Search the Community

Showing results for tags 'nexgen 1000 series plc ms-40m-e'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 70 results

  1. Does anyone have the User Manual for the Modicon Plus 1000? Trying to program a "ReadOut" template to show the value of a PLC-5 Integer file. Keeps saying that the "N" is not a valid file type. I've done this on the Cutler-Hammer PM1000. The Modicon will not allow the C-H program to download, says it's not a C-H product. Thankx in advance for any help
  2. A1S68DAV parameter

    please can anyone tell me how to set A1S68DAV analog output module parameters , such as voltage output and resolution? or is the parameter can't be set at aLL (ie, fixed at -10V to 10V)?
  3. Hi everyone; I want to communication Omron NB series HMI with Allen Bradley Micro 830 PLC. I don't know is it possible. İf its that possible, help me please..
  4. Hello I would like to first let everyone know I am new to the world of troubleshooting or programming plc's . What we have is a SLC500 system that is connected to a Panelview 1000 HMI via the DH+ network. The issue we have is the panelview displays a gate that is suppose to be closed at as gate fault. When i connect to the plc the ladder rung shows that the gate is closed. To show various positions of the gate the programmer used N13:70 as gate opened and N13:71 as gate faulted and N13:72 as gate closed. When i checked the logic it showed the bit N13:72 as engaged or true if you will. This logic is in the ladder rung that is labeled PV Status which i take is the status the HMI reads so my question is why does it show GF when it should be reading GC. Ive searched all through the logic and it doesnt appear to be wrong here is the logic the best I can simulate it  ladder 6 rung  53  instruction is  XIC O:13.0/11 and OTE N13:76/0 (Gate Open ) and the branch is XIC I:5.0/11and OTE N13:76/1 (Gate Fault) next branch is XIC N13:3/11 and OTE N13:76/2 (Gate Closed which this section is green or highlighted or true which ever you like) when i looked at the input XIC N13:3/11 this is what I found is that this XIC is on ladder four rung10 and has the following XIC T4:154/DN and branchoff that is XIC I:5.0/11(gate opened)XIC I:6.0/11(gate closed) which these two inputs are false or not lighted the output is OTL N13:3/11 and it is true which makes the previous rung true showing the gate closed. So why is the panelview showing the wrong position. I even went as far as resetting the HMI and the PLC so if anyone has a helpful hint I would greatly appreciate it.
  5. Device point error between Parameter and PLC

    Hello all, I am a beginner with PLCs programming. I have an issue on GX Developer programming software from Melsoft trying to program my Mitsubishi Q-series PLC. CPU is Q03UDCPU. When the program is written and I try to upload it to the PLC, with the write to PLC window, I check -Program -- MAIN and -Prameter -- PLC/Network/Remote, click EXECUTE and a message appears : "Device point that is set in parameter is not match the device point in PLC". I can't fix it. In Parameter - PLC Parameter - Q parameter setting (window) - I/O assignment tab : I have (see image). Whe I use CHECK button it says there is no error. The X41 input device is plugged on slot 1/00. I am making this folowing the instructions a PDF I found on the Mitsubishi electric's wesite : Q-series basic course (for GX Developer). Thanks for the help, A. S.
  6. Hey everyone! New member here, and this site has always been a big help!  I try to help other folks too, but a lot of guys are super quick on here.   I've got a problem using some obscure components. I inherited a sensor network at work that uses Panasonic S-Link and I need to read them from a Q-Series. Panasonic makes a module that slots into the Q Series called an SL-VMEL-Q that I have.   My question is:  Did I do everything correctly on my Mitsubishi side? I put it into the parameters as an intelligent module with 64 points and I put the correct address in for the start I/O. Is that all I have to do?  This is the first time I used a module that wasn't on the drop down list when you add one in GX Works 2.   I can read and write to the buffer memory, but I can't get the unit to send to or receive from the sensors. I think the problem is that there is no end unit on the S-Link line (I don't know if it's just a terminating resistor or what), but it previously worked without one, so I can't be certain.
  7. Dear sir, i want sample program for modbus tcp for q series plc
  8. Hi everyone,  I am trying to use Kepware to communicate with my PLC setup which is the iQ-R Series R08PCPU.  I read the documentation which is available at https://www.kepware.com/getattachment/3daf1ac3-5c76-49ce-bbfe-f0fb1015f6cc/mitsubishi-ethernet-manual.pdf I read through the setup for Kepware and the setup procedure for iQ-R series but it still didn't work.  From the documentation, it said something about "using special ladder logic to enable ethernet communications is required.", I couldn't find anything about this online.  Here what I did in addition to the documentation: - Enabled IP Packet Transfer - Ping the PLC's IP Address which was successful Does anyone have any idea what I didn't do to establish that communication between Kepware and R08PCPU?  Thank you in advance. 
  9. mitsubishi nexgenie plc target settings View File This target setting files are used with codesys software for programming mitsubishi nexgeine PLC series,    Submitter lionheart86 Submitted 01/18/17 Category Demo Software
  10. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  11. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  12. Fuji Wsz plc

    Please send Fuji Wsz plc software download link  
  13. Does anyone know a way to convert GOT 2000 screens to a GOT 1000? 
  14. Cable pin configuration required.

    Required cable PIN configuration for Nexgen 1000 series PLC, MS-40M-E, NT11-SF121B-EV1 , GT1020-LBD.  
  15. Dear all, i have using nexgenie 1000 cpu for my new project. but i am not able to connect with codesys v2.3 . I have installed target file T1.4 and T2.4. trie with both. Now i have doubt with communication cable. I have used standard RS232 Cable with 5and 8 Pin short. Kindly suggest the correct one. Thanks in advance
  16. How to connect Micrologix 1000 With Weintek MT6070ip HMI? i Can't connect my Allen Bradley Micrologix 1000 With Weintek HMI...
  17. GX Works2 Q Series TCP issues

    Hey guys, been looking around for a solution and I was brought here.  I'm a programmer at a place that just put in a bunch of these Mitsubishi Q series QJ71e71-100 ethernet controllers.  I wrote a TCP server in Java to try and talk to them.  I'm trying to get data sent over from a little GOT1000 test terminal.  The zp.open command is working fine and i'm seeing a good syn-ack handshake, and if i push some text to the plc from the program I get a response (even if it is always the same nonsense).  but when i try to use the zp.send it fails, I get error C1A6 on the ladder program and the q series lights up the comm error light.  I know I'm being super vague here, I was just hoping to gain some insight.  I don't much know what to expect from this forum if you guys are active or if my question even has an answer but i've been banging my head against the wall for days now.  I'm just using a tutorial program from the q series manual and a super basic tcp handler in java.  If there's any other information I can provide let me know.
  18. I'm having trouble in finding a complete manual instruction and set-up on setting up a communication on a Q-series PLC to a inverter a700/a800 via RS-485. I have a manual for fx series, are the parameters the same as the fx series? how about the program, like  starting or stopping the motor? Are they same or not? In the Q-series, do i leave switch-5 "station no. setting" blank? i just started this so i hope that i can make this work after new year. This is the manual for the fx-series plc====> http://www.automationsystemsandcontrols.net.au/PDF%27s%20Mitsubishi/Manuals/FPLC/FX%20SERIES%20USER%27S%20MANUAL%20-%20Data%20Communication%20Edition.pdf   PS: I'm mostly self study because i don't have proper training yet and my school sucks.
  19. edit comment directly from got

    hello everyone using gt designer 3, got 2000 series and IQ-R series want confirm something. it`s possible to edit comment group (that use for history, fault,etc)  directly on GOT using GOT tool or object or script? for script, searching on gs, gd list but find nothing. where the comment group is saved? thank you  
  20. Version 1.4.0

    26 downloads

    This is a custom template created for nb7w tw01b HMI. hope someone finds it useful. If you want to create custom templates for NB series hmi feel free to ask me. Cheers.
  21. View File Template for NB series hmi NB7W_TW01B This is a custom template created for nb7w tw01b HMI. hope someone finds it useful. If you want to create custom templates for NB series hmi feel free to ask me. Cheers. Submitter Aneesh Submitted 10/27/17 Category Other Omron Products
  22. Hello, Everyone . Do anyone has experience in FX1N-232-BD connect to GT11 (or other model) from Panasonic ? I try to connect them via RS232 port and I setup parameter following HMI manual but It doesn't work at all only RX led on 232-BD blinking Any suggestion ?    Matcha IMG_39346964.MOV
  23. View File GE SRTP Ethernet Driver for .NET .NET Component for use in Visual Studio.NET to create HMI/SCADA apps that communicate with GE SRTP devices via Ethernet. Supports PACSystems, Series 90, and VersaMax.   Supports PACSystems symbolic variables and CPU rack + slot specification. Does not require 3rd party drivers Does not require OPC x86, x64, and Any CPU compatible Visual Studio.NET 2005, 2008, 2010, 2012, and 2013 Compatible Most .NET targets are supported, including Web, Win Forms, WPF, console, and service apps. Build Windows Forms, console, and ASP.NET applications that run on Linux with Mono framework. Extremely high performance - 5~10 mSec typical transaction time Optimizes multiple register configurations into minimal transactions Tag database can be configured via code or visual designer Abstract base classes allow you to write generic code that works with all drivers Synchronous and asynchronous read/write methods Data change notifications Provides common user interface across all driver classes No limit on number of devices or data points Multi-threaded for high data throughput Includes extensive help system Windows, Console, and Web Example applications with VB and C# source code included. Easily connect office systems to factory floor. Free 30 day fully functioning trial version available for download Runtime-free for qualified applications   Submitter Automated Solutions Submitted 05/09/09 Category Demo Software
  24. HMI not recognized via PC

    I am trying to connect HMI( GS Series) to Laptop but every time it says " Device not recognized ".  Tried changing the port, Laptop, whole HMI.  It was working for 2-3 times after installation of new software( both Windows and GX Designer). Tries uninstalling and installing GX designer. Pls help.
  25. Hi Everyone! I try to read Analog Data in PLC Master through Salve Module (ECT-21) but i dont see any data, with an Digital Module i can read and write, but with analogic module i can't do anything. The analog module works perfect, i have 4-20ma Simulator and work fine. Modules: PLC: NJ501-1300 Slave: ECT-21 Analog: ADO81-V1 Can u help me? Regads..