QUOTE(Brent S in Cincinnati @ Mar 19 2008, 10:14 AM) [snapback]66665[/snapback]
My question is, even though I know it is acceptable in an enclosure to size the conductors to the load protection (motor protectors here) isn't there a minimum ratio ( 10:1 ) of the main fuse size to the current capacity of the conductors coming off of distribution blocks? I haven't been able to find this in the code.
I usually build 1 and 2 door PLC panels with servos and vfds, so I'm trying to be careful with the 8 door vfd enclosure I'm putting together.
I have a main disconnect for 3 phase 460VAC with 350 Amp fuses. This feeds a distribution block where the conductors step down to #1 AWG. From there I supply each of 4 distribution blocks, 1 for each pair of doors. From there I have #10 AWG feeding groups of 5 motor protectors through bus bars. In this setup the #10s are fed directly from 350 Amp fuses. It seems a little extreme to me.
There are 154 Powerflex 40 vfds, mostly 1 hp. Each Powerflex is fed from its own Motor Protector, AB 140M-C2E-B40 for the 1hp vfds.
I fail to see how you are protecting anything. If I understand you right, you are using 350 A fuses to protect #1 wire, which is rated to 100 A even with a 75 C rating. So far so good assuming that you are protecting motor circuits (350% rating) EXCEPT that first off you're not (there are VFD's in there), and second, you didn't derate everything by the 80% rule since it's a motor system.
Now you go to #10 wire. This is only capable of about 24 A at most depending on which chart you are looking at (my good one is at work). You have ZERO protection for your #10 feeders. The only way that this would be legal is if you fed a SINGLE downstream source with 5 of them as parallel feeders.
A motor protector is a secondary protection device. It is totally illegal for the purpose of protecting the VFD. A real protective device is required as primary protection. The proper device is either a real circuit breaker or a real fuse. You don't even need motor protectors in this system because the VFD itself provides motor protection (built-in overcurrent limiting and overload tripping). If you had fused the #10 wire correctly in the first place, this could serve as your VFD protection and you'd be done. No need for expensive secondary protection devices that are not doing you any good at all.