Posted 19 Jun 2017 Hi all. Is there any way, to add two events with same address in Event log? I need to make event list, when address is ON and when address is OFF? Thanks in advance, Miloš Share this post Link to post Share on other sites
Posted 19 Jun 2017 It appears you are not able to. If you can program the PLC then add a separate address there. 1 person likes this Share this post Link to post Share on other sites
Posted 20 Jun 2017 No possible - CX-Designer rejects the same address twice. That being said I wish there was a way to specify NOT 2.01 to say a light - have to revers the bit in the PLC and use it as a separate alarm or status point. Or is there a way? Always annoyed me - I do quite a lot of Citect SCADA and NOT is quite a normal function. Share this post Link to post Share on other sites
Posted 21 Jun 2017 It's common in many newer interfaces especially the PC based ones. The Omron NA screens allow this. NS is 15 years old. Share this post Link to post Share on other sites