larive
ADAM-5000/TCP Modbus Communication Watchdog
Hello, I would like to setup ADAM-5000/TCP racks so when Modbus communication is lost to a 5069 digital output module then the module would release all outputs after a certain period of time. The feature is available in the Adam 5000/TCP utility, but doesn't seem to work. Could any provide me with some idea? Thanks a lot!
I am not sure about those racks but I have some information for setting up other kinds of Modbus TCP racks. I included information on the racks below. Quick Start Guide: http://www.icpdas-usa.com/documents/et_87pn_quick%20start_guide_english_v1.0.1.pdf User's Manual: http://www.icpdas-usa.com/documents/et_87pn_user_manaual_v1.0.1.pdf Modbus Utility: http://www.icpdas-usa.com/documents/modbus/modbus_utility/ Modbus Master Tool: http://www.icpdas-usa.com/documents/modbus/modbus_master_tool/ ET-87P4-MTCP: $799.00 4 slots I/O Expansion Unit with Modbus TCP protocol, communicable over Modbus RTU, Modbus TCP, Ethernet, RS-232. Supports operating temperatures from -25 ~ +75°C http://www.icpdas-usa.com/et_87p4_mtcp.html I-8000W I/O Cartridges for the rack: http://www.icpdas-usa.com/i_8000_high_performance_modules.html I-87KW I/O Cartridges for the rack: My linkhttp://www.icpdas-usa.com/i_87k_high_performance_i_o_modules.html We provide free technical support in case we can help with anything. Maria Lemone ICP DAS USA 1-310-517-9888 ext 105 mariaL @ icpdas-usa.com (remove spaces in email address) http://www.icpdas-usa.com
The Adam-5069 does not support Modbus TCP; unless the rack system that you plug it into converter the Modbus RTU data to Modbus TCP. We have a simpler solution. Using our ET-7067. It is a Modbus TCP slave device which can be added to your SCADA system. http://www.icpdas-usa.com/et_7067.html To enable the safe values, you simply connect to the module with IE or Chrome and set the safe value on the web configuraion page.
