Hi PdL,
No you are not missing something. We are saying exactly the same only you use IR coils as intermediate.
As the example given was directly for DM100 so I proposed to use the DMcoils same as you do with IR coils. Now you do not need to move the IR all the time to DM.
regards,
QUOTE(PdL @ Jan 30 2008, 09:47 AM) [snapback]64405[/snapback]
QUOTE(MPM @ Jan 30 2008, 08:15 AM) [snapback]64400[/snapback]
It is offcourse possible but you will have always take care of the alarms that are already present.
If you have 10 alarms defined you have to define each combination possible when writing values to the alarm register.
If an alarm always comes alone it should be not an issue at all.
regards,
No need to write every combination, you could just program 16 alarm contacts directly to 16 coils of the same IR word, then do a constant move of the IR word value to the DM word ? Or am I missing something...