Face Book
B&R Modules in Simatic Manager Program
24 posts in this topic
Hi
Can you explain how to integrate B&R modules into Simatic Manager program and what is the difference between these modules as in the attached photo?
Hi Face Book.
You have configured your Slave as Node 6. Your Modules have different amount of Bytes depending on the slice/ module configured in your real hardware.
You should check this then ammend as required.
Edited by collinsd70
HI
The program is already run without any problem as the designer do.
I need to know the concept of this.
What do you mean by concept?
The way your Slave Hardware is laid out is all dependant on your field wiring and the requirements of this.
Hi
X67BC6321.L08
X67DM1321.L08
And other modules
I don't find  all of these I/O in the PLC modules
Those should correspond to Head Module part number.
Are you saying those numbers dont correspond to your actual hardware part numbers?
If you cant find them in your catalog, chances are you need a .GSD file update.
NO
I don't find  all of these I/O address in the PLC modules
What is the relation between
X67BC6321.L08
and the modules in the table?
Module:
X67DM1321.L08
and reserve 10 byte
for digital 16 I/O Module
How?
Edited by Face Book
The reason you have more BYTES than required is because maybe they are reserved for Diagnostic Bits. For this information you will have to test online with a VAT table or consult the documentation.
The ET200 slices also have this sometimes.
1 person likes this
Hi
1-How the modules connected in the table in the attached photo?
2-What is the difference between them?
3-What is the relation between
X67BC6321.L08
Edited by Face Book
X67BC6321 is your PROFIBUS SLAVE Module- the profibus cable will enter here and terminate; or move on to the next node PROFIBUS node.
X67DM1321 is an 2 BYTE I/O Module that is connected directly on the above module- this then passes on to Slot 2 on the X2X Expansion Port.
So in brief, the answer to your question is that they are 'local expansion modules' on your BR&R Slave...not profibus.
Regards
Daniel.
1 person likes this
Yes
But Iam not understand the connection between them
Can you draw a  diagram explain the connection between the modules?
They will be in a 'daisy chain' like Profibus.
The data between these module is passed back to X67BC6321 who in turn passes the IO Status to and from the Profibus.
See attached.
Regards
Daniel.
1 person likes this
Hi
 What are the physical I/O addresses that used in these modules?
"these modules contain large byte of I/O addresses"
Edited by Face Book
Check your symbol table.....
Regards
Daniel
I need to know how to address I/O for these modules in general?
Edited by Face Book
Hi
If we have  X67DM1321.L08
I/O as in attached photo
in HW Configuration:
I  Address:86.......91
Q Address:86....89
What are the addresses for these channels in this case?
Edited by Face Book
Your first 2 BYTES here will contain real IO Statuses.
The last 2 BYTEs is of type Unsigned Integer which contains the serial number for each module.
Regards
Daniel.
1 person likes this
Hi
Please Check the addresses in the attached photo.
Am I right?
Hi Face Book.
You will have to consult the manual and individual modules in more detail for this.
If you have eletrical schematics this will be easy to cross reference with the SIMATIC Manager.
Regards
Daniel.
1 person likes this
Your welcome. Good luck.
Regards
Daniel.
