QUOTE (macflight @ Nov 7 2009, 03:38 AM)

Hi,
Check your PC Adapter speed, if it is 187.5, you cannot transfer your HMI project if the OP is on 1.5
Check as well the address of the OP and parameter 'only master on the bus'
Good luck.
he he that would be funny, I would also say that if you do have the correct interfacing hardware test it on something else.
there is always the option to change the "tranfer settings" on the OP to be at 187.5 etc for the download.
From memory.
Start the HMI (cycle power).
select control panel
go to transfer
config it to be the correct comms settings.
Thens it it in transfer setings.
Also double check the Dipswitches at the back are correct.
Check you can see it in diagnostics on the Set PG-PC interface application.
The transfer.
If you need another interface or cable please check out this site:-
www.plccables.com.au
Best Regards
David Askew
www.fast-automation.com