Search the Community

Showing results for tags 'rotary mode'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 27 results

  1. 1769-IT6

    Hi all. I have a 1769-IT6 thermocouple/mv input module. It is connected to a micrologix 1500 unit. The green okay light illuminates on power up, but after you download the program and put it in run mode the processor faults. Terminal block with the cjc's are on the unit. The error message just says the I/O module has encountered an error. The hex code under status bit 6 is 179h. This error code is not in the manual. Has anyone else encountered this? Oh and I only have channel 0 enabled for type k thermocouple. Has anyone else had this issue, or know if it is a configuration issue. Any help would be appreciated. Thank you. 
  2. Hey, does anyone know why the simulation mode is on? how to change it? (LED SIM )
  3. simple motion cam curve

    Good afternoon, I have a problem in an application for a rotary knife, I'm using a MR-JE-B servo to make this movement, while my material is powered by an inverter connected to a modbus rs485 network, with a 5v encoder connected directly in motion. I'm having some problems and I think it's my cam curve. I have a very high refeneration, and the system doesn't obey the size of the length I want the cut. It always cuts the same size, regardless of the configuration I use, it always cuts to 245mm. Put some photos, how are my settings. Grateful in advance, if anyone can help me. Dover_roll_1-Motion-configuração_jog_manual.gx3
  4. I have an analog output card 1734-OE2V and there is in the fault/actions page parameters for program mode. What is program mode and when it is activated? Fault mode is clear but... Program should be written the value, but when this happens?
  5. FPWIN Pro 7 Help

    I am a novice trying to learn the instruction set to FPWIN Pro 7 for Panasonic PLC FP0H controller.   I am trying to use a rotary dial phone (Western Electric 500) to dial a certain 10 digits to unlock a normally locked electro magnetic lock for my son.   Does anyone know what the instruction program needed to perform this task. I have looked at the instructions: Pulse Relay Pulse Arc Center, and Pulse Target Value Match Set.  I do not know which one to use. Any ideas would be greatly appreciated. Thanks, William
  6. I am looking for how others have set up vertical axis motions using the Kinetix 5700 servo system. I have a 2 axis pick/place unit with a horizontal axis (X @ 2500mm) and vertical axis (Z @ 1200mm) that works as designed during normal operation. X axis has no holding brake and Z axis has a factory installed 24vdc to unlock brake. There is a GuardLogix L81ES control system that handles the safety and control. On pressing E-stop/opening Gates the vertical axis will stop the motion, apply the brake and hold with no problems. (2198-D032-ERS3 Drive, 2198-P031 Bus Power, MPL-B430P-MJ72AA X Axis, MPL-B330P-MJ74AA Z axis) The issue that I ran into was an accidental download of the program without activating the e-stop and the vertical axis dropped unexpectedly when entering program mode on the processor. I am aware that this instance was my fault as the programmer, however I am also concerned that this might occur again in the future if the controller ever enters fault mode or someone else completes a download. I have done some investigation with the "ProgrammedStopMode" parameter on this single motion axis and attempted all 5 options and the vertical axis still has a free fall drop for a second before the brake grabs hold - so evidently this is not working for me. (Page 24 of Vertical Load/Holding Brake manual - https://literature.rockwellautomatio...t003_-en-p.pdf) I am curious if there needs to be something done elsewhere as the X and Z axis are set up as coordinated axis? I also am unaware if I need to preform some action/parameter with the bus power supply for this? The current state of the machine as it sits now is preforming a MSF in manual mode after 5 seconds of inactivity or 30 seconds in auto mode. This axis is usually in demand every ~22 seconds. This will shut down the axis after preforming a brake test on the vertical load and seems to function OK, however it is still in the back of my mind the issues mentioned previously if we ever enter a controller fault while indexing. Thanks for your insight
  7. Hello everyone, I have a problem with packing machine. There are some issues with one of the axis, when axis actual position is near to 1800000 some error appear and operator has to turn off machine on main contactor. This axis is working in Linear mode. I think that rotary mode would be better for this axis. And here is my question. Which instructions, and what options i should change/check when i change count mode in axis's options. Can any1 point me some manuals to read or give me some advice ? Thank you in advance.  
  8. PLC occasionally going out of Run mode?

    Has anyone had an issue with Siemens plc's occasionally going out of run mode? I was doing some research and found that it could be due to a bad analog input. Is there a way to tell which input or output is causing this fault? I know I can create a hardware diagnostics error organization block but that only correct from what I've read.     Edit: I've added a screen shot of the diagnostics report. The fault that may be the problem is: Temporary CPU error: Serious firmware exception  CPU changes to DEFECTIVE mode (system reaction)  This plc / system was installed 2 year ago and we've had this problem occasionally since. I'm guessing the wrong firmware was used during the install. Will try upgrading firmware this weekend.   
  9. BECKHOFF CX-9020

    Hello PLC experts, I am master student currently writing thesis. For this, I have a initial task of making some changes to PLC program (Just started getting to know about PLCs- complete beginner). I have a BECKHOFF cx 9020 PLC connected to my notebook using ethernet. I am using TWINCAT 3.1 (VS) as IDE. Firstly, I cannot find my PLC IP address connected to my notebook . I added the route in the Twincat and it shows the PLC is connected. When, I am trying to run a program (activate boot project), I am unable to login to the PLC. It gives an error "login failed for application port 851". What I undertood from BECKHOFF scripts,  there is something wrong with the ADS ams net ID which I am trying to figure it out. I appreciate all the help. Thank you.
  10.  Hi all. I have a question about how to set up the motor in rotary mode. My application will be a basic rotary table driven by a servo motor without gearbox between. So, in my servo drive axis settings, I select the motor as a rotary mode. then I defined the maximum position setting value for 360 degrees, and minimum to 0. So far so good. But the problem comes when I want to make an absolute move using the mc_moveAbsolute to move 360 degrees. Whit this settings the error "target position settings out of range " will come up. So, what is the solution to rotate 360 degrees without generating this error? if I set up the maximum value to 361 degrees and then if I rotate 360 the error will not occur and the motor will rotate 360 degrees as I aspected, but it's this correct ? or there is another way to do it? Thanks  
  11. C-mode hostlink library for NJ/NX1P or CP1L

    Anyone knows if there is a C-mode hostlink library for NJ/NX ? Also, a C-mode hostlink library for CP1L could be helpful, to translate such a library to work with NX1P is probaly less work whan writing a new library.  Maybe Omron France has developed such a library? - they seem very active..   Background: Looking into writing a programmatic c-mode hostlink master for NX1P12, this is for connecting the handheld NSH5 HMI to the NX1P12 via RS232C using a CIF01. I have the hardware set up, and an machine built, expected some compatibility efforts by Omron.... but the NSH5 seems to talk C-mode hostlink, and the CIF01 only seems to support the FINS version hostlink.   On the NJ you can of course add an SCU module, thus not need a library.  But working with NX1 ( due to limited space available ), you are dependet on available CIF-modules which do not support C-mode hostlink.  
  12. Here is a link to a thread on a recent post showing how to communicate serially to an Omron PLC using VB.Net. This uses the Omron Host Link serial protocols. (C-Mode Commands) It will read 10 DM registers and display them on the form.   http://accautomation.ca/implementing-the-omron-host-link-protocol-vb-net/ Here is the source program that can be downloaded. Other links: VB6 Program: http://accautomation.ca/how-to-implement-the-omron-plc-host-link-protocol/ VBA Program: http://accautomation.ca/how-to-implement-the-omron-host-link-protocol-part-2-vba/ Regards, Garry www.accautomation.ca
  13. Hi, I have some trouble with a CJ2M-CPU33. My client did a backup to memory card earlier today, and after this we did some changes through remote link. Now the client wanted to restore the previous backup to the PLC and has done so, but the system would not function correctly. After going online on the PLC it seems like the PLC is stuck in "Stop/Programming Mode". When trying to change to "Monitor" or "Run" mode a dialog comes up containing the following message: "Failed to change the operating mode. The operating mode may be still changing in the PLC."  - All the dip switches are set to off after restoring backup - The PLC has been rebooted  - I have downloaded the application again through CX-programmer  - Verified that the PLC is set to start up in "Monitor mode" But nothing helps. The same message comes up when trying to change the operating mode.  Hoping anyone can help to resolve this issue as it is very critical for us and the client. In advance, thanks for any tips or help received. Best regards Stian
  14. Hello, I need to Synchronize two 4kW motors connected to their own individual AltiVar VSDs. To put it simply the two motors are pulling cables on a pulley and when loaded the motor's slip and the speed varies. I have an Omron CP1L-EM PLC and 2x Omron Rotary Encoders ( E6C2-CWZ5B encoders - 360 PPR) - connected to each motor,   What is the best way to read the pulses from the two rotary encoders then convert to RPM? 1) Using  PRV or PRV2(883) instruction,  - this would be the best option as it would convert the value to RPM - however, can I use this instruction on both Counter 0 & Counter 1? 2) Or read the raw value from  Counter 0:  A270 (connected to motor one's encoder) Counter 1: A272 (connected to motor two's encoder) Convert the pulses to RPM - then compare and adjust? 3) Or using CTBL. - is this a useful instruction for this application?   Once I get the RPM speed from each motor - I can then do a compare instruction - see if there is a mismatch and if so send a scaled analogue output to the VSDs to correct the speed if required. (10-50Hz) What would be your recommendations? any help would be most helpful. Thank you.
  15. Using Rotary Encoder

    Hello dear, may i need some help .. I want to use a rotary encoder for my CJ2M CPU32 , but i don't know what anything must i prepare for it. such as type slot for plc and what kind program for read pulse from rotary encoder ... Thanks before  
  16. Hello,  As the title indicates, we have a micrologix 1400 that has been installed for a long time.  Recently it faulted out on 71h and was in Remote Mode.  Do these PLCs revert to Remote Mode when in a fault condition?  We placed it back in Run Mode and everything worked fine, but how did it get to Remote Mode in the first place? Thanks,  J 
  17. Binary Mode vs BCD Mode

    Hi all, I have created a program using the binary counter and timer instructions and everything works fine (yay!), but I am not entirely sure if there is a major difference between using Binary mode or BCD Mode on the PLC. Does it just come down to personal preference or is there an advantage to using a particular mode over the other? Also, does the operating mode affect anything besides counter/timer? The option in CX-Programmer seems to indicate it doesn't. Cheers, Jay
  18. I got a CJ1M CPU11 that I can connect to but I can just go to run mode but when I try to switch to program mode I'm tell that I can modify the mode
  19. Dear Friends; Good day. First i install the windows  virtual xp mode on Windows 7 64 bit. After installation i installed the FTM, RSLINK,and rslogix 5.0 in virtual xp mode.  Then i activate the software by Factory talk manager and select the hard disk and for a single computer activation. This process successfully acomplished. But when i open the RSLOGIX it shows popup that activation path is not found. Then i again open the factory talk tool and note that there is no activation shows in current activate products, But the activation detail shows in the RE host tab. I re hosted the activation by using go to Rockwell site and message show successfully activation re hosted.   *** Now i am stuck here is i loss my activation?  *** in windows xp virtual mode how i activate my product that application find the correct path of activation file? ** In windows xp mode if i open my Computer there is shows other hard drive partition as well as Local disk C:\  and activation file save in virtual drive instead of real C drive in windows 7. But there is no file path option to save the activation. Its by default save on C:\documents and setting\all user\shared documents\rockwell\activation\*****   Please help me how i activate my product in windows XP mode successfully?  Thanking you. i will remain Regards  
  20. IPC 620-1536

    HI, there. I am new to the Honeywell PLC, usually dealing with AB or Omron. Need some help from the Honeywell PLC gurus, my the only one PLC IPC620-1536 , suddenly stop working. No "Run" light or any outputs are present. Turning the "Mode Key" to the "program mode" and back to the "run mode" doesn't make any difference. I attached couple photo. My question, is any other way to start PLC running again? If I purchase the Win.Loader and communication cable and connect to the PLC, can I change PLC back to "Run" mode and upload the program, or fail to change the Mode using the Key. means the same fail using the software? Please update. Thanks for advance, 
  21. Hi! I have my 1756 IF8 wired in high speed differential mode but i can't configure the RTS smaller than 11 ms. What I understand it should be possible to set as low as 5 ms if module filter setting is 1000 Hz. Is there anything else that i have to do?
  22. project or PLC mode

    Hi, I keep getting an error that project is in binary mode and plc is in BCD mode.  Wont let me change either. I must be trying in the wrong place...please point me to where i can change this in the PLC.   I am getting an error in my RXDU with a Honeywell barcode reader, on one machine, I am thinking it is related.   thanks for any help. 
  23. Auto Run Mode after Reboot

    Hi guys! Im new in using PLC and im using CPM1A, is there a way setup the plc to run mode immediately after rebooting it, also even without connecting it to PC or handheld device? I saw in the manual "Startup Operating Module" but i am lost, i dont know how to configure it. Thanks for your advice.
  24. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  25. Rotary input device

    I am looking for some sort of rotary input device which could be used for fine adjustment. Ideally it would have to two output pins, if turned clockwise it would send pulses on one of the pins and when turned counterclockwise it would sent pulses on the other pin. These could be connected to two inputs on PLC and a value in a given variable could be incremented and decremented depending on the direction of rotation. Almost like using potentiometer with analog signal. I guess if I can not find anything I could use incremental encoder and look at the phase of the output to decide which way it is being turned but hopefully simpler and maybe more cost effective solution is out there? Thanks.