QUOTE (DavisIMI @ Aug 29 2009, 01:13 PM)

I had the PIC driver disabled before I configured the DF1 driver so there was no conflict in RSLinx and I had the no handshaking option changed to Full Duplex. I still couldn't connect. This went on for over an hour, I'm sure I had all the parameters the same in the channel configurations but I could have missed something. I just don't see how I can connect easily at plant #1 and have the same settings at #2 and not be able to get on line with the processor.
The PIC driver can still be a problem, delete it.
What happens when you click on autoconfigure?
Another thing you can try is delete the Harmony files. See procedure below. Delete all drivers in RSLinx first. After deleting them Rslinx will recreate them next time it starts.
To Delete Harmony Files
--------------------------------
1. Close all software including Rslinx Classic. If Rslinx is "running as a service" disable it ( to disable Rslinx from
"running as a service" refer to answer ID 31054 ).
2. Then, go to Windows Explorer and , refer to the computer's hard drive ( for example C drive) where Rslinx Classic
is installed.
3. Next, click on the + sign next to the Program files folder, click on + sign next the Rockwell software folder and,
then, double click on the RSCOMMON folder. In the RSCOMMON folder two Harmony files ( Harmony.hrc
and, Harmony .rsh ) should be displayed. One of the Harmony file may be displayed as Harmony this is okay.
4. Delete each Harmony file ( Harmony.hrc, Harmony.rsh or Harmony) individually and, then re-open Rslinx Classic.
DO NOT Delete HRMYUI.DLL