHRIO module to other DH+ networks.
See the PB1400e Transfer Utility Manual, 2711E-6.16, for various downloading examples. Download from www.ab.com/manuals under EOI.
****************************************
MODEM DOWNLOAD ISSUES
Most any download using the RSLinx DF1 driver can use modems.
There is no need to attempt this with Interchange, we can now use RSlinx for both ND3 and END1 software.
There is information on this error on the Rockwell Automation website. I found these and did not have to login to my account.
It seem s that you may be losing communications to your panelview during the down load. Make sure there is no too much traffic on you DH+.
You can always upload and download using the serial port on the panelview. This is the easiest way to ensure that the application is downloaded. Just hook up your serial cable, configure your driver and you are golden.
Good luck.