[quote name='daxtojeiro' date='May 18 2009, 10:09 AM' post='82337']
[quote name='ssommers' post='82276' date='May 15 2009, 04:35 PM']
Hi Phil -
Welcome to the forum!
The key is going to be finding out what codes are applicable in your location. In the US, I use NFPA 79 which allows me to have multiple disconnects as long as I meet certain conditions - warning stickers, wire color code, etc.
HTH!
Susan
[/quote]
Hi there, thanks for that, how do I find out what code of practice I should be using? I dont mean to sound ignorant, but I really have no idea where to find out this info and our Health and Safety guy has no electrical knowledge at all

Phil
[/quote]
I don't know European codes, except that there are way too many of them and that the EU excels at creating giant unmanageable bureacracies! I'm not 100% sure but I believe it is IEC 60204. In the U.S., NFPA 79 is voluntary but since it's a consensus safety standard, it helps when something happens and the lawyers get involved.
[quote name='paulengr' post='82293' date='May 15 2009, 11:59 PM']
The more important issue to consider in this case is bus protection. Since you have tapped power off the main bus at two locations, both devices must be large enough to shut off power under load in a short circuit scenario from the feeder for both. In addition, the feeder wiring must be large enough to withstand a short circuit from either one. If not, then you may have code/protection issues due to undersized protection for the wiring and/or disconnects (a potential fire hazard issue). When you wire up something similar to what you describe, it often results in a seemingly silly situation of an enormous disconnect for a relatively tiny circuit.
[/quote]
Hmmm, so what you mean is if one supply shorts out then they both must trip out? Or do you mean if both short together? The two supplies are not on the same bus from what I gather. This install has been done by contractors under management supervision. We (the maintanence guys) have tried to point out that we dont think it's being done correctly, but we really have no idea what is correct
Phil
[/quote]
No, I'm not saying that they must both trip or short. What I mean is that I'm assuming that both are fed independently from a mains somewhere. What you will commonly find is this. Imagine that you have an existing machine with say #8 power conductors feeding the circuit breaker. Then this new add-on hardware that you are talking about gets added in. Well, they want it to be powered separately so they simply run #14 wire up and jam them down inside the lugs on the feed side of the primary disconnect. This creates three obvious safety violations:
1. The #14 wires are not adequately protected. The proper way is to use #8 wires to tap off the main disconnect switch to do this and run a second disconnect. However, this requires a separate enclosure with properly rated terminals to do it. Which brings us to the second issue...
2. The terminal lugs are almost gauranteed NOT to be designed or rated for running two wires on the same terminal because very few are rated for it. And...
3. The small #14 wires are probably far smaller than the rated wire size that the lugs on the main breaker are designed to accommodate.
The short circuit interrupting rating of the smaller disconnect or circuit breaker must also be large enough to handle the potential short circuit current that it is being fed with. This means that it can't be one of those tiny control circuit breakers that are commonly used in panels...it will probably be almost as large as the primary disconnect. Usually since the listing agencies and codes have standardized on circuit breaker interrupting ratings, this means that both circuit breakers will have the same ratings (such as 25kA, 65kA, 100kA, etc.).
So all I was saying is to watch out for these common screw-ups when someone does something like this.