prakash
Dec 4 2003, 07:17 AM
Hello,
I have system where in we have selected PV300(RS232 , DF1, DH485) AND Compactlogix L30, I have problem in Doing the Screens in Panel Builder, I have tag Mentioned PV1_DOOR_OPEN in my Logic , But i am unable to give the same tag address in the Panelbuilder. Does it Support these address or is their any alternative to do this. Thanks in adavance for help
Prakash
navillusi
Dec 4 2003, 10:51 AM
I may be wrong, but I seem to remember that some of the panelview terminals will not accept the tag based address system of the compactlogix processors, instead file:word/bit addresses have to be used. The variables that you wish to display on the panelview must be copied into an array, e.g. data[0..10] of INT, this array is then mapped to an SLC/PLC message file in the processor, e.g. to file 7.
So in the panelview it would be read the same as an SLC e.g. N7:0
Ken Roach
Dec 6 2003, 01:56 AM
Ian is correct; the PanelViews that use the old PCCC type networks (DF1, DH485, and DH+) only support PLC-5 or SLC-500 style addresses.
I usually set up an array or two just for PanelView communications and then set aside a periodic program to copy my functional Logix tags to the tag array that is mapped to PLC-style addresses.
prakash
Dec 6 2003, 02:36 AM
Thanks a Lot I followed the Same, But i still Not have the hardware to Test.Thanks again
Prakash
This is a "lo-fi" version of our main content. To view the full version with more information, formatting and images, please
click here.