Search the Community

Showing results for tags 'schneider modicon m340'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 117 results

  1. Hi, I have a modicon premium plc rack with TSX PSY 3610 power supply module. The psy 3610 power supply has an alarm contact and it is used in a loop to energize a hard ware relay for 24VDC supply to the DO module FTA boards. There is a safety button in parallel to the alarm contact so that during startup we can press this button, energies DO module loops and all IO faults cleared and power supply alarm contact latches The problem is that this power supply alarm contact remains always open even when IO report no faults. The PLC has MAST task only and it is running with no faults. If I jumper the alarm contact all the IO's are healthy . tried changing the power supply and DO modules. no hope. please help.
  2. hi guys i am using my Schneider m221 plc  but facing this below problem. how can write modbus address  i am trying below register data address but not accept this register data  address example i write %MW0:=16#10001 %MW1:=16#10002 %MW2:=16#10003 %MW3:=16#10004 so guys how can write this register address can me  share one example so i understand. also share read var setting . ObjType: FristObj: Quantity: IndexData: Thanks
  3. Hello Everyone. We have Schneider TM241 PLC Along with Citect SCADA System at 100MWp Solar Power Plant to monitor and control various equipments like Inverters, Switch-Yard, MFMs, Weather Monitoring Systems etc... Government Authority here asked every solar plant to control the generation as per the instructions by Load Dispatch Center, for that we need to implement logic to control Generation as per requirement. For that we are controlling generation from inverters by giving them generation setpoints calculated by PLC using PID function.   But we are facing one problem while using PID. (FB_PID of Toolbox Library)   Suppose we need to generate only 60MW out of 100MW. So we set PID setpoint to 60MW and according to that we get PID output and according to that PID output value we provide generation setpoint to every inverters.   This system works very fine until the clouds comes into the picture.   Now suppose Setpoint of PID is 60MW and PV is also near about 60MW, and suddenly large cloud comes over plant and block solar radiation.   In this case generation comes down to 10MWp(or any value below 60MW), So output of PID will Increase and keep increasing and settle at the Maximum value. but without solar radiation generation value stays very down then Setpoint.   Now suddenly Cloud moves and again solar radiation increase, but the PID output is maximum at that time so, Suddenly Generation goes from 10MW to near about maximum capacity (100MW) instead of 60MW, and then it will slowly comes down to 60MW.   We need to rectify this generation shoot up when cloud moves. Anyone have idea how can we solve this problem or anyone have programmed PID in this kind of situation.   Is there any function block available to do this correctly like function block of PID with two Reference or something like that...   We are using TM241 which is CoDeSys based PLC.
  4. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  5. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  6. I want to offer my industrial surpluses for your projects! All details are verifiable. Excess surpluses often occur. Sending to any country in the world. The price is low. I can pick something up for you personally. Sending can be made, both expedited, and economy air delivery. Ukrposhta or EMS Ukraine. Siemens Simatic, Wieland,  Wago 750, BECKHOFF, Schneider electric, Schneider Automation, Yaskawa Omron, KEYENCE, Pepperl+Fuchs, Telemecanique, ABB, FESTO,  DUNKERMOTOREN, Eaton, Micro Innovation, Jumo, Phoenix contact, Bruel & Kjaer, Unitronics, Samson, Danfoss, OMRON, Rexroth Indramat, Fanuc.  https://www.ebay.com/usr/vitalij6131   All parcels are sent by Airmail, are processed with disinfectants and sent with a large number of bubbles before being sent. For safe delivery of the parcel to you! I am worried about your safety, in this difficult time for you!
  7. Hello guys, I am very new at this. I am trying to make a Schneider PLC (TM251MESE) to send some serial commands (485)  to a integrated stepper motor from Automation Direct (STR-MTRD-17030RE, but I am lost. The driver has been program to receive the SCL commands. But not quite sure how to send those from the plc. Im using SoMachine V 4.2 Have any of you done anything similar? Any example will be greatly appreciated.  Thanks 
  8. Hello, Do you know what is the difference between the PID controllers PIDFF, PID1 and PIDP1 in a Schneider PLC? I have to modify a PLC program with a new standard of coding. The new standard use a PIDFF function bloc. If I change a PID1 bloc for a PIDFF bloc, can I use the same parameters Kp, Ti, Td? If I change a PIDP1 for a PIDFF bloc, can I use the parameters Ki and Kd to calculating Ti (ti=1/Ki) and, Td (Td = Kd)? Thanks you for your help.
  9. Dear All, TM241CE40R is installed with firmware 4.0.3.18 If I buy new CPU with some other firmware, will it work or I will need to change the firmware?  
  10. Hello. I am having 22 slaves communicating to a master on rs485 half duplex.i have selected baud rate as 38400 on a length of 800m.The problem is out of 22 devices only six are communicating .i have checked wiring,inserted termination resistor but still not getting rest of the devices alive.is it that i have selected high baud rate on a long length?this is the only problem as i am seeing it.can somebody help me on this issue
  11. Looking for any and all new industrial surplus and even some used on a case by case basis. Anyone have any questions feel free to email me at contact@trojansupply.com We also have some great deals on any items we have instock we compete on price as we are a small entity. Same day shipping available. 
  12. Hello - we run a car wash that is controlled by a Modicon TSX Micro 3721001. It is indicating a CPU fault. I've attached a picture of the unit in place, with the LEDs lit. I have ordered a new base unit (2nd picture). I haven't tried it out yet, but it is tested working. I am hoping a base unit replacement will solve the problem, but wondering if it it possible the problem could be in the modules? I did not order those but now wondering if I should have... If the issue could be with the modules, is there a way to test which one it would be so I won't need to order all 4? If it coult be a module, I might order that now as I am in a rush to get back in service. Thanks for any guidance! Andy
  13. Hello. I am trying to make a serial RS 232C connection between Schneider Magelis HMIGXU3512 and Omron PLC CP1E. However, there seems to be a communication problems between both of the equipment. I am using cable XBT Z9740 for the serial communication cable. The format used is 8.2.N for both equipment. The baud rate is 115200. No Flow Rate is choose. Anyone can help with this kind of problems?
  14. Hi, I've been having a problem with my Schneider setup, and I can't seem to figure out the problem. I'm using Machine Expert Logic Builder and Vijeo 6.2, and I can't seem to download to my PLC. I can download to my HMI just fine, but my HMI comes back with the message as mentioned in the title. Also when I perform a full download, machine expert comes up with the message "Could not connect to the device for item "xx", selected target system "PLC name" is different from the connected device "HMI name". The weirdest thing is that machine expert shows my PLC just fine, but doesn't show my HMI. I have no idea what to do, as I feel like I've tried everything. The IP range is fine, subnet is fine. The driver in IO manager in Vijeo has the PLC nodename in it, so that shouldn't be the problem either. Does anyone know what to do in a situation like this? Thank you in advance!
  15. Please could you assist with the software required to download data tables from 4 off DIRIS A10 Multifunction Meters into TM221CE40R Logic Controller via TMC2SL1 Comms Cartridge using Modbus Protocol over RS485. I have downloaded the Modbus tables from Socomec but not sure how to get these into the PLC. I would really appreciate your help in achieving this. I am using EcoStruxure Machine Expert - Basic to program the PLC & DAQ Factory Developer Release for my Touchscreen. Link to Socomec Modbus tables: https://www.socomec.com/files/live/sites/systemsite/files/SCP/6_gestion_energie/diris/diris_a10/DIRIS-A-10_COMMUNICATION-TABLE_2018-01_DCG01013_MULTI.html#General
  16. i am trying to connect a gf+ flow sensor  through the signet 8550 meter loop for 4-20mA - i am unable to get  a reading from the sensor as i am connecting to tm3Ai8 input analog module.   please let me know how i can do this need for and urgency at a site.
  17. Hello Experts, We are currently in the design phase of a system with 24 PLC's.  CPU is BMXP342020  [ CPU onboard Serial and Ethernet ports, both capable of MODBUS] Each PLC's are stand-alone and have communication with 9 Modbus RTU slaves.  Also, each PLC will be connected to OPC at central SCADA room via MODBUS TCP. Questions:  Regarding Serial MODBUS RTU 1. CPU onboard RJ45 Serial port can directly make communication with all 9 slaves via multidrop?  Using READ VAR/WRITE VAR function? 2. How many READ VAR/WRITE function can be used simultaneously?  Regarding MODBUS TCP 1. Which module is required for connecting to OPC?     BMX NOC 0401  or  BMX NOE 0100?     Can the above two modules be connected to OPC without any programming?  We need to read/write data to each CPU all the time.  2. Does BMX NOC 0401/BMX NOE 0100 need programming in PLC for communication? 3. Does CPU onboard ethernet port require programming for communicating on MODBUS TCP? Please guide.  We have used M580 CPU in 10 projects and all the time DCS [Client] can read/write data with M580[server] without any programming. But we used CPU onboard port or BME NOC 0301.2 So does that sounds similar to BMX NOC 0401/BMX NOE 0100 Thanks in advance
  18. Hello everyone, we have a problem with a connection of a Schneider HMI and a Schmersal Security PLC, do anyone have some experience in that? it's about addressing, it's unable to map address from Schmersal PLC to Schneider HIM the address of the I/O channels in the network ? What should I do?
  19. hello I have been forced to replace a TWDLMDA20DRT with a Schneider TM221ME16R. the plc is a slave but I am having trouble getting the Modbus data exchange to work like it did with the old plc. I have setup the serial port to use Modbus etc etc and I played about with the read_var FB but this wasn't required in the old plc so im confused as to why I would need to use it on the replacement. I have come across another FB send receive message but again i'm not too sure if this is required.  the master plc uses the msg2 and exch2 command. I believe I am just missing something very simple here.   Lighting Panel - Old_PLC.twd Lighting Panel1 - Master -.twd Lighting Panel - Pillar5 -.smbp
  20. Hello everybody,   First, I used the BMX NOR 0200H module associated with a GSM modem, for the time stamp and the problem is at the level of data recovery (slave PLC), I received the value of the variable (it's OK), but instead of the modification date of the variable, I received the send date (from the master PLC to the slave PLC).   After this application, I tried to use Web Desinger to do the timestamp by recovering a .csv extension file, but the file does not generate in the memory card (I accessed the module's memory card by an FTP client).   At this stage, the BMX NOR 0200H module, does not respond to a new configuration or a modification (either by Web Designer software or by Web Server, even these last two confirms me by a dialog box that the module has accepted the change).     Thank you all for your attention.    
  21. This course is designed to equip the novice with no prior PLC programming experience with the basic tools necessary to create a complete PLC program using ladder logic common to most current platforms. Use Software : - Somachine EcoStruxure Machine Expert Basic - Free - Vijeo Designer Basic Full Articel About Lear PLC Schneider  Video Tutorial Learn PLC Training Free
  22. Hi We have some plc programs written by concept 2.1 b2.1 XL ,concept 2.1XL. I need setups of these versions
  23. I am trying to write some citect variables back to the PLC. I have made a startup cicode script which is suppose to copy one variable to another which I found on the web. I am not sure if just using tag = tag is OK in citect 2018. Any help would be fantastic.   Cicode below: *********************** FUNCTION StartUpFunction()     INT hMyTask;     // Start a new task that runs all the time and transfers values using writetag     hMyTask = TaskNew("fnDoThis","",0); END FUNCTION fnDoThis;     //Never Stop this Loop     WHILE 1 DO         //Update the first Tag         TagWrite ("M340PLC_R02kW",Sub02Substation2PowerkWtot)         M340PLC_R03kW = Sub03Substation3PowerkWtot         M340PLC_R04kW = Sub04Substation4PowerkWtot         M340PLC_R05kW = TerminalSubstation_5InstantaneousPowerkWtot         M340PLC_R06kW = TerminalSubstation_6PowerkWtot         M340PLC_R07kW = Sub07Substation7PowerkWtot         M340PLC_R08kW = Sub08Substation8PowerkWtot         M340PLC_R09kW = Sub09Substation9PowerkWtot         M340PLC_R10kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_R11kW = Sub11Substation11PowerkWtot         M340PLC_R12kW = Sub12Substation12PowerkWtot         M340PLC_R13kW = Sub13Substation13PowerkWtot         M340PLC_R14kW = Sub14Substation14PowerkWtot         M340PLC_R15kW = Sub15Substation15PowerkWtot         M340PLC_R16kW = Sub16Substation_16PowerkWtot         M340PLC_R17kW = TerminalSubstation_17PowerkWtot         M340PLC_R18kW = Sub18Substation18PowerkWtot         M340PLC_R19kW = Sub19Substation19PowerkWtot         M340PLC_R20kW = M340PLC_G1_GEN_FREQ_PV                 M340PLC_R21kW = Sub21Substation21PowerkWtot         M340PLC_R22kW = Sub22Substation_22PowerkWtot         M340PLC_R23kW = Sub23Substation_23PowerkWtot         M340PLC_R24kW = Sub24Substation_24PowerkWtot         M340PLC_R25kW = Sub25Substation25PowerkWtot         M340PLC_R26kW = Sub26Substation26PowerkWtot         M340PLC_R27kW = Sub27Substation27PowerkWtot         M340PLC_R28kW = Sub28Substation28PowerkWtot         M340PLC_R29kW = Sub29Substation29PowerkWtot         M340PLC_R30kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_R31kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_R32kW = PV2_SSB1PowerMeterPowerkWtot         M340PLC_R33kW = PV2_SSB2PowerMeterPowerkWtot         M340PLC_R34kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_R35kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_R36kW = M340PLC_G1_GEN_FREQ_PV         M340PLC_PQM3_WATTS_PV = HV_MetersBunnings_Intake_StnPowerkWtot         M340PLC_SOL01_SSB1_KW = SolarSSB1PowerMeterPowerkWtot         M340PLC_SOL01_SSB2_KW = SolarSSB2PowerMeterPowerkWtot         M340PLC_SOL01_SSB3_KW = SolarSSB3PowerMeterPowerkWtot         M340PLC_SOL01_SSB4_KW = SolarSSB4PowerMeterPowerkWtot         //Go to sleep for 1 second so as to not overload CPU         Sleep(1)     //Go back to start of Loop     END //End of Function END  
  24. I have a Modicon NOM0200 unit connected to an access switch to send commands to various rs-232 devices. The Access switch requires a "disconnect string" to end communication with a particular port. The disconnect string is "CRTL+D", how can I send a "CRTL" keystroke from the NOM0200 unit? I know for carriage return it is "$R" is their a similar combination I can enter for "CTRL"?  
  25. Hello, Currently, I have Schneider PLC- LMC058 - LMC058LF42 which support Ethernet communication. I want to collect data from this PLC to Database "MySQL". In order to do this I have below options: ** I can use Kepware OPC to gather data, However, there are 2 issues am facing. ________[*] this PLC appears to be Telemecanique PLC instead of Schneider .. which is what I don't understand. ________[**] Kepware OPC doesn't support Schneider nor Telemecanique PLC ... that's what I found but not sure of it. ** I found Somachine SQL gateway which dumbs data to MySQL, however: ________[*] I can't find enough resources on how to use it. ________[**] It's asking for License, Is there a way to crack or bypass it? ________[***] Has anyone used Somachine SQL gateway to directly connect Schneider PLC to MySQL database. My preference is using OPC server as it's the easier way, Hope I can find support on any of these 2 directions! Thanks. AK