Search the Community

Showing results for tags 'fluctuating values in data register'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 129 results

  1. Emerson (GE) memory map data types

     I've always had this Allen-Bradley memory map taped on my wall in my office. It used to be handy to use, until I remembered al of the prefix letters for each data type. Now I am using Emerson (GE) the old proficy software now called PAC ME machine edition. Now I'm finding it's about impossible to find the data type list amongst the thousands of help files, videos, ect... it seems like a simple thing to find, but I'm not having any luck. They use I and Q for regular inputs & Outputs, but there are R files, M files, S files, N files, G files, ect.... this is old-school PLC software that doesn't use tag names.   Is there a steadfast rule for each type, or can they be used for any type of data? Dazed and confused...  
  2. WRITE MULTIPLE REGISTER MODBUS

    Hallo my name is Danu, i have a CP1E wirh CP1W-CIF11 and connect to modbus RTU device, i have done with write single coil, write single register,  read single register and read multiple register. But i try to write multiple register,  the indicator of CP1W-CIF11 is off and if i check d memory its no data. I attached my cx programmer. Can you help me create write multiple register in cx programmer?  Thank you AD4402-modbus edit edit edit edit edit.cxp
  3. Hi All, I need access to a the Safety function blocks within a safety CPU using sysmac studio on a machine we are upgrading.. Is there a generic password available to gain access? Best Regards, Paul  
  4. Dear reader, I am writing a C# program using the library  ‘EasyModbus’ that needs to communicate with Siemens WinCC via the connection type ‘Modicon modbus’ I have written a version using the ‘float’ data type in WinCC and that works perfectly. Here my code fragment: Method to convert ‘double’ to bytes in C#: public static byte[] DoubleToModbusFloat(double value) {     byte[] bytes = new byte[4];     float floatValue = (float)value;     int intValue = BitConverter.ToInt32(BitConverter.GetBytes(floatValue), 0);     bytes[0] = (byte)(intValue >> 24);     bytes[1] = (byte)(intValue >> 16);     bytes[2] = (byte)(intValue >> 8);     bytes[3] = (byte)intValue;     return bytes; } Call of the method and loading of the modbus registers in EasyModbus: Bytes = PublicCode.DoubleToModbusFloat(TmpDbl); int n = (int)ModbusStartAddress + ((i - 1) * 2); mb.ModServer.holdingRegisters[n + 1] = (short)((Bytes[0] << 8) + Bytes[1]); mb.ModServer.holdingRegisters[n + 2] = (short)((Bytes[2] << 8) + Bytes[3]); So far so good – this works fine. But I also want to be able to use the ‘Double’ data type in WinCC because I sometimes need more precision than the 7 figures of the ‘float’. I thought it would simply be a case of doubling up the code so I wrote: Method to convert ‘double’ to bytes in C#: public static byte[] DoubleToModbusDouble(double value) {     byte[] bytes = new byte[8];     long intValue = BitConverter.ToInt64(BitConverter.GetBytes(value), 0);     bytes[0] = (byte)((intValue >> 56) & 0xff);     bytes[1] = (byte)((intValue >> 48) & 0xff);     bytes[2] = (byte)((intValue >> 40) & 0xff);     bytes[3] = (byte)((intValue >> 32) & 0xff);     bytes[4] = (byte)((intValue >> 24) & 0xff);     bytes[5] = (byte)((intValue >> 16) & 0xff);     bytes[6] = (byte)((intValue >> 8) & 0xff);     bytes[7] = (byte)(intValue & 0xff);     return bytes; } Call of method and loading of the modbus registers in EasyModbus: Bytes = PublicCode.DoubleToModbusDouble(TmpDbl); int n = (int)ModbusStartAddress + ((i - 1) * 4); mb.ModServer.holdingRegisters[n + 1] = (short)((Bytes[0] << 8) + Bytes[1]); mb.ModServer.holdingRegisters[n + 2] = (short)((Bytes[2] << 8) + Bytes[3]); mb.ModServer.holdingRegisters[n + 3] = (short)((Bytes[4] << 8) + Bytes[5]); mb.ModServer.holdingRegisters[n + 4] = (short)((Bytes[6] << 8) + Bytes[7]); However, this code does not work correctly. I have tried all combinations of byte and word reversal, and whatever I do WinCC either displays nonsensical values or ‘####’ showing that it cannot display the value. I have tried reading as much documentation as I can but it still looks to me as if I am doing the right thing. Also, I have downloaded a number of ‘modbus master’ code examples, and they seem to be able to read the ‘Double’ from my program without any issues. In WinCC I also see that there are two types of double – ‘Double’ and ‘+/- Double’ – I am also unsure as to why this is – there is no ‘+/- Float’ data type, which seems inconsistent to me. I am obviously missing something, but cannot seem to discover what exactly. I hope that someone can point me in the right direction as to what I am doing wrong. Please see attached word file for a picture of the configuration of the connection in WinCC.   Thanks in advance for any help !, Dave Long Double trouble.docx
  5. Hi All, As a system integrator coming from an Allen-Bradley based environment to a Mitsubishi based environment (GX Works 2, Q series PLCs), I am used to doing this with Allen-Bradley PLCs: when you hit save while online, you are prompted to upload the values in the tags and can save these values and view them offline - which is useful when doing modifications and analysis offline, as well as backing up settings in case your PLC dies and has to be replaced with a brand new one. I was wondering if anyone knows if there is a way to store the current values of the devices in a Mitsubishi PLC to my PC along with the .gxw  file that is saved when doing a "Read PLC"? I am aware you can set up a File Register but it seems to only save ZR devices as well as specifically designated "Extended Data/Link" D and W devices, but most data is not stored in these devices. Thanks
  6. Data register over flow

    Hi, data registers are getting full, because of extremely high speed pulsing is there any way , if the data value in register goes above the capacity of 32 bit register, it automatically attaches itself to next set of data registers so lets say if data was written in D10,D11 Upon reaching the limit, it goes to D10, D11, D12, D13 please share if there is an alternate way to do this
  7. Data register over flow

    Hi, data registers are getting full, because of extremely high speed pulsing is there any way , if the data value in register goes above the capacity of 32 bit register, it automatically attaches itself to next set of data registers so lets say if data was written in D10,D11 Upon reaching the limit, it goes to D10, D11, D12, D13 please share if there is an alternate way to do this
  8. Hi, I'm Jovel, I'm new to learning how to program PLC. Just want to learn how to use Omron Sysmac Studio . I have a question about the Data Type Data Type - Structure ( Offset Type - Offset Byte )  / Union   I Don't Understand this 2 Data types and how going to use them, can anyone teach me and have a sample program? Thank you
  9. Hello and good day I have a Mitsubishi fx1n-14mr PLC controlling a band saw. The PLC is connected via a DB925 - MD8M cable to a Beijer/mitsubitshi E100 HMI for communications and as a power supply via RS-422. When powered on the display on the E100 panel fluctuating, i.e. the screen turns on and off repeatedly. If the main switch is then switched off, then on again the screens seems to stay on and the machine operates normally. The PLC has a built in AC/DC power supply and I suspect that is may be the problem. Is is possible to switch out the AC/DC module? To make sure that the E100 panel is not the problem I want to connect a 5V external supply to the port located on the back. Is it safe to have the RS-422 and the 5V external supply connected simultaneously?
  10. Hi All I am trying to connect Cognex OPC Server with Mircrosoft SQL Server (SMSS). Do you have any idea how to do that? I couldn't find relevant information online.
  11. I have an old Panelview 800 in a system that consists of the PV, a Micro 850 and 10 Powerflex VFd's running conveyor motors. My problems started when one of the motors would not run. It seemed that the PLC was not sending the Run command or the Speed. The problem got worse as I was working on it when two others did the same thing. The current situation is that 8 of the VFD's are getting a Run command and 2 are getting a flickering command. All 10 are getting a 0.0Hz speed command. I connected to the equipment with my laptop and looked at the PLC program and the PV program. I found that in the PV program that all of the user input data, which consists of Motor Speed (Hz), Accel and Decel times and some other timer values for the timing of some conveyor starts and stops, where all gone, set at '0'. this equipment is several years old and predates my presence here. The PLC program seems to be running and passing the commands that it receives to the VFD's. The data is passed to the PLC via Global Variables. I've never encountered this particular problem before. Any ideas?
  12. Hi, I have a problem with Omron PLC and Beckhoff IO. The IO just disconnects in a few minutes and comes back! I received different errors: Link off error, Illegal slave disconnection, process data reception timeout. When I also check "Display Diagnosis/Statistics information" I see errors on all ports A and B of all nodes.  I have called and talked to both Beckhoff and Omron.  I have two NX1 and one NJ101 to test. And I have three EP2318-0001. I have the same problem with all the PLCs and EP boxes. It does not matter if I have one, two, or three nodes. I have tried different revisions of the EP2xxx from the XML file, different settings for the slave, different task periods, and the error still is persisting.
  13. Currently have NX PLC setup as an OPC UA server and an OPC client setup and communicating.  The issue is only tags that do not have a Data Type are showing up in the OPC client.  I have 2 separate OPC softwares connected to this plc through OPC UA and both are having same issue.  If I setup the OPC as a polling service, then all the tags show up as expected.  Does anyone know if this is a known issue with Omron and their OPC UA server, or is there something that I am doing incorrectly (possibly a setting within Omron that I am not aware of)?
  14. NE1A-SCUP02-EIP

    Does anyone have experience with the NE1A-SCUP02-EIP safety PLC? We had a machine shutdown yesterday with a L9n4 error on the NE1A unit. The manual says this is a tag data link error. Does this cause the safety PLC itself to shutdown? I always thought the EIP portion of the safety PLC was only used for status reporting to the PLC. The safety portion is strictly on DeviceNet and is independent of the EIP network.  The CJ2 PLC's error log tells me it had problems communicating with the safety PLC, the VFD, and NX I/O's which were all in the same panel going through an Ethernet switch. 
  15. Hi, I have quite a noobie question. I want to create a function block to do some simple operations on 2 variables. Both variables are In/Outs (see picture attached). How can I make this function accept variables regardless of the data type? Given these is just simple math I am able to use the same instructions in REAL, INT, UINT, etc. But, the function block only lets me assign one Data Type to the In/Out variables.
  16. Data Historian

    Hello, What would be the best data logger for Backhoff automation based automation? Idea is to record some analog and digital tags at certain time intervals. Present them in tabular as well as graphical form and print some reports based on selected time window. I have looked up TwinCAT Analytics and that seems to be one option. But want to check others before making decision.
  17. Memory registers on KINCO PLC

    Hello to everyone. I hope you are doing well. I have a KINCO PLC HP043-20DT. I'm communicating through free-protocol instructions XMT and RCV. The manual states that memory registers SMB86, SMB186 and SMB286 contain information about the state of the reception instruction. I would like to ask if any of you know of the existence of an analog register but with respect to the transmission instruction, instead of the reception. The manual does not indicate it and I could not find any information online. I've sended an email to the manufacturer but, until now, I have not receive any answer. Otherwise, how could I search for this information? I tried through the manual providede by the manufacturer, but maybe there is other way. I would appreciate any information. Thank you so much. Kind regards.
  18. Hi gents, I need to build up a communication between nx1p2 to another omron plc (any type with sql support). This is due to the fact that I have finaly to prepare the plc communication with the sql database, and nx1p2 doesnt support this.  Sorry, i know it's probably a noob question, but I'm a beginner. What type of technology i shoud use to make this connection between NX1P2 and another Omron PLC? Or might be some share some project?  
  19. Hey guys,   I know this is a topic that has been discussed before, but I am having trouble finding exactly what I am looking for.. I want to know the most efficient way to record data from my PLC to an Excel file on my PC. I want this to be done without the use of the PLC's webserver.  Specifically I am trying to record vfd speed every 10seconds with a time and date stamp. How can I do this?   Thanks, James  
  20. Hi, I have inserted new RTD module into in my SLC500 as replacement to defected RTD module however the module LED is enabled but the channel LED's are blinking. I have checked the following: In the advanced I/O configuration the module configuration is shown as expected In the data file word format it is not corresponding to the channel preferences What should I do and how to fix the word bits?        
  21. Open data log in HMI

    Hi there! I have S7-1200 controller connected to a Comfort Panel. The machine has some pressure and temp sensors, as long as many valves and other stuff. I generate a daily datalog with some of those variables but, the thing is, I've been trying to figure out how to show these data in the HMI without using a trend viewer. I don't know if it's possible, but I want to be able to see what valves were open (for example) the day DD/MM/YYYY at HH:MM:SS, using the generated data log, kind of knowing the state of single bits at different past moments. I've been searching the web but I didn't find something exactly like this, don't know if I'm doing it properly so I'd like to know if you have done this or you can throw some light on the topic. Thanks in advance and hope you can help me!
  22. Have been able to exchange data types of BOOL, INT,  DINT & REAL between Omron NJ/NX CPU with Allen Bradley Logix CPU's with Ethernet/IP using the CIPUCMMRead & CIPUCMMWrite instructions. I now have a need to exchange "STRING" variable types. Have tried varions string lengths in the NJ without sucsess. AB default string length is 82 & Omron 256 but I think the difference is the length headder that AB has with within their String Tag type. I know I could convert my strings to an array of bytes & sent them this way, but was looking for a solution to sent them as native strings. Hope someone out there has done this & can share their leg work? 
  23. INDIRECT REGISTER

    i want to use indirect register, but why contact 100,IR0 is not ON, is it my program correct?
  24. Hi I'm trying to set up Modbus RTU communication between FX3U PLC and a weigh module. I would use the ADPRW command using 0X03 to read the 16 bit Holding Register but in the weigh module the Data Address/Holding Register of the value I want to get is 400047 - 400048. How to translate the value in 16 bit?   Thanks, Fabio
  25. Hello all, I need to read device memory mostly I need to read R registers from PLC L26. I read device data, but inside of table, I can't find R or ZR registers. Can you help me?  What I did wrong?   BR KS