Search the Community

Showing results for tags 'panelview plus 1000'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 56 results

  1. I have an old PanelView 1000 catalog number 2711-K10G1 that needs to be replaced, I don't want to replace it with another panel view 1000, I want to get a panelview plus, the problem is that the Panelview is connected to a PLC-5 and it's connected by DH+. The only thing I can think of is to use an 1761-NET-ENI to connect the PLC-5 to ethernet/IP...but even the ENIs are discontinued by Allen Bradley. Are there any panel views that have data highway? 
  2. Looking for PanelView suggestions

    I have a customer that insists on me using a panelview for his project and I have basically no experience with them. I have been using another brand exclusively for many years so I'm well versed in how to use an HMI, just not Allen Bradley. I'm hoping to get some advice about which unit to use. The system is a simple waste water facility and the controller will likely be a micrologix 1400. The customer wants something in the 15" range. Looking on the AB website I see Plus 6 & Plus 7 both seem to give me that size. Are major differences that I should know about? thanks     
  3. Hello I would like to first let everyone know I am new to the world of troubleshooting or programming plc's . What we have is a SLC500 system that is connected to a Panelview 1000 HMI via the DH+ network. The issue we have is the panelview displays a gate that is suppose to be closed at as gate fault. When i connect to the plc the ladder rung shows that the gate is closed. To show various positions of the gate the programmer used N13:70 as gate opened and N13:71 as gate faulted and N13:72 as gate closed. When i checked the logic it showed the bit N13:72 as engaged or true if you will. This logic is in the ladder rung that is labeled PV Status which i take is the status the HMI reads so my question is why does it show GF when it should be reading GC. Ive searched all through the logic and it doesnt appear to be wrong here is the logic the best I can simulate it  ladder 6 rung  53  instruction is  XIC O:13.0/11 and OTE N13:76/0 (Gate Open ) and the branch is XIC I:5.0/11and OTE N13:76/1 (Gate Fault) next branch is XIC N13:3/11 and OTE N13:76/2 (Gate Closed which this section is green or highlighted or true which ever you like) when i looked at the input XIC N13:3/11 this is what I found is that this XIC is on ladder four rung10 and has the following XIC T4:154/DN and branchoff that is XIC I:5.0/11(gate opened)XIC I:6.0/11(gate closed) which these two inputs are false or not lighted the output is OTL N13:3/11 and it is true which makes the previous rung true showing the gate closed. So why is the panelview showing the wrong position. I even went as far as resetting the HMI and the PLC so if anyone has a helpful hint I would greatly appreciate it.
  4. details: panelview (2711P-RDT15C) connected to "switch A" (ntron p/n: F-716TX) "processor A " (1756-L62) is connected to "switch A" "processor B" (1756-L73S) is connected to "switch B" (ntron p/n: F-716TX) "switch B" is connected to "switch A" I'm trying to use a single panelview to communicate to 2 separate PLC processors (separate chassis). When I go to add the shortcut in factory talk I find the "processor B". When I connect my laptop to  "switch A" I can see every thing in RSlinxs.  Any one experience this issue or know how to make this setup work? Maybe there's a switch setting that is not allowing RSlinxs enterprise in the PV to see both processors? 
  5. HMI panel view plus 600

    Hello, my AB HMI panel view plus 600, when I power it only the comm green light comes on, the touch screen does not come on, any help I will appreciate thanks. 
  6. I have a Panelview model 2711-T5A20L1 that the IT Dept. tells me has SNMP Protocol active. They want it turned off. Is it possible, does the device need this protocol? If it's possible to turn it off, how? I have search the knowledge base on AB.com and found nothing. I have done a search of PDF manual for "SNMP" and turned no results.
  7. Uploading from Panelview 600

    I am trying to upload program from panelview 600 with a windows xp pc using true serial port. The HMI has device net and rs232 port I am using straight rs232. Is there any set up or can i upload from the memory card attached to hmi. The HMI has a glare and display is not visible, we are trying to upgrade to panelview plus. Thanks  Model 2711-B6C10x FRN 4.48
  8. mitsubishi nexgenie plc target settings View File This target setting files are used with codesys software for programming mitsubishi nexgeine PLC series,    Submitter lionheart86 Submitted 01/18/17 Category Demo Software
  9. I have some old Panelview plus displays (version5) that are not being used.  I would like to set them up to communicate with some version 30 PLCs for some basic indication (nothing important).  I know the hardware version won't support it communicating in the standard way, but has anybody been able to set up generic communication for something like this.  I hate for the displays to go to waste, but AB will just tell me to buy a new display.  I figure there has to be a way to communicate to the display with MSG statements or something.  This isn't for a specific project, just trying to not watse displays that we have.   Thanks.
  10. Does anyone know a way to convert GOT 2000 screens to a GOT 1000? 
  11. Cable pin configuration required.

    Required cable PIN configuration for Nexgen 1000 series PLC, MS-40M-E, NT11-SF121B-EV1 , GT1020-LBD.  
  12. Dear all, i have using nexgenie 1000 cpu for my new project. but i am not able to connect with codesys v2.3 . I have installed target file T1.4 and T2.4. trie with both. Now i have doubt with communication cable. I have used standard RS232 Cable with 5and 8 Pin short. Kindly suggest the correct one. Thanks in advance
  13. I got into a project were they have 20 panelviews plus 1500 around the building, and they want to be able to serrate the displays accessible by the users based on the physical location of the panelview, for example Room1 should not see room2 but can see room3, at this moment we have a complete application with all the screens that have been downloaded to all panelviews, in order to avoid maintain 20 different ME applications I would like to ask if any of you had this problem before or any ideas on how to go forward with it.   Thanks
  14. How to connect Micrologix 1000 With Weintek MT6070ip HMI? i Can't connect my Allen Bradley Micrologix 1000 With Weintek HMI...
  15. Hey, this is probably a stupid question, but how do I delete old FactoryTalk View Programs. They are the ones that I have uploaded from a PanelView Plus via the "Transfer Utility" and then restored runtime using the "Application Manager". I open up FactoryTalk View Studio and I can see a list of all the runtime applications or I can create a new one. My question is, where are these applications stored by default? I have a bunch of old ones and test programs that I want to delete that are just cluttering up my list. I attached a screenshot to show you exactly what I'm talking about. Thanks, I'm sure this is a pretty easy/ dumb question. Howard
  16. SLC 5/03 AND EZ3 TOUCHSCREEN

    A couple of mounths back a posted about the need to replace a no longer available panelview550. I got allot of good feedback and decided to go with a panel from EZ automation and the DH485 network protocall. Last week I installed my new EZ3 touchscreen and debugged over a couple of days, Overall I am happy with the product and the operators seam to like it (the graphics are allot bigger and in color).  I wonder if the EZ automation screen will last 17 years like the Panelview? I am down to 1 problem that i have not been able to resolve, the machines have parts counters on them that display the  number of parts produced since they where last reset. I am using C5:00.acc and so forth for the display tags and reseting with a B:3 bit. The parts counters count and reset like they should but the problem is that they do not retain the count totals when the power is turned off at the end of shift. Looking for advice on making a retenative timer
  17. Hi there, I'm wanting to connect a panelview 800 to an SLC5/03 the SLC is connected to an 1747-AIC which is run to another 1747-AIC. I'm trying to figure out what cable I require to connect the peripheral of the second AIC module to the panelview. I can't seem to find any reference online. Any help would be appreciated. Image attached to clarify.    
  18. I'm trying to connect a 2711-K5A8L1 FRN 3.13 PanelView 550 (DH+ three wire connector) to a 1747-L553 SER C REV C (RS232 and ENET). I read that I may need FRN 3.3 on the PanelView 550 to do a passthrough. This will be a dedicated connection with no other devices. The PanelView 550 has only the three wire DH+ connector and an RS232 printer port. I was trying to connect PanelBuilder 32 to the RS232 port and may only have PRINT and DOWNLOAD capability on this port. Is there an inexpensive way to connect the PanelView 550 and the PLC CPU? Something like the 1761-NET-AIC would be fine, but I did not see an option for DH+  .
  19. Hello I downloaded a .mer file on the Panel view 1000 but it shows errors on the display graphics. i have configured the Rslinx communication several times by selecting the rigt PLC in Design and Runtime mode. I am using Facotry Talk view 8.20 and creating 5.10 runtime file. Please advice. I was able to correctly download and use the HMI on a similar machine. I dont know what am I missing on this one.    Thanks Pratik Jain
  20. We've purchased an Autoclave at auction with CompactLogix L32e and PanelView Plus 1000.  With the help of some forum members and a local engineering company we have the machine finally working! I'm looking for some advise as to how to train users for standerd operation.  For example:  Their is a toggle switch on the front which powers on everything (PanelView, processer, switch, etc).  We close at 5pm each night.. Should we Power down the machine each night, or leave it on? Another user mentioned a battery and I was a bit confused with the manual. With the machine off, Is the PLC only holding the program because of the battery?? I have backups of the following.. (.acd, .apa, .mer) files.  I also have created a Disc Image of the Internal Flash card on the PanelView.  Is their anything else I should have a backup of? Their is a CF card in the PLC.  It has a folder called "Logix" and one called "System Volume Information"  In the Logix folder is  a CurrentApp folder with a .bin and .p5k file.  Does anyone know what exactly these are doing?? Any other advise is greatly appreciated.  Thanks so much for your time.
  21. CVS file log not generated.

    Hi guys, Yesterday I posted a question about how to create a trigger for a log. Now I have the next problem. I created my log, loaded the Logging firmware on the GOT but the CVS file is not generated. Can someone tell me what i'm doing wrong? I am attaching all the settings and the PLC part of the program. I want the values of ZR1200 ZR1204 and ZR1205 every time they change. They are recipe values. I tried also putting a button to create the log file on the HMI. Did not work.  
  22. Find password from .mer or .apa

    We have a sterilizer w/ Allen Bradley controls which we bought at auction.  It has a panelview plus 1000.  It came with a CD containing .mer and .apa files.  I was able to load the .mer file via the configuration screen by using the external CF card.  When I run the application, their is a login button in the bottom right which when pushed brings up a user/password screen.  We do not know the user/password for this.  Is it possible to find the password by somehow reviewing the files.  We do not have any software, and do not want to make any changes to the program (rather than changing the password).  I've attached the files in case anyone can help. Also, was i correct to load the .mer file??  or should I be using the .apa?  I followed these instructions here. http://www.judiwa.com/2010/10/05/how-to-copy-panelview-plus-application-with-compact-flash-card/ Thanks for your time PA1525_PVP1000.mer PA1525_PVP1000.apa
  23.  I am a begiiner at this so please bear with me. Recently we replaced a HMI that had gone out and we upgraded to a fairly newer version our old unit was a PanelView 600 and we upgraded to a PanelView Plus 700. I thought the process was going to be straight forward just swap and go boy was I mistaken not only was the panel a upgrade but we had to get new editing software. So I took the pba. file and converted it to a Factory Talk mer. file I thought I had completed the task after converting the file I got the following messages. Screen 1 - RECEIVING: Message display object will be converted to Multistate Indicator object at (226, 63). Screen 1 - RECEIVING: Message display object will be converted to Multistate Indicator object at (140, 35). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (80, 30). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (226, 0). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (0, 120). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (0, 0). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (300, 120). Screen 2 - LOAD OUT: Message display object will be converted to Multistate Indicator object at (273, 120). So I continued with the file and then I went to the communications section and selected the target area and because we are using DH+ communications we installed a communication module to the panel and installed a resistor  as directed in the AB instructions. Now back to the software I selected the target area and added a driver for the DH+ then selected the DH+ and added another driver this time I selected the SLC 5/04 1747 L541. Then I went to the the shorcut area and added a shortcut to what I believe is the PLC we are connecting to then selected the driver and selected apply then I went and created a runtime application and saved it to a usb device and loaded it on to the panelview plus and when it runs all the tags show a erro such as the picture shows I uploaded I cant decide if it is a missing communication driver or a error in the programming would love to hear your thoughts on the issues. Thanks everyone for any posts you have  
  24. Comunication HMI and PLC 5

    Hello every people, I am working in to project with one PV Plus 1000 (2711P-B10C4A1 with Logic Module 2711P-RP1A), one KF2 and PLC 5/15, I have finish logic of PV 1000 and PLC 5, but the communication not good , this is the configuration made:       NODOS PLC 5/15 have address nodo 11 KF2 have address nodo 60 PV Plus 1000 have address nodo 0 PINOUT CABLE  DB9 (PLC) -- DB15 (KF2) 1--5--7  --->   8--6--7 DB9 (PV 1000) -- DB25  (KF2) 2--5--3   -----------------> 2--7--3 I wait for your help   Thank you         
  25. Hello, I am currently installing a PLC control panel and due to space constraints, we will need to install the Panelview 600 HMI separate from the Micrologix. We purchased a 50ft Allen Bradley communication cable, but 50ft will not be long enough. We have about 70 to 75ft of conduit between the panel and the HMI. I would like to know what options we have for this connection. I read that for serial connection, we shouldn't go past 50ft. I understand the Micrologix 1100 has an ethernet connection and the Panelview does as well, but I'm not sure what changes would be needed in order to communicate through the ethernet port, instead of the RS-232 port. Any suggestions will be greatly appreciated.   Thanks, JCG