Search the Community

Showing results for tags 'ethernet modbus tcp'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 466 results

  1. IEEE-754 Floating Point

    Hi, Is there a simple way to convert hex value of IEEE 754 to real value in gx works 3 Regards, Ramkumar  
  2. Good day everyone, First post here so hopefully I'm not violating community guidelines in anyway. I've got a system that has some 50 odd Micrologix 1100 and 1400 in use and I'm currently working on setting up an auto timesync for all of them using just 1 of the PLCs that will be my master time PLC. So far I've put together the logic for all the message instructions with the corresponding IP of the slave devices. I'm running. Into an issue with not being able to terminate/break the message connection on a PLC that I have already synced. Is this even possible to do on the ML1100. Once I get to 16-17 messages DN it starts to ER and will not complete any further messages. What I have is a message instruction ladder with a timed trigger to activate a MSG and write the RTC data then time down and connect and write to the next and so on. When it triggers the message instruction of one PLC it also fires an OTE to trigger the BK of the previous message instruction. However it doesn't seem to be actually cutting the message connection and holds it persistent until a power cycle/download event.
  3. I want to establish Ethernet IP communication between the following PLC CPUs. Schneider Electric - BMEP582040 Honeywell - ControlEdge UOC CPU900-CP1. Where the Schneider must be master and Honeywell must ne adapter. Let me know if anyone have done this or can help me to do so.
  4. Hi everyone, I'm new here. Thank you all in advance for the help you can give me. I have one machine with PLC Omron NJ101-9000, and this is Server in the Modbus communication. In the attachments, you can find the function block I used to communicate with 1 client. This work OK and I don't have problems, but I need to communicate with 2 clients at the same time. This block only admits one connection at a time. How I can connect 2 at a time? If I create 2 of these blocks, does each client need to connect to a different port? Do I need "open" this port in PLC configuration?   Thanks!
  5. Hardware IQ-F connected via Modbus TCP on the NZ2FT-MT works Fine with normal IO. Now i want to run the NZ2FT-C24 with an modbus RTU protocol, i'm planning to make this. Anyone having an example for the NZ2FT-C24, what can help me?
  6. Hardware IQ-F connected via Modbus TCP on the NZ2FT-MT works Fine with normal IO. Now i want to run the NZ2FT-C24 with an modbus RTU protocol, i'm planning to make this. Anyone having an example for the NZ2FT-C24, what can help me?
  7. QCPU to 2x kyence iv2

    Hello all, we are using Q03UDECPU and via built-in ethernet port its connected to two IV2-G30. (through unmanaged switch) to establish connection we are using FB LQnUDEEthActive (hereinafter referred to as  FBLQ) two instances of FBLQ in two instaces of our FB which is responsible for creating messages that are then send via FBLQ Both keyence devices have different IPs, ports and connection number. Problem is that it is working flawlessly, except the time its not working :/ from time to time it simply doesnt trigger Keyence device. It looks so far like its independt of turning machine OFF/ON, also both keyence devices are used in different times (about 10-20seconds of difference) Im currently working on sime kind of internal diagnosis to see whats happening when its not working, but im just curious if there is something obvious we are missing? any help will be apreciated Thanks  
  8. Hi. I have this project where we read out data from temp sensors and vaccuum stuff. We use Pfeiffer vaccum cpt 200 for the vaccuum, and we create a frame to send to the modbus unit to pull a value from example '306'. With all the current items we pull data, all the values are only updated every 5 seconds, is there a way to perhaps pull several frame/addresses in one request per device? Current codes we read, some are in sequence of each others, but more has a bit of gap like 00, 02, 306, 307, 398, 330 and so on.    
  9. I am trying to create a simple `Hello World` Modbus TCP/IP program using Twincat3 and virtual PLC (PLC running locally on my computer).   I have set up a LabVIEW Modbus TCP/IP master + slave program (both of which are working see screenshots below).  I can send data between LabVIEW's master and slave programs. And also read the data from Python script (so I know for sure they are all working).  Now I have tried to create a Twincat3 program to set some registers using Beckhoff example What I have tried:  - I have tried changing the ipAddr parameter to: 'localhost', '192.168.88.1', '192.168.88.126'  - Also I have tried the nUnitID set to: 0, 1, 16#FF (16#FF as specified by Beckhoff docs) This is my Beckhoff code:     PROGRAM MAIN     VAR         ipAddr         : STRING(15) := '192.168.88.1'; //Tried also 192.168.88.126 and 192.168.88.1 'localhost'         M0 AT %MB0     : ARRAY [0..3] OF WORD;         nValue         : ARRAY [0..3] OF WORD;         fbWriteRegs : FB_MBWriteRegs;         bWriteRegs     : BOOL;     END_VAR           IF NOT bWriteRegs THEN         nValue[0]                := nValue[0]+1;         nValue[1]                := nValue[1]+1;         nValue[2]                := nValue[2]+1;         nValue[3]                := nValue[3]+1;                  bWriteRegs                 := TRUE;                  fbWriteRegs.sIPAddr     := ipAddr;         fbWriteRegs.nTCPPort     := 502;         fbWriteRegs.nUnitID        := 16#FF;             //Tried setting this to 0,1 and it also and didnt work ...         fbWriteRegs.nQuantity     := 4;         fbWriteRegs.nMBAddr     := 16#3000;         //Tried: 16#3000, 0, 1         fbWriteRegs.cbLength     := SIZEOF(nValue);         fbWriteRegs.pSrcAddr     := ADR(nValue);         fbWriteRegs.tTimeout     := T#5S;         fbWriteRegs                (bExecute:=TRUE);     ELSE                  IF NOT fbWriteRegs.bBUSY THEN             bWriteRegs             :=FALSE;             fbWriteRegs            (bExecute:=FALSE);         END_IF                  fbWriteRegs                (bExecute:=FALSE);     END_IF  What should I change in my code in order to make this example work? Thank you in advance for any support!   Info about LabVIEW programs:  I am using the Modbus TCP Master / Slave examples  The IP address is set to localhost and the port to 502 (which should match the IP address in my Beckhoff code)  I am 100% sure it works because I have also tried connecting to this program via Python script. Picture of my LabVIEW programs:
  10. Hello, I am using Easymodbus library to Communicate with Modicon TM218 PLC. Reading and Writing of Holding Registers working fine. But coming to writing of single bit in data register i am facing Problem. Need to know how we find coil address of a data register. e.g I have to write bit 1 to MW70.1 address. How we do that. Right now i am reading complete MW70 Register and Manipulating it using bit manipulation techniques and again Writing using Write single Register Function. It's working but some times because of reading problem it writes some garbage values. At that time complete system effecting.    Please provide me any solution. Thanks in Advance. 
  11. Dear All, At the moment, I have project with PLC Delta and HMI Proface. I design HMI GP2500 by GP-PRO/PBIII ( V7.0). I see in List Device PLC of Software  not support PLC Delta.  Can you tell me how do you connect or Software HMI Proface ( Gp2500) support PLC Delta ? Thanks you very much.
  12. Fatek Ethernet PLC Module online

    Dear All,  Anybody can help me in communication between Fatek 20MAR2 & CBEH2A. The jumpers setting are JP1 is on left two pins (No password protected) & JP3 is on right two pins (forced boot operation mode). The Ethernet cable i used is type b T568. Fatek Ethernet module config software detecting module successfully (shown in attached pic) but on online PLC via ethernet cable its showing connection failed.   please help   thanks in advance
  13. Hello, I'd like to ask for a technical confirmation on using MODBUS TCP in a M340 + Fiber Converter Card (BMXNRP0200C) or Switch (ADAM 6521) + Fiber Optic patch cords and cable topology to communicate with a SCADA system. The main objective is to provide a fiber optic connection point inside a control panel because it is located in a area prone to electrical interference. The protocol to be used would be MODBUS TCP. We have two simple topologies in mind but we are not sure if they are feasible. So i'm asking for a little support about it. Considering the attached simplified topologies (Drawing1.jpg), am I able to use MODBUS TCP to communicate a M340 with a SCADA workstation with no problem? I'm not sure if the protocol allows this kind of change on the physical medium like if it was pure Ethernet.    
  14. hello Every one,    I am using a CP1-L PLC and want to communicate to domino ax350i printer over TCP/IP socket programming. For socket programming, I used Omron Function Block CPU012_SendCommand.  I defined network ID and node address. However, I am getting 0502 error which means routing table is not set yes. So, how can I set routing table for both devices?. my PLC on 192.168.250.1 and Printer is on 192.168.250.123 node 7000.    Can any one suggest me best way to do.  Thank you   attached file is for what I did in setting and program for the communication.      
  15. How to enable modbus in mitsubishi plc

    hello there, I have Mitsubishi FX3G 24m PLc which has an ethernet port for communication port. how to enable Modbus TCP/IP for data collection of sensor values and sending it to a 3rd party. If this has been answered pls link to the thread.
  16. Monitouch HMI slow screen

    Hi there! I'm having some issues with a FUJI MONITOUCH V9100iSD HMI that communicates with a CJ2 PLC via Ethernet. This HMI is a migration from a previous V810iSD model. The thing is that the previous model worked correctly, but when using the new one, the HMI seems to be pretty slow when switching screens, for example. All parameters are the same, and after reading Fuji's FAQ, I've run out of ideas. Have you faced the same problem? Thanks in advance!
  17. FX3U to FX3U via wifi

    Good day fellow PLC ninjas! I have a question/ concern which I would love your opinions on. We have 3 FX3U PLC’s+ENET cards. Two of the 3 PLC’s move around in an EMS trolley. The other is a ‘base station’ with a GOT2000 connected via Ethernet. Base PLC IP = 192.168.1.11 HMI IP = 192.168.1.31 Carrier 1 IP = 192.168.1.61 Carrier 2 IP = 192.168.1.62 I have programmed the base PLC to use Active communication; we are using fixed buffer communication to send and receive data to/ from the Carriers. The carriers are set up as Fullpassive ‘slaves’. This part works well and the update time changes (using a counter in the base station) from 1s to 100ms (because it enters a different work station).  My issue is the following: using a network sniffer (WireShark), I pick up plenty of re-transmits and sequence number errors coming from the base PLC’s ENET card. This is troublesome and causes delays when the update time is required to be fast (100ms). I am sending and receiving 10 words of data. The wifi seems stable, and there is minimal noise in the area. The power has been turned down and the antennas used are suited well for the application. The antennas are at a similar height to minimize possible loss of signal. I have LOS (line-of-sight) to the carriers at all times; to at least one of the antennas (I am using 802.11n). Has anyone picked up issues or found settings which can be used for comms over wifi? I can easily do this using a S7-1200 Siemens PLC and have done so using 12x S7-1200 clients and 2 AP’s with 1 base PLC. I have also successfully done this using 8xFX3U client with a System Q base PLC. My suspicion is that the delay in reading and writing to/ from the BFM in the ENET card is causing this. I am not sure that if I change to a FX5U will help. The communication cards on the Mitsubishi PLC’s seem very limited. Does anyone have any technical details on the access times between the CPU and communications cards’ BFM? Help is as always, appreciated.
  18. CP1L Unknown IP

    Hello. I have CP1L EM30 with unknown IP. I have tried to use "Direct Ethernet Connection" with "Network Browser" but with no success. I have manually set the ethernet IP4 address to 192.168.20.20 / 255.255.255.0 I've got error: "The OMRON Ethernet Direct Connection Manager service is starting in Safe Mode because Windows APIPA is enabled. (0x82020003)Omron.Cxmw.Modules.SystemLibrary.SysLibException" The PLC does NOT have default ip 192.168.250.1. What Can I do? Please help. Thanks. BR, Andrej.  
  19. Hi all, First i apologise for my english, but it's not my main language. I am very new at this world so sorry if my question is too newbie but i have been for several hours trying to get some data from an Omrom NPX1P2 DT-100 using Ethernet/IP and now i am a bit desperate. I am trying to connect this PLC using a C# Library provided by steffan rossman and it seems to be very easy,  i can manage to connect it but every try i do to request data it fails. As i can see there are several ways to get the data, for example: In this example the function GetAttributeSinglec(ClassID, instanceID, attributeID) i need the ClassID, wich i don't know what is, the instanceID, i think in my case is 100, and the attributeID wich i don't know what is or where to define. If someone could help me about how to request data it will be very appreciated. Thx in advance    
  20. My HP laptop will lose communication with Mitsubishi PLC occasionally after removing ethernet cable to download from WiFi. Our company limits the ability to use the wi-fi when I have an ethernet cord connected to my laptop, it has to do with security. If I am connected to the Mitsubishi PLC, then want to download another file from our autosave, which we connect through the wifi, I have to remove the ethernet cord from my HP laptop to enable the ability to go wireless, however sometimes when I attempt to go online with the PLC after I re-connect my ethernet cable, GX developer will not allow it. I can ping the plc and even go online with other PLCs on the network, but for some reason, the one I was connected to will not connect. I restart my computer and even re-download the file again from autosave but no joy. Its not until an unknown amount of time that it will allow me to re- connect, its as if I lose the socket connection on the plc and it needs time to reopen. I talked to our IT department and they have no ideas. Thank you in advance for any help on this matter.
  21. Digital sealing

    Hi, I'm trying to figure out a way to make an automatic digital sealing for a NX-controller. Functionality: Each time I do a remote connect and/or change to the program on the PLC via VPN/Tosibox I want a counter to automatically increment. This counter is the digital sealing (checked by the authorities from time to time), and is displayed on a HMI. When the sealing breaks, the new value of the counter has to be reported. I've been thinking about incrementing the counter each time the Ethernet port on the PLC registers a rising edge on online establishment. But this will not work if there is a power failure (then the counter will increment unitented), or someone by mistake unplugs and replug the Ethernet cable. Antoher idea was to ping a specified IP-address, but there seems to be no PING-functionality. I've also been thinking about using some program data (i.e. last modified), but it seems there's no system variables on the PLC that contains this kind of information. Any ideas how to solve this in the PLC? Basically I want to know if the PLC program has been changed or if there a specified IP-address has been connected to the PLC-network.
  22. How to scan Ethernet/IP network?

    Scenario: You show up on site and the only knowns are Omron PLC and EtherNet/IP network. You have a laptop loaded with CX-One, an ethernet cable, and the ethernet port that is connected to a known EtherNet/IP Omron network (you can not see the PLC). I have previously worked with Siemens systems and used Primary Setup Tool and Proneta with wonderful results. Do similar tools exist for an Omron environment?  Question: How to (relatively quickly) scan an EtherNet/IP network for connected devices without knowing their ip addresses?  
  23. Hello, Has anyone got an Omron PLC NX1P2-1140DT1 running with Modbus TCP/IP? I tried to reach Schneider several times, but there is "live" or email to discuss or get help, has to go to thru someone from Mexico then he will email to France. All of my attempts was lost, I can establish a "CONNECTION" but I can't READ the Coil - I got the error "Gateway Path Unavailable" (that means  "Used alongside gateways. Basically, this code means the gateway couldn’t allocate an internal path to process the request. Therefore, the gateway could probably be misconfigured or overloaded") My program is based on the MTCP_Client_NJ_E (Revision 2.3 date 23/07/2021 - JP Viskovic from France) I can read the coils using MODBUX Doctor (France) but I can't make work with Etherway. Any advice is welcome. Thanks   MTCP_Client_NJ.slr MTCP_Client_NJ_E.pdf
  24. If this has been asked and answered already, please point me in the right direction. I have a production line that uses Gefran Geflex temperature controllers on a Modbus and Machine Net communication system. The main control panel (MCP) is the master on the Modbus and communicates directly with 3 slave Geflex units (Group Leaders?) which then communicate with the others in that group via a Gefran Machine Net type interface (ribbon cable daisy chained from one unit to the next). The issue is twofold: These temperature controllers are slowly becoming harder to find AND they are a PITA to change out because they have to be put in place and then properly addressed using software on a laptop. This means more downtime waiting for someone who knows how to set these up to get there to do it say on a weekend/middle of the night type situation. (I do like my beauty sleep). I'm looking to replace these units with standard SSRs and control them with a PLC (P-2000 most likely). What I would need to be able to do is interface between the MCP and PLC in some way that the MCP still believes it is controlling 24 units (24 Modbus IDs) and have the PLC receive the reads and writes from the MCP and know which ID it was meant for in order to set the SV and respond with the PV and/or alarm codes as that ID. I hope that all makes sense. Basically I need a way for a PLC to act as if it were 24 separate Modbus slave units. Could I just use a separate HMI next to the MCP? Yes, but there are temperature dependent routines in the main operation of the line (extruder run inhibit, etc.) that requires the information reported back on the Modbus. I've looked into Modbus Gateways but the MGs I've found so far don't seem to be capable of assuming the role of 24 different slaves and interfacing with the PLC in a way that would allow the individual control.  Any ideas would be greatly appreciated.