Search the Community

Showing results for tags 'digital input/limit status of lexium 32 a drive'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 107 results

  1. This is a bizarre one... CompactLogix, 1769-IF8 with 1492-AIFM8-F-5 wiring system. My client has reported several instances where one of his flow rate displays is frozen at its maximum value.  Each time, I have gone to the site, found that the value in the analog input tag is at full scale, and measured more than 20mA at the input - as much as 28mA!  I measure it using a clamp-on meter and I measure it at the input module (1769-IF8) and the external, pre-wired terminal block (1492-AIFM8-F-5).  I cycle power to the PLC.  No change.  I cycle power on the transmitting device.  No change.  I disconnect and reconnect the input (signal wire at the module or the terminal block) and everything goes back to normal.  This has happened on multiple channels on multiple input modules and with two different types of transmitters. I didn't install this system, but it seems to have been done properly and it had been running fine for many years.  These problems just started happening out of the blue. Has anyone out there had any similar experience?  This is a new one for me after more than 25 years in the business.
  2. Analog Input Addressing

    Hello Everyone, This is first time i am using Omron's CX-Programmer. PLC-  CP1L-EM40DT1-D I have 2 built in analog input of 0-10V on PLC Board. I want to know the default resolution, Data Type and Register address to detect analog Input for my further programming. Please Help me with these...
  3. Is there any reason not to have input and output modules on the same rack as the processor and Ethernet cards? We have RIO’s and sometimes have networking outages, I want to move critical IO to Rack0 the same rack as the processor, is this bad practice?  I've seen architecture for BMS that only have Ethernet cards and processors in Rack 0... 
  4. PLC Not fast enough?

    Hello, I used a Schneider Electric SR3B261B PLC to create a trivia machine (as I call it).  Basically 20 buttons that let contestants ring in to trivia.  There is a display that shows the number of the person who rang in.  It works pretty well unless people press the buttons at exactly the same time.  Then it shows 2 results at the same time.  Usually resulting in a display of 18 when really it was 12 and 14 that rang in, for example. The PLC has options for: "Adjustment of the basic cycle time of the module."   and "Type of Hardware Input Filtering." Which I assume would make the PLC operate faster and avoid two inputs triggering at the same time.  If I change the setting and update the changes do not keep.  I appear unable to change it past 20 x2 ms  and slow (3ms). Is that a correct assumption that changing this would fix it? Why can I not change this?  Is it because I have so many inputs (14 or so) and Outputs (16 or so)? or because my program uses nearly all 240 lines of ladder logic allowed? What can I do to fix this?   Emerald
  5. Control Panel

    Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software?  I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously.  Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
  6. Hi Everyone! I need some help with configuring an inverter. The inverter type is powerflex 70. How can I set the next parameters. It should be work with two speeds.  First:  around 40 Hz.  Second around 10 Hz.  I think first I need to decide the direction, So I need two digital input for forward and reverse. Then I need plus more digital input, one for the high speed and one for the low speed. I guess I have connect dc 24 V too. I just dont know where should I connect this signal. I didnt find the properly manual. Do I forget something ?  Can anybody help ?  Thanks in adnvance!
  7. Omron Hardware

    Please let me know if it is allowed to sell PLC hardware on your forum. I accumulated lots of Omron hardware  that I want to get rid off. Here is the list, I have several of each type, asking $12 each plus shipping. All in working condition.  Base Unit C200HW-BI051 Base Unit C200HW-BC101 16 Point DC Input Module C200H-ID212 16 Point Digital Output Module 24VDC C200H-OD212 Power Supply Module C200-PA204    
  8. Anyone have experience with the Peak to Peak hold function on Keyence IL-1000 amplifier?  I have an IL-030 lase head running off it and I want to utilize the peak to peak hold function.   I connected the red wire from a generic 24VDC, 1A, power supply to the IL-1000 Pink/Purple (timing input wire) and the black wire from the power supply to IL-1000 Blue (0V).   I have a 24VDC, 5A, power supply connected to IL-1000 Brown (10-30V) and IL-1000 Blue (0V) to power the IL-1000.   What I thought might work is to plug the 24VDC, 1A power supply in and out of an outlet to trigger the timing input for the P-P hold (similar to an on/off button).  But it's not doing anything.   I am not an electrical guy.  Any tips here?  Thanks,
  9. HI I'm using PlC5/20 when I click on setup screen on the BTR block (to view the analog input configuration) i find the following message: No modules exist in the IOconfiguration for this R/G/M however the analog input signals is running properly....i just want enter the setup screen for configuration. I'm assuming that I need to enter I/O module in the I/O configuration? Can I do this without taking PLC to Program mode?  
  10. Hi all. I have a Kinetix 350 and an AB TLY servo motor. I'm using the drive's STO function. AC power is supplied into the drive, passing through an "M1" contactor. It makes sense to m e to keep that contactor open, preventing AC power to the drive, until the drive is fully awake.  Is that what you guys do? Someone suggested to me in another forum ( http://www.plctalk.net/qanda/showthread.php?t=121021&highlight=drive+awake ) that there is no reason not to supply power to the drive right away because the STO function is inhibiting power to the motor anyway. 
  11. In One of my machine we using one stepper drive thatCTA2H328M-MB model made by Centrust Motors China running without pulse input.Direction and  Enable input only connected. My problem is motor running in low speed since drive is 2.89 Amps and motor is 4.2 Amps so its not supporting.I want change drive capacity but i couldn't found a drive with same concept.I couldn't able to reach the chinese vendor.I have tried many drives which is in my stock all are enable input used for enable/Disable the drive.I am bit confuced. http://www.centrust-motor.com/?c=msg&id=2337 Kindly help what type of drive is this? Which model will suitable for my requirement?  
  12. Hello everyone, I'm currently trying to communicate  via ethernet with a Parker drive IPA15-HC. I'm using a 5069-L306ER CompactLogix 5380, revision 30.011. There are add-on instructions that allow you to control the drive, but since they're really basic I'm trying to use message instructions to get more data out of it.  The knowledge base provides a zip named IPA_AOI_Rev4, that includes the add-on instructions and the program you should download to the drive to use them, this is the current file downloaded in the drive. Now, I've tried different msg configurations: CIP Data table read, CIP Data table write, CIP Generic copying the values in the examples and I always get the same:  Error Code: 16#0001 Extended Error Code: 16#0000_0125 That extended error code is nowhere to be found, not in the Logix designer online help and not in rockwell's knowledge base. Any idea?
  13. ZCP Instruction

    Hi group! I am struggling to figure out what I am doing with the Limit instruction (ZCP 088).  I want to turn on a permissive if the compared word is between 1 and 12.  Rockwell makes this so much easier!!! It looks like my "=" instruction is not correct but this is how they show it in the manual???????    
  14. High-Speed Counter Input

    Hi, I working on reading impulse from the input. I am using M8000 as a contact, on the coil [C235 K9999] and it is working fine on the lad, but the problem is I need to applicate sth like that in structure ladder but I dont know how. I found function on the image below but it is for FX3U. I know that 2-phase 2-count input use OUT_C(for example EN True| CCoil CC251| CValue K0) and then DMOV(for example EN True| s CN251| d D100), so is there any method to read impulses from the input? .Thanks in advance. PS I have Mitsubishi FX3G series.  
  15. QJ71C24N INPUT PROBLEM

    I am using QJ71C24N to communicate with my devices, ASCII mode. I can send my output to the device by using non-protocol method ( G.output). However,  when I using G.input to try to receive the feedback from my device. The signal seen not stable to receive by my PLC. Sometime can get the full signal sometime can't and sometime I get some messy signal. Is there any setting I need to set to get the stable feedback from my device? Please anyone can help me to solve this problem? 
  16. I'm sorry, guys, but I wouldn't be asking if I hadn't dedicated about 12 hours to this already. Long story short: ACS800 with RPBA-01 Profibus Adapter and RTAC-01 Pulse Encoder Interface. All we send to the drive (aside from CW permissives) is a position reference, and I believe the DriveAP functions execute how the drive will achieve that position. My final aim is to separate the encoder from going back to the drive, to instead going to a FM350-1 Counter module. I'm following someone elses work that is long gone, has been changed multiple times, and comments are almost non-existent. Where I'm stuck is understanding the data coming from the drive and being sent to it. PPO Type 5; DPV 0. In Step7, I have a DB for 20 bytes of data to drive and another DB for 20 bytes received from drive. I understand (with respect to data from drive) that it should be: SW; ACT; PZD3...PZD10 (10 x 2 byte Words). But, when I looked through all the settings in the group 51 parameters, the values in the form of (xxyy; index then subgroup; ex: 106 is parameter 1.06) don't seem to exist in the ACS800 Firmware manual. PZD 3 OUT: 7 --- PZD3 IN: 6 PZD 4 OUT: 8 --- PZD4 IN: 10 PZD 5 OUT: 0 --- PZD5 IN: 106 PZD 6 OUT: 0 --- PZD6 IN: 0 PZD 7 OUT: 0 --- PZD7 IN: 611 PZD 8 OUT: 0 --- PZD8 IN: 612 PZD 9 OUT: 0 --- PZD9 IN: 701 PZD 10 OUT: 0 --- PZD 10 IN: 706 The manual says parameter values 1-99 refer to a "Data Set" and each number specifies a certain word in a Data Set. For example, PZD3 IN: 6 refers to Data Set 2 Word 3, which is defined by paramater 92.03. But, that turns up something about short circuit protection, when what my DB value is displaying a distance (from a linear string pot encoder) that matches what the mill is actually at. The ACS800 manual says Data Set Actual Signal words are defined in Group 92. So I looked there: 92: DS Transmit (From Drive) --- 90: DS Receive (From PLC) 92.01: Status Word (Fixed) --- 90.01: 4501 92.02: 103 --- 90.02: 4309 92.03: 402 --- 90.03: 4505 92.04: 412 --- 90.04: 1 92.05:106 --- 90.05: 3 92.06: 0 Any help would be appreciated. Thank you.
  17. My subcontractor use ABB ACS580 instead of ACS880. They argue that can program to control crane with it. Load capacity and motor power is no problem here, but the purpose of inverter I concern here. Is there any advice?
  18. QJ71C24N-R4 G.Input command

    I need some help with G.input and g.output commands. I have a Q04UDEHCPU and my slots are as follow: slot 0 - QJ61BT11N cclink slot 1 - QJ61BT11N cclink slot 2 - QJ71C24N-R4  2-channel RS4222/RS485   I need to have 2 separate RS485 stings going to different devices. I cannot find the way of setting up the g.output command. G.Output "Un" (s1) (s2) (d) "Un" says it is the start I/O signal of the module, but I am not sure what that means. What there be a different "Un" number for each channel?   
  19. I have 200W - 200VAC : Omron R88D-1SN02H ECT Servodrive and Omron R88M-1M20030T BS2 Servomotor I wish to make myself the connection between Drive and Motor , with self made cables. Connectors ( JAE ) - Japan Aviation Electronics JN6FR02SM1 - 2 pins - brake cable in motor side JN6FR07SM1 - 7 pins - encoder cable in motor side JN6FS05SJ2 - 5 pins - power cable in motor side Molex 55100-0670 - 6 pins - encoder cable connector in drive side - ( IEEE 1394 - Firewire 400 ) https://assets.omron.eu/downloads/manual/en/i823_1s-series_setup_manual_en.pdf http://multimedia.3m.com/mws/media/569007O/3mtm-i-o-interconnect-system-2-0-mm-for-ieee-1394-ts2296.pdf http://www.jae.com/z-en/pdf/MB-0161-1E_JN6.pdf https://industrial.omron.mx/es/media/I586-E1-02_1S-Series_EtherCAT_UsersManual_tcm851-112757.pdf ======================================== How can i know which it's pin #1 from each socket from Drive and Servomotor ? Atention !!! I'm not talking about pin numerotation from connectors which i connect to drive or motor . I wish to know the pin #1 from Drive CN2 socket and from Motor sockets ( power , brake and encoder ) http://www.jae.com/z-en/pdf/MB-0161-1E_JN6.pdf In MB-0161-1E_JN6.pdf you can see the numerotation of pins from "Receptacle" . That means , the "Receptacle" it's that part what is in Omron Servomotor ? Or it's the part of JAE connectors , which it's inside of connector housing ? The question is , how can i be sure i don't make a mistake, and i know the right numerotation of Encoder socket of Omron Drive : CN2 and the right numerotation of Omron Servomotor ( brake , power and encoder cable ) I've found schematics about how to connect the Drive with Motor with power , brake and encoder cables , but i didn't find a pin numerotation of sockets ( drive side CN2 encoder socket and power , brake and encoder from motor side ) I didn't find nowhere the right numerotation of pins from CN2 socket of Drive and from Servomotor sockets ( i find it something from above JN6 series connectors from JAE connectors ) I wish to know where can i find the numerotation of pins from Omron R88D-1SN02H ECT Servodrive and Omron R88M-1M20030T BS2 Servomotor Specially , the Encoder cable numerotation from Drive side and Motor side . I've noticed in attached picture the numerotation from Drive , CN2 encoder socket ( IEEE 1394 - Firewire 400 ) . That's correct ? It's right numerotation ?              
  20. Hi,   I am using Omron CP1E NA 20DTD with built-in ANALOG inputs and output. I know how to deal with digital inputs. But I have no idea about analogue input wiring and programming. I tried connecting gefran LVDT PY2 directly to an analogue input of plc. But the indicator light did not turn on. Do I need to use any signal conditioner or converter? The output of lvdt is 0 to 25volts. I HAVE ATTACHED THE DATASHEET OF LVDT. DTS_PY2_06-2016_ENG.pdf
  21. [Manuals] - 3G3HV User's Manual

    3G3HV User's Manual View File Older Omron AC Drive Submitter Michael Walsh Submitted 10/03/17 Category Manuals
  22. 3G3HV User's Manual

    Version I515-E1-3

    10 downloads

    Older Omron AC Drive
  23. I'm looking for some general information about different types of vibration/temperature sensors. What type, brand, model number, etc. will best fit my application.  Scenario: I want to monitor the vibration and temperature of multiple motors and gearboxes for a large overhead conveyor system. If an oil leak occurs and temperature increases, I want to see a temp. alert via a HMI. If a something mechanical fails, I want to see a vibration alert via a HMI.  I've looked into sensors that stick to the outside housing of the motors or gearboxes via a magnet. My concern is justifying the temperature readings. How accurate would a sensor that reads an "ambient" temperature be (compared to a thermocouple on the motor coil itself or some sort of probe)? Also, would the location of the magnet  on the motor or gearbox drastically affect the temp. or vib. readings? Has anyone had success with a similar setup? If so, what devices did you utilize? Are these systems truly beneficial?  I'm currently considering Banner's wireless products...
  24. Hi, I was wondering if there is a way to limit the number of allowed on-line connections at a time to a PLC? Like can you somehow set in the PLC parameters that only 1 'connection' can be on-line in the device at a time? Thanks Edit: I'm referring to connections from the TIA portal - not HMI / ethernet connections and so forth
  25. Hello, We have this SCADA system Vijeo Citect 7.2 running in Windows 7. Primarily used as generator's alarm history & monitoring. PLC: OMRON C200HG All communications are good but DIGITAL data (alarms, bustie) from OMRON is not updating in real-time. (Need to restart the Vijeo Citect to make it work).  While BCD & LONGBCD datatypes (voltage, speed current) are working good and showing real-time *OFSVIJEO: INT datatypes are also working good. Protocol UNITY         MODNET30 OMRON      OMRON OFSVIJEO  MODCELL