QUOTE(BobLfoot @ Apr 19 2008, 08:31 PM) [snapback]67987[/snapback]
Annual Maintenance starts with load shed of all 480 loads and then opening of the main switchgear. Our Electricity Vendor then disconnects the 13.8 from our Main Switchhouse and we ground the 13.8 loop at the main. This is followed by grounding the 13.8 at each and grounding of the 480 at each sub. Once the system is "cold" maintenance begins.
There-in lies the issue. Electrical equipment is funny stuff. It does NOT follow the standard assumptions for maintenance. Most electrical failures will happen within the first few weeks/months of operation. After that point, as long as you don't disturb it, it will typically run and run and run right up to the end of it's useful service life and then fail, sometimes with early warnings. This is contrary to mechanical equipment that is usually the most reliable and holds specs only when it is brand new and goes on a linear downhill curve from there.
The cycling of the equipment is far more damaging than not. A classic example is that there are two plants in central Georgia almost side-by-side. One does a similar outage procedure every year. The other does...nothing. The difference in maintenance costs? Significantly higher for the plant that does annual maintenance. Difference in reliability? Zilch. Roughly the same number of failures, etc.
If in doubt, doing nothing is far better with electrical equipment than doing anything at all, contrary to popular opinion in "proactive" groups. For instance, all the old text books (American Electrician's Handbook for instance) still recommend taking your motors apart annually and regreasing the bearings! If you follow the greasing schedules you typically get for mechanical equipment, you'll push grease up inside the motor and cause premature failures in nothing flat. The best grease schedule is absolutely minimal, and nothing is second best to overgreasing. One of the formulas I've seen is 1 pump (one stroke) per 25 HP. This is very little grease indeed.
QUOTE
changing the battery in it's trip unit
I definitely stopped doing this. Depending on the trip unit, the only thing the battery does for you is store settings in the event of a trip and the breaker becomes unpowered. It's nice to do but rarely has any value. This is a nice to have but makes sense when you are already doing maintenance work.
QUOTE
applying a fresh coat of electrical grease and re-racking the breaker.
Good idea, since you disturbed a connection that was gas tight.
QUOTE
This is followed by a cleaning of all buss bars and checking of a joints for torque.
Bad idea. You are actually gradually INCREASING the torque and not following torque specs. This is the same as taking your torque wrench and hitting it multiple times. There is plenty of mechanical maintenance literature talking about this fallacy.
QUOTE
We also vacuum our and dust each transformer enclosure and check cooling fan performance.
This is a good idea. I highly recommend doing this as long as you're not disturbing any of the connections.
What I didn't see is any mention of doing thermal (IR) scans. Though it's not a 100% gaurantee and there are some basic rules about doing it right (such as not scanning your transformers at high noon when solar radiation accounts for more hot spots than actual problems), it does tend to catch joints and some component failures in the earliest stages of failure. I recommend every 6 months, and that seems to be the general rule.
Second, annual transformer oil analysis is generally a very good idea. It doesn't cost much. It will let you know what's going on in your transformer IF you keep records. Educate yourself on this stuff because there is a lot of "noise" in addition to the data. You can easily be fooled by simple garbage data coming from AA spectroscopy for instance (but very few companies run anything else). Karl Fischer is notoriously unreliable and the moisture data is difficult to make sense since it's an ongoing process.
Third, IEEE and NFPA recommend draw out circuit breaker testing every 3 years. Might as well do a Dobles test on your transformers (turns ratio test) while you're at it. These are the just about the only electrical tests worth messing with on distribution equipment because they directly measure performance against specs. If you've upgraded your circuit breakers to electronic trips, they frequently have built in tests. But in addition you are supposed to exercise the mechanisms periodically (manufacturers specify frequency; I believe S&C is the most aggressive @ twice a year) and sometimes grease them on a recommended schedule.
I know that plants that do no maintenance are always concerned about doing the right thing. The few that do far too much are just as bad but it's much harder to change the culture there.