Search the Community

Showing results for tags 'omron plc analog value read with vb with fins udp ethernet connection'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 855 results

  1. CP2E Modbus RTU Slave

    Hi, I would like to know CP2E have any modbus rtu slave function block. CP2E with add on CP1W-CIF12
  2. Hello everyone I'm new to omron plc . I have a system which consists  1. Omron Plc CP2E 2. Two stepper motors and their drivers.  3. 4 Inputs-  one stepper start push button, second stepper go back push button, third stepper 1 home sensor, fourth stepper 2 home sensor 4. 4 Outputs- stepper 1 step(-) Q 100.00, stepper 1 dir(-) Q100. 02, stepper 2 step(-) Q100. 01, stepper 2 dir(-) Q100. 03 Seuence is like that:- Initially both stepper motors are at their home sensor.  When start push button is pressed both stepper move 110 mm distance and then stop.  Now when go back push button is pressed both stepper motors should go back to their home sensors and should stop at reaching their hone sensors.  This is the sequence. Can someone please send me the program by writing in cx - programmer or upload the photos of ladder program and settings also. Please
  3. I have a bit of an issue with communication between GOT1000 HMI (I think the exact model is GOT1675V) and Q03UDE PLC over Ethernet. The GOT is set to 192.168.1.4 and PLC is set to 192.168.1.2 but I get the error "Communication Error. Refer to System Alarm in Utility Menu". Now how do I access the utility menu? I have tried to tap and hold on the upper corners of the HMI but nothing happens. I also can not switch between screens when I press buttons even though they are directly linked via screen #. Almost like the HMI froze up. Wonder if anyone had similar issue and what the solution might be. Thanks for your help.
  4. I recently wrote a simple java driver to communicate with Omron devices (CJ1 and CJ2) via the FINS protocol over UDP. I've installed this software at a number of my client's sites and it works well most of the time. However, I've encountered a number of instances where a CJ1 device will consistently return what looks like a valid response but every memory register I request will return zero. I've deployed the software to 5 sites with identical configurations. The sites have one CJ2 device and one CJ1 device.  The CJ2 devices work exactly as expected. Three of the CJ1 devices work exactly as expected but the other two have this issue where every value is zero all of the time.  This issue is not intermittent at those sites - I have never had it return anything other than a zero for any memory register for a CJ1 device at those two sites. Example: TX: [80, 00, 02, 00, 0a, 00, 00, c9, 00, ff, 01, 01, 98, 00, 00, 00, 00, 64] RX: [c0, 00, 02, 00, c9, 00, 00, 0a, 00, ff, 01, 01, 21, 08, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00]  
  5. Hi, I have a project including 32 digital outputs, 8 Pt100 probes, 4 thermocouples, and 4 analog inputs so I have to choose an OMRON PLC. The supplier in my country has only CP2E and CP1E PLCs. Is there a way to connect more than three expansion modules to the PLC? On the website is stated that the maximum number of expansion units is 3, if the answer is no, is there a solution to this problem? Thank you
  6. I'm working on a program where I manipulate REAL numbers in Sysmac studio using an NX1029020 PLC. My problem is I am new to automation and I don´t know how to display those numbers when connecting to an NB HMI. I´m trying to send the data to a bar picture and a number display. My question is which AT Specification Attribute should I assign to my variables in Sysmac Studio and their corresponding Area in NB-Designer? I tried using the DM area but it didn't show numbers on the displays, only shows *****. Should I convert my real variables in Sysmac first? Or how can I keep decimal numbers and then display them? My current configuration in Sysmac: Name Data type AT Network publish ST1 REAL %D5 Publish Only ST2 REAL %D3 Publish Only My current configuration in NB-Designer Bar Picture Addr. Type D Address 3 Code type BIN Number Display Addr. Type D Address 3 Code type BIN Data type Float Integer 4 Decimal 2
  7. Hi, I have a problem with Omron PLC and Beckhoff IO. The IO just disconnects in a few minutes and comes back! I received different errors: Link off error, Illegal slave disconnection, process data reception timeout. When I also check "Display Diagnosis/Statistics information" I see errors on all ports A and B of all nodes.  I have called and talked to both Beckhoff and Omron.  I have two NX1 and one NJ101 to test. And I have three EP2318-0001. I have the same problem with all the PLCs and EP boxes. It does not matter if I have one, two, or three nodes. I have tried different revisions of the EP2xxx from the XML file, different settings for the slave, different task periods, and the error still is persisting.
  8. Im trying to integrate the Omron Nx-ID3444 terminal with the TwinCAT software via EtherCAT, connecting the teminal to a ECC-202 coupler and it to a PC runing TwinCAT, the problems come when using the terminal timestamp whrn the digital input change. The bit input change is detected perfectly but the timestamp corresponding to said bit is always 0, I've been talking to Beckhoff and they tell me that the descriptors on their web might not be in the last version, have you experienced anything similar? I link the files for you to compare https://assets.omron.eu/downloads/ddf/en/v6/omron_nx-ecc20x_ethercat_esi_file_en.zip
  9. LOGO For Excel

    Version 1.0.0

    22 downloads

    LOGO For Excel allows you to retrieve, view, log and write data to one or more Siemens LAN connected LOGO! 8 basic modules using Microsoft Excel without the need of a touchpanel or any other hardware or driver. Configure in no time Excel spreadsheets that contains live LOGO! data.
  10. View File LOGO For Excel LOGO For Excel allows you to retrieve, view, log and write data to one or more Siemens LAN connected LOGO! 8 basic modules using Microsoft Excel without the need of a touchpanel or any other hardware or driver. Configure in no time Excel spreadsheets that contains live LOGO! data. Submitter progpro Submitted 03/25/22 Category Demo Software
  11. This is a machine with a CQM1 PLC and a NT31C HMI. Battery of the HMI run out and the HMI program was lost. I got the PLC program and identified some of the memory locations, can use the machine but not fully. Omron is not my thing so I am looking for some help to identify program functionality. some sequencer functionality and a servo, not many I/O's. The entry from the HMI is converted and has some math maybe to address the 16bit limitation, not sure. Is a home made machine and the original controls contractor cannot be located.
  12. CP1W AD041

    Hi.. I have a problem with my analog CP1W AD041, it's reading value always "0". Can someone help me to configure software setting? I use PLC CP1E-N60SDT-D Thank you        
  13. MX2 Modbus doubt

    Hi there! I'm programming a CP1L-E CPU to control 3 3G3MX2 inverters via Modbus. It got some things right, like the INV002_Refresh_X31 block and its parameters. The thing is, I also want to read some parameters from the inverter using the INV206_ReadParameter block. My doubt is, do I need to be careful so both blocks don't execute at the same time and use the serial port at the same time? Is it better to use one INV206_ReadParameter block for each parameter I want to read? Thanks in advance!
  14. Omron 1S Servo

    Hello:           Does anyone know the details explanation of the Homing Settings for the Axis? Set the homing operation. 0: Proximity reverse turn/home proximity input OFF 1: Proximity reverse turn/home proximity input ON 4: Home proximity input OFF 5: Home proximity input ON 8: Limit input OFF 9: Proximity reverse turn/home input mask distance 11: Limit inputs only 12: Proximity reverse turn/holding time 13: No home proximity input/holding home input   Limit Input referring to Input (I/O) ? How about Proximity Input ? It is confusing with the terms. The manual has no explanation for each of the above selection.   Any one?   Simon
  15. Hi! I would like to ask your help. I want to know more about the communcation systems what allen bradley use. Most important for me, is Ethernet IP communication, Controlnet communication, Sercos (servo) communication, maybe devicenet communication.  I know I can find some manulas on the web, but I thought I ask it here too, maybe you guys have some more documents which is contain more information. Every information is highly appreciated. Thank you very much guys.  
  16. mx2 control with modbus

    Hi all im back to trying to get my inverter to work but this time with modbus, from this post http://forums.mrplc.com/index.php?/topic/38445-controlling-mx2-inverter-without-modbus/ and im stumped, im sure its just one thing somewhere messing it up i have a cp1l-el20 with a cp1w-cif11 and a 3g3mx2 inverter and am attempting to control it via modbus, it is wired up as follows, sp+ to RDB+, sn- to RDA-, common to the plc pin and plc output pin 100.00 to logic input 1. im using 100.00 to put it into run mode the paremeters ive put in are a1=3,a2=1, a4=50, c070=3, c071=5,c072=1, c074=00, c075=1, b27=1. im using MOV to set my speed to d1001 attached is my inv002_refresh x31 fb thanks to any1 who can see my silly mistake    
  17. Hi. I use the email block on few of our NJ101-9020 controllers to send out daily reports or any status updates. Recently the PLC's started an unknown issue and fails to send email out anymore. I use the Mail_Send function block from Omron to send emails. The only Error ID i can get is 2005, with status being "Connection to SMTP" failed. Looking at the troubleshooting guide, i cannot find anything to do with error id 2005, in fact its missing. There is 2004 and 2006 but no 2005. I've tried all the obvious thing like, power cycle, redownload the whole project, create a new instance of Mail_Send function block etc. Nothing seems to have fixed this unknown issue. Our IT department did a full check on their side and nothing seems to be out of order. I can still remote into the PLC, so i dont know what exactly is the problem. Has anyone came across this error ID before? Any ideas why this might have been happening? It was working well until few weeks ago and nothing changed and this suddenly started. Any input is really appreciated. Thank you.
  18. unit of time in D8284

    Hello PLCmaniaccccssss, What is the unit of time in 'average time for the channel -1' (D8284) while programming for analog inputs? I have moved k10 to D8284 in my program in gxworks 2, does that mean the time average will be taken for 1Sec or 10msec or any other time unit??? I require this to eliminate the flickering of the input from the load cell transmitter. Thanks and God bless!!!
  19. We have an SLC 5/05 on our automation network, one of several SLC 5/05 processors on site.  It functions perfectly well and no ethernet messaging issues or SCADA drop outs.  The difficulty I am experiencing with it is when I am required to fault diagnose it takes a very long time to get online to it with our laptop running RSLogix500.  It sometimes takes as long as 10 minutes.  It makes no difference whether I use the Ethernet devices or the EtherNet/IP Driver in RSLinx, it nearly always takes an age which is frustrating in a breakdown situation.  I don't ever experience these long wait times connecting to any other of the SLC 5/05 controllers or any other controllers for that matter.  Once I am connected to the problematic controller I don't experience any issues, it's just the initial time getting online.  I try to leave the laptop permanently connected to it to avoid the long wait time to connect.  When I open RSLogix500, select Comms, Who Active Go Online, Ethernet devices driver, I can see that the problematic 5/05 has Active as its Status whereas the other 5/05 processors have Remote Run as their status.  Please can anyone advise as to any possible program parameters, RSLinx settings or hardware faults I should be looking for?  I have considered it could be a network problem but I'm unsure about this given how the processor performs well in every other regard. Neil
  20. Hello everyone    I am working on modbus TCP protocols to communicate between SEW drive and Omron PLC CP1L-EM. I am following modbus TCP function block from Omron, But i have updated that block because of is not fit to SEW modbus communication. Currently, I am sending a control work to SEW but I am getting error on Modbus TCP from SEW drive, which is invalid data. So I am looking your help is you work with SEW drive before and communicate over modbus, then please let me know how to make a data string for read and write (SEW Drive function 23). I am using 3PD data structure.    Thank you
  21. From Allen Bradley New to Omron

    Im used to Allen Bradley. How do I get online with Omron in a way i can use steps to remember
  22. Hi I am looking for a way to read and write data from PLC omron words, bits via FINS or EtherNet/IP protocol using python programming lang. Does anyone have any results in this? I really want to see your work, because all my attempts have failed. Thanks.
  23. Hello all,  I have a temperature sensor with a reading range of 10F to 212 . The input card I am using is an Allen Bradley 1734 IE8C 8 Channel Analog current input. The current input values are 4-20 mA. Currently I have my raw low at 4000 and raw high at 20000. Can anyone explain how do we go about selection of this values ? I found these values in the configuration tag of the input card properties.  Thank You 
  24. cj2m

    hi i am wrting an essay about my final project , i created a scada for omron plc (CJ2M) in factory . ( i am a computer data student )  the thing is , i can't find a good and an easy  documentation ( not the CJ2M datasheet ) to talk about the CJ2M component (port and stuff like that) any help please ?   
  25. Hello guys I am a beginner in FINS TCP communication and I am trying to do a FINS TCP communication between an omron PLC CP1L-E in client mode to communicate with my PC that is in server mode, I am using the SocketTest v3.0.0 program that is in listening mode and still was unable to receive any information from the CLP, can you help me? The program and some images of the simulation are attached Thanks for reading SERVER PC IP ADDRESS 192.168.15.160 CLIENT PLC IP ADDRESS 192.168.15.10 tcp socket_vms.cxp