QUOTE(Ken Moore @ Oct 23 2007, 04:29 AM) [snapback]60780[/snapback]
What Ken Roach said was generally true until about 2-3 years ago. Many DCS vendors now have dedicated comm. modules for most of the industrial protocols. I have an older DCS using the KF2, but I plan on upgrading next year to a dedicated DH+ module.
Regardless of the hardware link, the DCS will poll the plc for the required data, the interface is similar to a SCADA system interfacing with a PLC via DH+, no messaging required.
Thanks!
If I understand correctly, I should not need additional hardware, such as the KF2 module or other. The DCS should be able to connect directly to the DHRIO serial port.
Also, I believe that I understand that the DCS will reach out and grab the desired registers from the ControlLogix memory, without me having to message them out or put in special memory areas.
Please confirm.