Search the Community

Showing results for tags 'ip address table'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 26 results

  1. Lets say i have a PLC, with a name PLC1 with IP/Subnet of 10.125.34.243/255.255.255.0 I have to communicate this PLC1 with 2 other PLC's, PLC2 and PLC3 PLC2 with IP/Subnet of 10.125.34.10/255.255.0.0 PLC3 with IP/Subnet of 10.125.46.10/255.255.0.0 I imagine that, all these three are in different subnets, and so there should be no communication at all, but when i tested it, PLC1 to talking to/from PLC2 and not PLC3.  anyone know the answer to this ? How does it talk to PLC2 with different subnet, but not PLC3 which is in different subnet as well. 
  2. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  3. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  4. CX-Supervisor 3.4.1

    Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
  5. Double address - Alarm

    Hello, I would like to see your logical opinion about this situation and in which part of system where I need to find solution - software or in the physical field. Subject: Twelve old system based on Mitsubishi PLC AnS series, Profibus Here is pneumatic transport, with 5 lines, each line have a shredder and discharge valve. A few months ago, when line 1 works , display shows line 2 and vice versa, it was first problem, but the system was still working. From the last week system doesn't work. On the display appear line 3 in works, but system can not started. Alarm shows Double address (perhaps two valves have some address), Alarm still appear after reset and even all lines are turned off. What is your opinion where to find proble (PLC, I/O moduls, cables,...)  
  6. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  7. Dear all, I'm first time using M580 (hotstandby). Now finish the configuration, but the problem is how to write the address for Digital Input, Digital Output, Analog Input, and RTD module in elementary variable ? I try to put name DDI_1 and the address is same with M340 topology like %I2.1.0.1.1  and for digital input but got message after build : {Elementary Variables}    :     The instance is located on an address that isn't configured. :     DDI_1 Thank you for your advice regards  
  8. Dear all Please identify me i am having one Issue in my PLC.When I changed the IP of my plc then suddenly its showing error ERH its mean IP address wrong but  My CPU setting is same like previous means unit no=0, x16^0=0 ,Node=x16^0=1  and IP is 192.168.0.15 Mask add.255.255.255.0. but when I, transfer to PLC (in Program Mode) its not transferred(Failed to Transfer) please rectify me where I am doing wrong.
  9. C500/C120 Support

    Hi Could anybody tell me if the C500/C120 support tool in CX Programmer uploads the I/O table when it uploads the program from a C500. I have already backed up a program from a C500 using SYSWIN but SYSWIN doesn't allow me to edit, create or generate an I/O table, so when the program is downloaded to a sister machine, I get I/O errors that can't be cleared. Any help grateully received
  10. I READ IN THE MANUAL FOR THE CJ2M-CPU34 THAT IT IS POSSIBLE TO CHANGE THE IP ADDRESS BY WRITING TO D30098 AND D30099 (MY DEVICE IS UNIT 0).  I TRIED TO DO THIS ON A TEST PLC BUT AM NOT HAVING ANY LUCK... I WROTE MY IP ADDRESS #C0A8 TO D30098 AND #0E30 TO D30099 (IP ADDRESS 192.168.14.48) WITH THE CPU IN PROGRAM MODE, I SET THE RESET BIT (A501.00) TO TURN ON ON THE TRAILING EDGE OF THE FIRST SCAN BIT, I CAN TELL THE CARD RESETS BECAUSE I AM CONNECTED VIA ETHERNET AND I GET DISCONNECTED, BUT THE IP ADDRESS DOES NOT CHANGE.  IS THERE ANY WAY TO CHANGE THE IP ADDRESS WITHOUT CX-PROGRAMMER?  I NEED TO GET A SOLUTION TO MY CUSTOMER TONIGHT AND MY SUPERVISORS DO NOT WANT TO RELEASE OUR DEVELOPMENT CODE TO THE END USER.   THANK YOU!!!
  11. hi.  i want to make some program that work with indirect adress. example, i make program with many much type. I make with Got-1000 mitsubishi.   can you bring me some example? i am sorry, my english is Bad
  12. HI Everyone,  Recently i have bought a plc fx3ge and gt2000 hmi .the problem is that whenever i use a device address d280.b1 in hmi .i am not able to use the same address in gx works for plc (LD D280.1).can anyone help me with this problem.   
  13. Hi guys, I'm attempting to implement a fuzzy logic controller from scratch. I plan on using a lookup table to assist with retrieving the membership value. Does anyone know how to implement a lookup table. I know there is a L9P_LKUP block in the LL984 editor..except I'm not sure how to actually enter in the parameters or read from it.   Kind regards, Luchek
  14. CPU 948R

    We have Redundant S5- CPU948R we have the requirement of knowing input address for FUM signals(Open & close signals).. Also how can we identify which cpu is acting as main CPU and which one is Standby. We look forward to a solution. Kindly advice us.
  15. Hello, we have 6 encoders and 2 of them lose their mac address every time power goes out. The other encoders find their Mac address by themselves. Can anyone help me with this issue? Thanks for reading. Have a great day.
  16. How do I assign an IP address to an S71200 CPU for the first time? Is it possible to do it over ethernet? Thanks in advance!
  17. Hi friends, The scene is like this... I have some 200 energy meters whose readings are continuously logged at 15-min intervals into a logging table. The meter does not have any other value logged. Let's consider these readings as analog tags. However these tag values are continuously increasing to ever larger numbers. Thus we have a problem for display on trends. Customer now requires that the Citect shows usage trends for any meter for a specified period of the past. That is to say, the meter that he wishes to observe is selected - along with a period typically between 2 dates (perhaps also with a sampling period) - and the trend must appear. So in other words, given a single trend object, how do you make values appear for any selected tag on this trend. Perhaps this can be overcome by some genie/super-genie mechanism. My approach to this is...For the selected meter, I use SQL to query the 15 minute logged values (also taking into account the required sampling period) taking the reading on starting date as initial. All values thereafter are subtracted -within the SQL query- and the result of this query is kept in a 2 dimensional array(x for time, Y for value) or a new database table so that the trend displays values starting with zero. This much I can do with Cicode. After this, I need a method to display the values so obtained in a trend object. Essentially this is the same as feeding a trend object with a set of X & Y values that I have in the form of an array or in a database table. I shall greatly appreciate any help to meet the above objective. Thanks for looking in. With best wishes.
  18. connecting ixt4a to a cj1m/cp1l/ns network

    hi everybody i have a network with 2 pieces cj1m and 2 pieces cp1l communicating with a ns15 monitor. everything is fine. i need to connect an ixt4a monitor in that network. my question is : do i have to make new routing tables or it is not neccessary? my routing table for cj1m and cp1l cpus are attached. if then i have to make new routing table so that the cj1m will be able to communicate ixt4a monitor, how am i going to do it for both monitors? Any help will be mostly valuable and appreciated. thanks
  19. CPU 314IFM adress

    Hi, I have a CPU 314IFM order number 6ES7 314-5AE10-0AB0 when i select it in hardware config it show I/Q adress 124 -155 while it should be to 129 only (the manual mention that and it covers all inputs and outputs and the special funaction also) I try (offline) to change the order number only (another 314IFM) found it give different address range for each CPU while it all have 20 DI/16DO 4AI and 1AO
  20. Submitting with an SLC

    Hello, At the plant I work at there are devices with IP addresses starting with 192.168.0, 192,168.1, and 193.168.2 The SLC in question is on 192.168.2 We would like to access it from our laptops which are on 192.168.0 The laptops have their subnet mask set to 255.255.252.0 and we are able to pull see other controllers on the 192.168.2 network. However, for some reason we can't with this one, not even when I'm plugged directly into the Ethernet port on the controller unless we change our IP address to one on 192.168.2 I believe the subnet mask on the controller isn't set right. Can anyone tell what I'm missing here? Here's an overview of the current settings: Laptop: 192.168.0.20, 255.255.252.0 Controller: 192.168.2.17, 255.255.252.0 Any help would be greatly appreciated. Ben
  21. For some reason, some of the symbol names and comments in my symbol table in my project have disappeared. They are present in a previous version of my project. I would like to copy the symbol table from the old project version into the new project version. Can I do this by simply copying a few files from the old project folder into the new project folder? Which ones?
  22. I have a list of 100 faults for my machine. Each fault has an integer variable in the symbol table, containing an integer that matches its position in the list. Say I then want to add a fault in at position 12, I would then have to renumber all the following faults. Is there a built in way to do this automatically? Alternatively, if you have any other suggestions for achieving a similar thing, I would love hear them.
  23. I have had a GE 90-30 CPU331 in my house for 17 years with no trouble at all. I have a problem that I have never seen before. I was editing the program using LM90. I don't know what I could have done in the program to disable an output. Just 1. All the rest of the points in that group on that card still work. I swapped cards with no difference. All of the elements of the rung are true (highlighted). The output is not on or highlighted. The nickname over the output has ONE letter highlighted. The bit in the reference is "0" and is highlighted or "grayed out" (the cursor is not on it). I searched for coil conflicts. I am using this output contact lots of places but only one output. The logic is working correctly when I use another output or %M. This is an isolated output which needs to be in this group (moving it would be awkward). What does a "grayed out" reference bit mean?