QUOTE(tunnysting @ Mar 28 2009, 10:29 AM) [snapback]80468[/snapback]
Hi all,
recently I have seen more projects that state the cable screen should only be connected to ground at one end. Up until now the screen was grounded at both ends and we've never had any problems. Just wondering what experience people have had.
Cheers.
It depends. There's grounding, and then there's grounding. If you are talking about power circuitry, then BONDING is required. If you ground at multiple locations, you can create a distributed ground. This MIGHT be OK in some instances but it is generally a very good idea to avoid this if at all possible. The infamous "stray voltage" problem that you may hear about is because utilities commonly use distributed grounds (ground everywhere it is feasible to do so) and the results have been true ground loops with voltages and currents high enough to cause problems with livestock and various other strange situations. The following web site explains how/why this occurs towards the end with utilities that violate the basic rules on isolating grounds:
http://www.bassengineering.com/SV_Cause.htmThat's not the best ground anyways. I currently work in a mining company. We run 7200 volt and 4160 volt equipment for the most part. Even the usual safety function of proper grounding and bonding (tripping the overcurrent protection device in the event of a ground fault) simply doesn't work in many cases because the fault current is insufficient to trip anything. At 7200 volts if the line impedance is 10 ohms, the fault current is 720 amps. That's OK except when you have a 1000 A piece of mining equipment...the circuit breaker will never trip. In addition, achieving an adequate Earth ground isn't easy with the soil around here (very sandy and dry). So we run high resistance grounds with ground fault detection relays (to handle the low fault current issue) and try to do the best we can with bonding and grounding to Earth ground, which is much less critical in a high resistance grounding system. All equipment is connected to a 4-wire system (to provide the lowest resistance bonding paths we can get).
If you've never heard of this, check out this article that explains it:
http://www.kilowattclassroom.com/Archive/NeutRes.pdfAs to why you'd want to do it, check this out:
http://www.mikeholt.com/mojonewsarchive/GB...ng~20040812.phpOn the signal side of things, if you connect both ends of the shield to a ground, then what you've just done is to create a continuous loop. A loop is a form of antenna, and specifically current loops are optimized to receive magnetic fields...which also so happens to be the same RF noise that is most common in industrial plants. So effectively you've created an antenna and you are coupling it into your signal lines by induction...not a good idea. The gain isn't great but I think some of the numbers I've seen on Ethernet shielded vs. unshielded systems suggest that you can get at least 5-10dB of RF gain sucking in all the available nearby noise. Of course your results may vary because you may or may not have lucked out and experienced this problem and because noise interference is highly situation dependent.
