Full Version: ioscanner loss of communication
Forums.MrPLC.com > PLCs and Supporting Devices > Modicon
jagg
have setup ioscanner between 2 plc's with noe cards for communication.
have had problem with 1 of the bits not being updated it seems to me, this is a bit that should stay on all the time as a
permissive for system to run. the others are on only when required by system when running
ei: home position or extend position .....
now on thhe unity installed plc under the communications tab under noe i have setup the transfer of info to other plc.
the one thing iam looking at is this has a "device control block" i have not set this up as i dont think this is needed ? maybe iam way off here
any ideas?
maybe i missed something quite basic and general to the setup of the ioscanner.
the original setup using hardwire between the plc's works fine but when i switch to ioscanner and disable the hardwire setup is when i see the problem.
thanks for any help
Crossbow
IO Scanner function is typically for remote I/O devices, like Momentum I/O blocks with Ethernet comm adapters, you should use the Modbus read/write commands in the PLC to communicate between two processors. At least that's how it was 8 years ago when i last touched a Modicon PLC.
aggattapauer
QUOTE
I/O scanning is a service exactly the same of read/write commands. There's no difference except for the function code 23 used to read and write at the same time.
You could use I/O scanning service anytime you need to communicate with any modbus devices (not only with very OLD momentum).
First, are you talking about Quantum or M340? Untiy or previous PLCs?
Second, could you post exactly your configuration?
the control block is not necessary, you're right.
jagg
hello thanks for the replys
yea i have quantum setup
the 651 50 has unity v4 and the other quantum setup is with proworx32 model ummm i forget it but is 1 of the older ones a 234 think.
the setup isis using 2 noe cards 77101 these are setup in its own run of network cable
now i have setup the discreets in proworx to a 4xxxx reg. this is to be read by the unity setup
now the variables in unity have been declared and used with a "bit to word" then a "word to int" blocks which is to be read by the proworx setup.
have setup the ioscan in both plcs and things seem to work for a while but then it seems i lose communication on the 1 bit that
should be always on, it then causes the machine to lose auto we then reset and restart machine and things are fine again.
when i run with the original hardwire setup ioscan disabled it runs good no problems.
i do have the proworx "read count" set at 100 which i intend to set to 1 when iam able to do a start/stop of plc, the "read lenght" in unity is set to 1.
the "health timeout" is 1500 in both plcs, the repititive rate iam unsure what i set those to right now but it will be around 20 is this a value which should be the same in both setups?
the "last value" is set to fallback to zero in both setups.
ok think i have most of it stated here anything else please let me know.
wandering if scan time difference between the 2 plcs has something to do with it being that the unity setup should have a much lower scan time is the proworx setup with
its higher scan time causing a error?
aggattapauer
do you need to exchange only 1 word??
ok, first you don't need to setup io scanning in both plc's. Choose the one you want to be the "master".
I suppose the Quantum Unity. I suppose you want to read from Proworx the address 41000 and store it in %MW2000. I don't understand if also Proworx has to read a word from Unity... so I suppose yes and it's mean Unity has to write its %MW2100 to Proworx 41100.
Now you have to setup in Unity noe two io scanning line: one for reading; one for writing.
time out 1500 is enough
the repetitive rate must set greater than the maximum scan cycle so 20 (milliseconds) could be critical. This setting is needed to configure how many milliseconds the io scanning has to wait before sending every new command.
reading register start from 2000 (%mw2000)
the address to be read is 1000
the length 1
the write section must be 0
the second line is to be set the same as above but for writing section
writing register starting from 2100 (%mw2100)
read address and length must be 0
the address to be write is 1100
the length 1
Now when write 1 in 41000 you'll have 1 in %mw2000 and by writing 1 in %mw2100 you'll find 1 in 41100.
Tell me what are exactly all configuration you did with correct addresses.
Good job!
jagg
hello
yes only doing 1 word each way sup. wants only reads done so each plc does a read of the other.
ok i verified few things today
unity
cpu=65150
noe=771-11
f.w=4.3
ipaddress=proworx noe ip address
unit id=255
health timeout=1500ms
repetitive rate=16ms
rd master object=%mw150
rd slave index= 4499 (which is offset for the proworx plc reg.=404500)
rd lenght=1
last value(input)=set to zero
proworxnxt
cpu=213-04
noe=771-00
f.w=4.3
ip address=unity noe card ip address
unit id=255
repetitive rate=20ms
function =read
fallback value=zero
read ref. local=404505
read ref. remote=400155 (which is %mw155 address in unity )
read count=100 (when able will lower to 2)
i did a check on scan times
unity=29.9ms
proworx=49.9ms
think that it for now
i have a ntron switch beteewn the plcs and will be changing that out when able
aggattapauer
QUOTE
unity=29.9ms
proworx=49.9ms
set both more than 50 ms for instance 60 or 70
QUOTE
ok up to you, in that case I would prefer to perform only one IOscanning (read and write) so I won't run into synchronization problems. As I understand you have to manage something like a sequence..
