Shorting an analog output on purpose? |
Nov 6 2009, 05:01 AM
Post
#1
Sparky ![]() ![]() ![]() Group: MrPLC Member Posts: 375 Joined: 16-March 05 Member No.: 6,777 Country:United States
I am going to assume the AO is 4-20 mA and I know the hardware is a Flex 1794-OE4.
Has anyone ever been asked to short the analog out [Example terminals A-0 to A-1] of the card under a certain set of safety conditions or any condition? The terminals would be shorted using a set of contacts from a relay. Thanks |
Nov 6 2009, 10:30 AM
Post
#2
![]() Guru ![]() ![]() ![]() ![]() ![]() Group: MrPLC Member Posts: 854 Joined: 1-December 04 Member No.: 2,647 Country:United States
I am going to assume the AO is 4-20 mA and I know the hardware is a Flex 1794-OE4. Has anyone ever been asked to short the analog out [Example terminals A-0 to A-1] of the card under a certain set of safety conditions or any condition? The terminals would be shorted using a set of contacts from a relay. Thanks I have seen "open" it but not short it. Why short it? For what purpose? |
Nov 6 2009, 11:21 AM
Post
#3
Mickey,
I am told they want to do this to force the signal to 0 and in turn force the valve to the closed position. |
Nov 6 2009, 11:23 AM
Post
#4
![]() Guru ![]() ![]() ![]() ![]() ![]() Group: MrPLC Member Posts: 817 Joined: 6-May 05 Member No.: 8,628 Country:United States
I saw it once on a vacuum furnace - the over-temperature alarm relay shorted the 4-20mA command coming from the temperature controller. If you have a form C relay then you could use one contact to short across the input of the field device and the other contact to open the 4-20mA loop, that way you don't have to worry about the load on the analog output.
Attached image(s)
-------------------- Venn ist das nurnstuck git und slotermeyer? Ya! Beigerhund das oder die flipperwaldt gersput!
Nov 6 2009, 11:41 AM
Post
#5
Depending on the input impedance of the the valve and the output impedance of your PLC AO you could throw in a small resistor as long as the overall impedance stayed lower than the max impedance of the AO. In theory the 4-20mA AO should be able to deal with a short but I wouldn't bank on all manufacturers building their product that way. The command shorting relay on the vacuum furnace I mentioned was shorting across a very large rack mount Honeywell controller with a voracious power appetite and a power supply to match.
Attached image(s)
Nov 6 2009, 11:48 AM
Post
#6
Alaric,
Here is what they are proposing.
Attached File(s)
Nov 6 2009, 12:12 PM
Post
#7
Nov 6 2009, 12:19 PM
Post
#8
If that is what the customer is proposing then give them that. Their design. Their responsibility. As I said, I've seen it before. As a precaution however I would configure the output for 0-20mA and program it to output 0 mA when ever CR06330 is off and operate in the 4-mA range whenever CR06330 is on.
Nov 7 2009, 06:07 AM
Post
#9
Mickey and Alaric,
Thank you for your help. Bob |
| Think this page or topic is awesome? Submit to: |
Lo-Fi Version | Time is now: 20th November 2009 - 06:14 PM |
