Uwe_A
Keyence KV-B8XTD beginners question
9 posts in this topic
I'm trying to make my first steps with a Keyence GPIO unit called KV-B8XTD connected to a KV-7500.
I'm using the KV-Studio 10 for control. The only thing I want to do is to switch an output of the GPIO from low to high.
I set the KV Studio to "Monitor", open the KV-B8TXD and set some outputs (see image)
I would assume that OUT0, OUT2, OUT3, OUT6 and OUT7 on my B8XTD are showing +5V but they don't. All outputs stays at 0V.
What is going wrong? Do I misinterpret the "I/O unit monitor" if I assume it is meant to be used for setting the output signals?
Uwe
The KV-B8XTD has sinking type (NPN) transistor outputs. This means the outputs will switch the negative side of an external voltage to a load. Once you have connected a complete circuit, you will measure +5V or +24V (whichever you use) at the output terminal when the output is OFF. Turn your output ON and you will measure close to 0V.
Mr_PLC_KVB8XTD.PNG.675fd8b8e5c27bd425e4a
Thank you for the information!
Now I have 4,63V at OUT0 but unfortunately it does not change to 0V if I turn the output to ON.
Is this I/O unit monitor the right tool for setting the outputs?
Or do I have to set it via a Ladder program?
Quite honestly, I have never used the I/O Unit Monitor. It may work but I prefer to use ladder, especially if the output is already programmed in ladder. I would like to give you a better answer but I find KV Studio to be very confusing at times. I believe the Japanese to English translations are very poor. It's good software with a lot of functions but I have trouble understanding most of them.
I would write a test program where you can use internal bit to drive your outputs. Then, in Monitor Mode, double click the internal bit to toggle ON/OFF.
Mr_PLC_KV_Monitor.thumb.PNG.80c9e36c09e7
I wrote a test program with two commands:
1. "A 0" (reading from IN_0) and
2. "O 100"(writing to OUT_0).
Is that correct? (I was not quite sure how to use an internal bit to drive my output...)
I would assume that if I supply +5V to IN_0 I should see a reaction on OUT_0. Right?
But there is another issue: It looks like I cannot start my PLC program. If I press the "RUN / cont. scan" button nothing happens. The "PROGRAM / stop" button is still highlighted. Additionally the status bar keeps showing "- PROG" but it should switch to "RUN", I think. Can you verify?
(I set the "PROG/RUN" switch of my 7500 to "RUN" otherwise I get a message that I cannot switch to run mode)
Yes, this will work for testing. You should review the manual for the different memory types. In my example I used internal bit "M240". You can use M0, M1, M2.... up to M15999 in my case. I'm using a KV-5500. The 7000 series may have a different amount of memory.
No. The module is sinking (NPN). This means you supply negative to the input terminal. See the input diagram.
Mr_PLC_KVB8XTD_Input.PNG.0d65d133c72c7d9
Did you perform a Transfer to PLC? It looks like you have.
Perform a Convert (Ctrl + F9) and verify no errors.
From the Monitor/Simulator menu, select Unit Monitor and verify the Error Status.
In the case of the KV-7500, the internal bit memory is "MR" 0 - 399915. See the User's Manual - List of Devices.
"Convert" shows no errors.
Error Status is "None".
But the bottom line status still shows "/ PROG" even if I press "Start Monitor" (F4).
Is my PLC broken??
1) Right click on [0] KV-7500 from the project tree and select Error Monitor. The manual states the PLC will be switched automatically to PROG mode in the case of a serious error.
2) From the Monitor/Simulator menu, select Verify with PLC/synchronize. This will make sure you have a program in the PLC.
