Hi Dear,
I am working on a project the communication system topology is mentioned below. i am using the Delta product, if anybody has worked on this product, kindly let me guide through the communication scenario.
there is a network of Modbus Ascii with below mentioned devices.
PLC: DVP-EH (Station Address bydefault 01)
HMI: DOP-AE (Address 02)
PC: (RS232 to RS485 converter) Kepware OPC server installed driver of "MODBUS ASCII SERIAL" for SCADA application.
*-The question is that how can we configure the 1 Master (PC) and both other devices on Slave like (HMI) and (PLC).
we have successfully communicate the device with (PC to PLC) and (HMI to PLC) on Modbus Ascii individually. but when all of three devices wheres come into the network it may display the error message on both HMI and PC time by time.
if you have any query regarding above, kindly let me inform for further.
Regards.