Search the Community

Showing results for tags 'modbus serial'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 305 results

  1. Hi every one. I have strange problem with Modbus communication in Citect 2018. I am communicating to the site switches through Modbus TCP protocol using MODNET driver and reading its sates. I am reading data from Input registers (registers addresses starts from 3x). In default, MODNET driver initializes communication trying conecting to holding register 40001 so I changed initialization in citect.ini to address 30001 because driver didn't want to establish connection because switches don't support holding registers. Now, connection to switches is working but only when page is open where I showing data from them. When I change the page, Citect loses communication and inform this showing alarm on HW alarm page. When I again open page where I show read data, communication back again. Where could be a problem? I will mention that I have more different Modbus TCP devices in project configured and with them don't have such problem. The only difference is that I am reading from holding registers and initialize parameter in citect.ini is not defined for them as for switches.
  2. Hello All, Please Help Me.. How I can to connect Omron CP1L-M + CP1W-Cif11 with Mitsubishi Inverter D700? Thank you. Omron modbus belum fix.cxp
  3. Hallo, i want to connect PLC Omron CP1E to indicator weighing scale with modbusRTU connection and i have a CP1W-CIF11 module to connect indicator with CP1E. ,but I have no experience in RTU modbus communication in the PLC. How do i start?   *i just need output: 1. Coil (Reference No = 0. Output bits) for input switch with address 3 (Tare). 2.Input Status (Reference No = 1) for output lamp with address 17 (stable) 3.Input register (Reference No = 3) to read data with address 5 (gross weight) 4. holding register (Reference No = 4) to write comparison data with address 17(over) page 85 - 94 in attachment     ad4402_manual.pdf
  4. Hi guys, this is my first topic on this forum. I need an help with modbus communication through NX1P2+CIF12 and slaves inverter. I have never used this board, so i need an example to understand. Thanks
  5. Has anyone successfully used a 1783-NATR for Modbus TCP communication between a ProSoft MNET card (in the ControlLogix rack) and a Modicon Quantum? ProSoft MNET:  10.x.y.z Modicon Quantum:  192.168.1.x There is one (1) ProSoft MNET and four (4) Modicon Quantum's. NOTE:  I know there are other devices that support this behavior...the NATR is the suggested standard hardware.  We are getting various responses from distribution and support.  ...I was hoping someone in the community could confirm.   Thanks for your time!  
  6. Hi there, I am fairly new to programming serial communications, especially with Mitsubishi PLCs. Can someone walk me through in ladder logic how to bring in ASCII to the PLC, store the data in the data registers. Then send the data out to another PC once an 'X' input is satisfied? ASCII code would go like the following: C2,0,1,123,2,ABC,3,456,CR
  7. Hi I'm trying to set up Modbus RTU communication between FX3U PLC and a weigh module. I would use the ADPRW command using 0X03 to read the 16 bit Holding Register but in the weigh module the Data Address/Holding Register of the value I want to get is 400047 - 400048. How to translate the value in 16 bit?   Thanks, Fabio
  8. Hi,   we have a Mitsubishi PLC Fx3U-128MT and a A&D weighing module AD 4212L. The weighing module supports MODBUS RTU communication via RS-485. We are looking for the most affordable and simpler way to establish communication between PLC and weighing module. At pag 20 of the manual " MODBUS Serial Communication Edition " https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf there are three options of communication equipment. According to your experience, what specific interfaces do you suggest us to invest in? Thanks    
  9. Hello,   Any one  have idea how to read and write variable for Schneider tm221 plc with Modbus function codes 3,6,16. I attached file for power supply communicator with registers, I need to adjust power supply from 25% up to 100. Please need help. Best regards,   Chyngyz   Modbus OPERATING INSTRUCTIONS.pdf
  10. HI All,  I have an issue with my SCU32 communication.  Back ground Two SCU32s  (top and bottom side) connected via a 1100M datacable  using port1 ( 9600bps,  8-2-E, start code FF, end code FE, Tx save to d1000-d1200 , Rx save to d2000-d2200). PORT2 of bottom SCU32 is connected to a compass( 2 wire, 8-1-N, 19200 bps, serial gateway MODBUS ). Refer to photo Issue  Without compass, the receiving data at top is very stable and is didn't see any fluctuation. But if is compass is connected at bottom side port2, there is a fluctuation at the top side RX data(specifically d2000-d2005 ) .  I checked the data a bottom side TX (d1000-d1200) and it is stable. Only after sending the data and Receiving at Top side, then only the starting words fluctuate. I am not sure sure what is wrong, I am using logical ports for the DTXDU/DRXDU and compass.   Appreciate all your feedback and suggestions.  
  11. Hello all, I am working on a project where I am communicating with a Mensor CPT6100 pressure transducer using a Micro-850 PLC. For this, I have used an AWA instruction to write some ASCII characters to the sensor. The sensor then responds to the write instruction by sending ASCII characters to the RX buffer and I used ACB and ARD instructions to read the ASCII characters. Now, I have set the ACB trigger type to 0 (msg triggered only once) and it successfully reads from the sensor. However, when I set the ACB trigger type to 1 (msg triggered multiple times), I do not get any reading in the ARD block. As a matter of fact, the ACB Q bit switches off every time the program is executed when the trigger type is set to 1. I am trying to get continuous readings from the sensor, but when the trigger type is set to 0, the program latches on to the first and only reading and it won't change. My question is, how can I change my program so that it can continuously and autonomously read from the sensor without me having to manually trigger the AWA and ACB instructions every time. I am attaching the program to this thread for your reference.  ASCII_Test_Copy.ccwarc
  12. Hi all, I'm having an issue with EcoStructure Control Expert where when using DTM browser I try to connect but I get a message "No Ethernet/IP device at specified address...." My issue is that I had a device communicating using modbus but it has stopped and I cannot diagnosis the issue. I can ping the address and run a modbus poll from a PC on the network and everything performs correctly. Any help would be greatly appreciated. 
  13. Need help in table scrolling

    Hi all, We have a DOP 107CV HMI we interface this HMI with microcontroller through RS485 Modbus protocol. I'm new to HMI and PLC's although we are successful in interfacing HMI with Controller(Communication Established successfully) We made a table in HMI and allotted some registers to Modbus address and data is transferred from controller to HMI up to this we are good in communicating Since the table created is static and we cannot scroll down from that table so, to overcome this problem we found History buffer and made PLC trigger and allotted address. In that History Buffer we created 7 rows and the data is sample whenever we triggered the PLC in that case scrolling is working fine, but the problem we are facing is whenever we update 3 rows out of 7 and triggered the PLC only 3 samples are updated in first column and in the next step we updated the other 4 rows and triggered the PLC the data is sampled on next column but we required it to be sample on first column instead of second.  
  14. Delta plc Communication Issue

    Dear allI have DVP14SS211R series Delta PLC Which is having 24V DC supply voltage. I am using PLC as master and My end device as slave. My slave device set device_iD=1I am using Modbus RTU protocol for Function code1baud rate =9600parity =noneStop bit=1data length=8I would like to know how to send request with Function code 1(Read coil Register). i have attached code reference. Communication block it wont give error it shows 0 .means No error
  15. Hey Everyone,   My company decided to purchase a piece of equipment from China, and I have the pleasure of updating its terrible existing controls. We were given the PLC program by the manufacturer, so I was able to make my changes pretty easily - or at least that would be the case if I could actually connect to the dang thing. The source program is indeed openable and editable via GX developer (the original configuration shows it as an FX3). I figured connecting should be straightforward, but I was wrong.    I initially used a serial/usb converter that I've used on some older Allen Bradley equipment (which worked fine for that). However, after no luck using it on the "Mitsubishi", I purchased a different cable that I found recommended on this forum (Tripp Lite USA-19HS - https://www.alliedelec.com/product/tripp-lite/usa-19hs/70101537/?gclid=Cj0KCQiAj9iBBhCJARIsAE9qRtB_n8TVAnJdFyYokoEu42W6H6LaT4kVsgJQI1qvPUsUF3rFviKpbt0aApLHEALw_wcB&gclsrc=aw.ds). Still, no luck. I've tried 7E1 and every baud rate possible, as well as some other bit/parity configurations (and yes, I've verified that I'm using the right com port, as well as tried moving the converter to different ports and trying those). Nothing seems to go through.  I have almost no experience with Mitsubishi beyond a couple of FX5s (which have worked fine, but I connect to those via ethernet). Any help would be greatly appreciated; if I can't make these changes, I'm going to end up rebuilding the whole cabinet with a PLC I can rely on.   Thanks in advance.
  16. modbus rs232 communication error

    hi I am traying to connect 10 plc's FX3U to a scada system, on the plc's there are a rs232db and FX3U-232ADP-MB cards. i have devices transmit the rs232 by lan or any thing I need (rut955) my problem is when i download the program on plc same times the communication go right , but if i powering pls off then on the communication fail down. I initialized the plc  like photo https://drive.google.com/file/d/1Tr367wfVCRG6vvKcsOFyTKG_FExAsnVy/view can any one help me? sorry for my English
  17. Hi, I have an Omron NSJ5-SQ00B-M3D Programmable Terminal (HMI) that I am trying to get to communicate with an Omron CJ2H PLC through a DeviceNet module (DRM21) in the main PLC rack.  I don't see how to configure CX-Designer to communicate via DeviceNet.  How is this done?  Many thanks for any help.
  18. CJ1M+ETN21 Modbus TCP

    Hello. I'm trying to use Omron ETN21 as master for ModbusTCP protocol. I can communicate with 1 SLAVE UNIT (standard modbusTCP slave) using FB MTCP_ETN_Client.zip  from https://www.myomron.com/index.php?action=kb&article=1245. It works perfectly. But I have three SLAVE UNITS to communicate to. I'm trying to do this using [524]Modbus_TCP_FB.zip sample. I have copied SECTION1 to SECTION2 and changed IP number and SOCKET number. But this doesn't work. I would realy appriciate a working sample where OMRON PLC is MASTER for THREE (or more) SLAVES. I'm attaching code file... Thanks. Best regards, Andrej. Modbus_TCP_FB.cxp Modbus_TCP_FB.opt
  19. Hello out there   I've searched for quite some time but unable to find any information helping me through this. I got a Omron PLC NX1P2 where im supposed to setup modbus communication over TCP/IP but so far i've only been able to find information regarding RTU setup. But seen forums mention its possible to setup via TCP/IP Anybody who can help. A program sample would be helpfull aswell. Im a trainee as automationengineer and this is my first encounter with Omron PLC and Modbus so quite new to the field.   kind regards Ivan T.
  20. Hello, We have a FX3G connected to a FX3U-ENET-ADP inside a main cabinet. We are then using that master PLC to collect data from 2 other fx3g plcs in a node:node serial network. I was assigned a small project of pricing out some wireless adapters so we can upload/download to the two slave plcs. My question is, is it possible to upload/download programs to/from the slave plcs through the ENET adapter and serial network in the main plc? It would save us some money if possible. thanks.
  21. Hello, I'm trying to connect a CJ1M-ETN21 as slave Modbus TCP with a Modbus/Dali Gateway. I download from Omron website some FB with ones should be possible.   https://www.myomron.com/index.php?action=kb&article=1245 The FB only can be used with the direction unit 0, but we can change some directions inside the FB and can be adjusted to other units. In the download I found this FB: MTCP_ETN_Connect, MTCP_ETN_Fn01, MTCP_ETN_Fn02, MTCP_ETN_Fn03 .... Supposed with connect we can establish the connection with the master, but the FB never make nothing. Should I make some special configurations to use this FB? I appreciate any help. Thanks
  22. Indusoft Web Studio

    i am using indusoft web studio for the modbus logging. program runs successfully but after a half day or a day it shows error " error initializing the driver modbu 10.10: invalid serial port "any suggestion will be appreciated.RegardsZubair Ahmed
  23. Proface with Serial Printer

    Dear Sir, Good day. I facing difficulty on using proface to print out the data using serial printer. I did follow all the instruction on proface reference manual but still fail to print out anything. Anyone here having experience on this issue? Thanks. 
  24. Modbus with CJ1W SCU31-V1

    Hi every one, I want communication Inverter mitsubishi D700 with module CJ1W SCU31-V1,  any one give me a correct solution and send any sample program. Thanks
  25. I'm trying to communicate with INVT PLC and DGM8002(grain moisture analyzer) via mobus RTU.   Can anyone explain about these Modbus address ? Please kindly see in picture . example working mode address K0 (0-stop ,1-manual,  2-Auto) Actual Moisture Address K6 What is meaning of K0,K1,K3,K6.  https://drive.google.com/file/d/1-mGzpEvw4UlewWhR9k3wOd1mO-uhsklL/view?usp=drivesdk Is that K0= 0000 K2 = 2000. K3=3000 ? Any suggestion please. I'm really appreciated your comments.❤️