Search the Community

Showing results for tags 'diagnostic of profinet communication'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 211 results

  1. MC protocol

    Hello once again, before I'll dive into mitsu manuals, does anyone of you know if there is some special relay signaling that PLC (FX3GE) have lost communication via MC protocol? Thank you in advance
  2. 2 PLC WITH ONE HMI

    hi.   Can i connect two plc mitsubishi with one hmi . is so .. can u guide the connection between them . Hmi is of weintek.  one plc is FX1S and the second is FX2n
  3. hy everyone.. I want to communication inverter SJ700 to hmi mitsubishi GS2017 for read an code error in interface HMI? is it possible to communication between them?
  4. Hi everybody, I have a GT2310 communicating with the Mitsubishi F800 VFD. I am using the Freqrol 800 communication driver, connected to the RS-485 terminals of the GOT and on the F800. The comm settings are the same on both devices. I also tried to use the “auto negotiation” setup. I have communication between the two devices. I can read and write to F800 registers.   Anyways, The GT designer diagnostics is complaining about a communication error in the system alarms. The error can be reset but it will appear again.   This also happened when I created a new, empty project where just the communication was setup as described above.   Did anyone experienced the problem and how to troubleshoot / solve this?   Best regards
  5. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  6. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  7. Hello I have a problem with dl-ep1 ethernet modul. I connected the module to a IL-1000 sensor amplifier. There is some problem with the communication. How should I adjust ? I made some pic about the trouble. The sensor is a IL-600 laser distance sensor. I dont know yet how can I get the actual value.  Anybody knows how to set this modul ? If I think correctly after the right setting, if I check the sensor output:0 then, I can see the actual value of the IL-600 sensor. But unfortunatelly this part also not so clear for me, because I can connect about 15 sensor this ethernet modul.  Thank you so much if anybody help.
  8. HI All, i am new to this site, if anyone can help me out for below topic. I am trying to communicate E1101 hmi with Q06UDEH PLC but its giving me continuous communication error. i am using e designer for hmi and gxworks2 for programming. i am attaching the communication screen shots for both,i am quite stuck at this point as i have used all options still not able to solve it. if anyone can help me out with this,help is much appreciated. Thanks in advance  
  9. error HMI in proface GP477R-EG11

    Hi everybody, can someone help me, to solve my problem with commnunication error. ??? I have plc Q03UDVCPU using module QJ71C24N and HMI proface GP477R-EG11  using RS 422.. I had connected them but still error.. Side hmi that im connect is 10 RDA to SDA 11 SDA to RDB 15 SDB to RDB 16 RDB to SDB 7 SG to SG  
  10. i am new in indusoft web studio. i am facing a problem about communication of indusoft with plc.   i am communicating with plc through fx2n-422-bd card.   can some one guide me the steps of communication.  he/she will be a life saver.. as i am  in a deep trouble
  11. CP1E RS232 communication to my weighing

    hello, i want to connect CP1E to EK300i (weighing scale) with RS232 communication. i attach file of datasheet ek300i, wiring CP1E to ek300i and my cx programmer. if i push send data on ek300i, com LED indicator in CP1E is on. and i dont know why my cx programmer can't change data of memory with data from ek300i? what should i do?   ek300i.pdf CP1E to EK300i rs232 communication (belum dicoba).cxp CP1E to EK300i rs232 communication (belum dicoba).opt wiring rs232 ek300i to CP1E (belum dicoba).txt
  12. Hello every one. I have three FX3U plc needed to be communicate over a wireless network. I'm using serial adapter FX3U-485ADP. I got E-byte data trans reciver E-30 for wireless communication. Now need help to setup the whole thing. Previously the PLC's serial connectors were connected through a flexible bus but when the platforms are running fast there is interruption in the  communication. So we want those PLC's to be connected over wifi.  Thanks in Advance 
  13. Anyone know any free libary to communication with FX3u-enet-adp, please help me ? Note: I've used mx Component , it work very well but it is too expensive and I dont even know it can work in windows server 2012/2016 or not.  one more question, Is there otherway to make program run in other computer without install mx compoment, it is very huge to install in every client computer Thank for reading and sorry for my bad english  
  14. i am using a VSD Altivar71 and controlling it through serial MODBUS communication, the probllem is sometimes after stoping the motor the drives gives the "nst" fault which means according to the programming catalouge "freewheel stop" it doesn't do that all the time but it happens a lot and after uploading the code again to plc the problem is gone for a while before it happens again. i am sure that the fault is happening because if communication because when i controll the drive from hmi it never gives that fault, i checked the setting and tried different cables but it still gives "nst" and motor never moves, i found that in catalouge but i am not sure how to address the problem.
  15. Hi everyone, I just want to layout the structure of the question. I have a GOT2000 (GT27* series) that I have hooked up and communicating with an Allen-Bradley PLC. I have established connection and can pull out certain tags values from the PLC program in RSLogix 5000. While I can read the tag values, I cannot modify them (in certain conditions).  So let say that I have a User-Defined Structure named "Smoke_Detector" and here are it's available members: Smoke_Detector:   - ALARM (BOOL)   - ON_TIME (DINT) * DINT in Allen-Bradley but Signed Binary 32   - Battery_Life (REAL)  My question is that while I can read and display the tag and its members through the following:   - LAMP for Smoke_Detector.ALARM   - Numerical Display for both Smoke_Detector.ON_TIME and Smoke_Detector.Battery_Life But when I tried to modify the values via a Bit Switch or Numerical Input, it does not operate on them.  However, if these tags are members are just standalone tags, meaning that they are not within a UDT in RSLogix 5000, then I can operate/ modify them just fine.  Here are the things that I have tried: * Making sure that the permission are set to Read/ Write in RSLogix 5000 * Making sure that the tag definition in GT Designer 3 follows the structure where @[channel]:[Network #]:[Station #]::[Tag instance and member (e.g Smoke_detector is the instance and Alarm is member] Any possible insight and input are appreciate! 
  16. Hi all !    I need a help about connection between mitsubishi GOT Simple series (gs2110) to kawasaki robot via crossed ethernet cable on tcp/ip protocol. I actually have a fx3g for main unit of my project, and also i have a kawasaki robot for slave unit. My purpose is basically to control both with HMI. I used RS422 between plc and got gs2112 and I want to use a crossed ethernet cable between robot and got but i did not communicate with ethernet even between pc and got. There is a manuel which I found on internet about GOT2000  Connection Manual (Microcomputers, MODBUS/Fieldbus Products, Peripherals) I think i need to work on  microcomputer connection (ethernet) subject, what do you think about that ? I need all advices and ideas which come from you.   [ROBOT]--------Ethernet--------[HMI]--------RS422--------[PLC] https://electrobit.ee/web/file_bank/Manuals/operaatorpaneelid/mitsubishi/GOT2000/GOT2000-connection-manual-ENG.pdf
  17. Hello All, What are the methods to get the monitoring data from A series PLC? I know its not supported any more, interface modules are not available...,    So the basically,   If I want to write customer software (may be embedded) what is the protocol I need to follow? I am connected to CPU unit by the way, there is no other modules except few digital and analog interfaces on PLC. Thank you in advance for your direction, direction in any way would help!
  18. Hi guys,  I have been trying to sync up my RSLogix 5000 tag to GT Designer 3 (GTD3) objects but I noticed that GTD3 only recognize certain native data types from Allen Bradley Logix5572 Controller (Model 1756-L72).  In the documentation that I found, it show that certain AB Native Tags are transferable to GTD3 Data Type (See the attached file "AB Tags to GTD3 Tags" ) One of the User-Defined Data Type from the RSLogix 5000 that I am trying to sync to Text Display Object in GTD3 is called "UDT_MY_CLTR_INFO" here is it's hierarchy of inheritance from RSLogix 5000     Name                                                                     Force Mask                                                                                   Data Type MY_CLTR_INFO                                                     (...)                                                                                                 UDT_MY_CLTR_INFO      MY_CLTR_INFO.NAME                                                                                                                                           STRING           MY_CLTR_INFO.NAME.LENGTH                                                                                                                      DINT           MY_CLTR_INFO.NAME.DATA                                                                                                                           SINT[82]    In my exported tag which is a CSV file, it doesn't list the sub-classes MY_CLTR_INFO.NAME, MY_CLTR_INFO.NAME.LENGTH, and MY_CLTR_INFO.NAME.DATA, it would only list MY_CLTR_INFO.  How do I link up my "Text Display" Object in GTD3 with the tag "MY_CLTR_INFO.NAME" whose Data Type is STRING and GTD3 does not have a STRING Data Type?  I appreciate anyone that took their time to read my problem and any attempt to help me out. Thank you. 
  19. C200H communication issue

    Hi We got 2 laptops Laptop1 communicates with a CJ1M and a C200H PLC. No problem. Laptop 2 communicates only with  the CJ1M, Not with the C200H, Same program, same conditions. I also tried with "Direct online" but no succes How can I get laptop 2 also to communicate with the C200H? Thanks
  20. Hello,   I need to communicate a Datalogic Qw2120 ( with a USB connector  )  to a Modicon M251, it has a RJ45 Serial, i don´t know where to start , can anyone please give me a hand ? I would appreciate it very much.    
  21. Hello,   I need to communicate a Datalogic Qw2120 ( with a USB connector  )  to a Modicon M251, it has a RJ45 Serial, i don´t know where to start , can anyone please give me a hand ? I would appreciate it very much.
  22. Dear all, i have using nexgenie 1000 cpu for my new project. but i am not able to connect with codesys v2.3 . I have installed target file T1.4 and T2.4. trie with both. Now i have doubt with communication cable. I have used standard RS232 Cable with 5and 8 Pin short. Kindly suggest the correct one. Thanks in advance
  23. Modbus/TCP PN communication

    Hello, I'm trying to make communication between a 315-2 PN/DP and MSA Gasgard XL. I want to read out 40010, and 40020 from GasGard, it works sometimes, but most of time the connection does'nt  build up.  The parameters i using are: Start address: 9 Lenght: 10 Recv_Time: 5s Conn_Time: 5S I did playing with Recv and Conn Time and it effected the rate of succesful connections, but it still drops too often. Also i tried to read only 9 and 19, but then it didn't read 19. Anyone knows how could i optimize the connection? Thanks  
  24. All, I am using Keyence CV-X422A vision controller for my application. It is interfaced with Siemens S7-1500 PLC on PROFINET. I am able to communicate with Vision controller through PLC logic command and status IOs. There is some communication issue in updating the o/p values from Camera Controller. I have tried with & w/o Handshake Mode with these settings. The camera display shows the reject but camera never turns ON the NG Status o/p. I tried different things told by Keyence Tech support but none of them worked.  He told me to have you enable the “Result ACK Flag” in the bit allocation area and send  a signal to it. Then trigger it again with a no good part and see if that fixes the issue. I tried setting the “Result ACK Flag” to 1 after I get the “Command Complete Flag” for the trigger signal that I sent. Sometimes this works but still it is not reliable. Do I need to send only a pulse to “Result ACK Flag”? Anyone here has ever faced similar issue?  Thanks for your help. AP