Search the Community

Showing results for tags 'datalink cj2m ethernet ip fins communication'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 341 results

  1. Hi All, Am trying to communicate and make In-Sight bar code reader to trigger through MicroLogix 1100 with RSLogix 500.  Does any have any info as to the steps to follow. Most of the info I saw and have tried were for SLC processor In fact, I created the String file ST10:0  for the target device as was mentioned in one of the posts but when I complied it there was error saying that St10:0 was not supported by the module. Please see attached file. Any insight will be appreciated  
  2. LOCAL MELSEC COMMAND

    Hi everybody,  Is it possible to send MELSEC commands to oneself, locally, not using the phiysical ports? I would like to use some commands described in the "Communication_Protocol_Reference_Manual_(MELSEC)" to get some self-management functions in my PLC.  For example, in OMRON this is possible using CMND instruction and setting the FINS address to 0.0.0 in the parameters of the instruction. Thank you very much. 
  3. Hi everyone. I have project to use PLC Mitsubishi Q03UDECPU with QJ71EIP71 to connect with SICK FLEXI soft Ethernet/IP (FX0-GENT00030). I have check both manual but when I turn on Y0 (communication start) there are error code F100h on my QJ71EIP71 and I check that it can only use with produce/consume tag from PLC (such as OMRON, Allen Bradley) but for SICK device it can use only for assembly instance. Then I have use Ethernet/IP scanner (Molex) to read attribute (service code 72h) then I can read status from SICK but as I told before QJ71EIP71 can only communicate with tag-based. Then I have to ask everyone that 1. Are there method that can use QJ71EIP71 to communicate by use Assembly Instance? 2. Could I set consume tag name on FLEXI soft Designer? 3. Are there any protocol gateway device that match with these solutions?
  4. Diagnostic of profinet communication

    Dear Experts, I want a sample block to find out the status of my Profinet cable w.r.t Hardware configuration. whether the cable is connected or disconnected from the node. Either my nodes may be VFD, HMI, SCALANCE, etc...  please share the sample blocks... S/W ===== >Tia portal v14 sp1 update 6  H/W ===== >CPU 1214C DC/DC/RLY hanks in advance
  5. Hello! I have a problem with Allen-Bradley High Speed Counter card 1734-VHSC24/C. I need to make changes to the configuration parameter .OnValue1 (DINT) during the system is running. Now, for changing the parameter value, I need to switch off the module and this can not be done during the line is running. I think that maybe this can be done using the explicit messaging. I could not find information for this from internet, so now I ask you to help me with this item. If anyone have experience or knowledge of this, please help me. I do no have experience using explicit messaging. My configuration: Studio 5000 Logix Designer V24.00, 1756-L71S V24.11, Ethernet/IP, 1734AENTR, 1734-VHSC24/C countermodule.
  6. Heavy Ethernet Problem

    Hi Dears, I have one heavy ethernet network I have 21 station PLC (S7 300) that each station have one server & I have one server that connected to all of this PLC in center. all servers are in one ethernet network I want to know that this configuration is ok? ethernet network can support these number of servers? or may be network fail?
  7. Fatek PLC Communication Problem

    hy all. i am having an error while communicating with fatek plc. when i communicate it gives an error. " Com port open fail, plz check if this port is used by other programme when we online the PLC (Fatek/ WinProLadder). kindly Guide me   as it looks like port is already used by another program . and i dont know how to kill that program ..       
  8. Network Number Problem

    Hi,  I am trying to connect a new CJ2M-CPU31 to a used NS12-TS01B-V2 (it seems to be restored to default). I want to connect that using Ethernet.  In the Cx-Designer I have set the following for the NS ethernet Port:   - Ethernet: Enable   - Net number: 1   - Node number: 5   - UDP Port: 9600   - IP address: 192.168.140.5  //  255.255.255.0  //  0.0.0.0  //  0.0.0.0 And the following for the host:   - Name: CPU_A   - Type: SYSMAC-CJ2   - Protocol: Ethernet/IP   - IP Address: 192.168.140.10 In the Cx-Programmer I have set the same IP address for the PLC from the I/O table configuration.  However, they are not connecting. After some seconds the HMI shows a Time-out Error. I am used to works with this kind of HMI, I think the problem is in the PLC because this is my first time working with a new, out of the box, PLC. I have tried to comunicate them using the "Com. Test" tool from the System Menus of the HMI; however, I didnt get it.  I think the problem is than the integrated ethernet port of the PLC is not in the Net Number 1. I have tried to set it using Cx-Integrator. I have clicked in "Create routing tables" -> "Insert SIO CPU unit" for the Unit250(Integrated Ethernet Port) -> Local network number = 1 -> Transfer to PLC. Nevertheles, the windows "Online Connection Info" is allways showing Net(-) instead of Net(1):    "Ethetnet [CJ2M-EIP21] Net(-), Node (10),  Unit (0)" I have checked the Cx-Integrator Manual and says in this case it is only neccessary to "Connect", but I have tried it, waited for the 254 nodes, and... it doesn't work!! I don't know what to do! Thank you.
  9. DB9 Connector SLC 5/03

    Hi Im hoping someone can help me out! i have a PLC SLC 5/03 and i want to connect the DB9 port with DH485 protocol to a computer 100 fts from there, is there any problem with the distance? and what kind of cable should i use , i already connected with my laptop with a USB-serial with a null modem cable RS232  (i did the cable by my self) but for the distance i cannot keep using that protocol so what is the recommendation?    
  10. Mitsubishi plc communication error

    I have Mitsubishi FX-1N P.l.c i found a problem about communication port.Run and Power L.E.D on as per routeen but i cant communication with GX.Works 2. PLz tel me how can i fixit this problm....
  11. CJ2M HSC input

    I have omron plc CJ2M CPU15 and I have input module CJ1W-MD261 (32 inputs, 32 outputs) and I was wondering can I MD261 module for hsc inputs? When I open CX programmer and go to settings and go to "IO Module" I see that I can include HSC input and I assigned it to Input 08 and what is that input? Is that input 0.08 on MD261 because my plc has no integrated inputs or outputs  (image included at the bottom). Any help is wellcome
  12. Nachi to Proface over ethernet/IP

    Hi I am trying to connect a Nachi MZ01 robot to a proface (LT400M) HMI/PLC, I cannot seem to get the communications fully working as I have a response error on the proface and a I/O error on the robot pendant, I also cannot find the assembly instance in the manual for the robot to set in the proface device setup, I am using 256 Bytes in inputs and outputs, I have attached the proface software below. J2204 - Welding Cell V2.prx
  13. IC220PNS001

    Hello, I currently have two IC220PNS001 connected to IC695PNC001. The PLC being used is IC695CPE330. Out of the two PNS001, one of them has a solid SF Red light on which means bus error according to the Status Parameter IO. I disconnect every single IC220 card connected and downloaded the whole configuration but I still have a Bus error.  PS: I have also tried to switch the PNS001 with the brand new out of the box and I still have the same error. In the manual, it says Profinet Diagnostic available, can somebody please guide me as to where I can find the Profinet Diagnostic, also is there any manual for PNS001 which explains the in-depth debugging process for this PROFINET Controller.  
  14. HI ,  Thanks a lot for the reply & help on previous topic. Now i setting up a new system with 2x CJ2M CPU13  and 2x SCU32 and the connection via 1000M RS485 cable. May i know the best communication to use for the serial communications?   Regards, TJ SHARON.
  15. Diagnostic of profinet communication

    Dear Experts, I want a sample block to find out the status of my Profinet cable w.r.t Hardware configuration. whether the cable is connected or disconnected from the node. Either my nodes may be VFD, HMI, SCALANCE, etc...  please share the sample blocks... S/W ===== >Tia portal v14 sp1 update 6  H/W ===== >CPU 1214C DC/DC/RLY hanks in advance
  16. CJ1W-ETN21 Detection

    To all the gurus. We have a project now that is using CJ2M PLC. However some hardware is using 1 piece of ETN21 card while some machines are using 2 cards. Programs sequence is quite similar. However Customer wants us to be able from program side able to detect if there is 1 card presence or 2 cards presence.   Not sure if there is certain bits or memory in PLC that program can tap to "detect" number of cards that is presence.
  17. CIF41 Connection Problem

    Hi Dears I have one CP1H with CIF41 in its option port1. Firstly I connected to CIF41 ( ON DIP Switch 4,5) and I could download to CPU with ethernet FINS and I connected my HMI to this network and every thins be OK. after one week I power ON the panel and now CIF41 not working. every setting is ok (DIP switches and other settings). now when I connected to CIF41 no LED is on and my laptop network dont recognize the CIF41. can you help me? what is the problem?  
  18. Hi, I can’t find an answer to the following and I was advised to ask it here.I’m programming an Omron CJ2M with an MD212 high speed I/O card. I usually do all my programming in Structured text, simply because I like it a lot over ladder or sft.Now, if I want to read the hight speed counter (incremental encoder), I have to make a ladder section and use the PRV instruction to store the present value in a chosen location.The manual says the current PV is stored in A271, but I can’t get a readout there. Apparently the only way to read it is through this instruction.Does anyone know if there is an equivalent to the PRV instruction for Structured text? or another way perhaps? Again, when I check the actual memory adress, there’s no value there withouth the use of the PRV instr.
  19. GE ENET station manager

    HiI am just starting out at a new job full of GE systems.I have a IC695ETM001 ethernet card which has a RS232 port for Station manager access.I can currently see some info (such as IP, firmware version etc.) from the card when I connect with Putty and cycle the power but I cannot send commands to the card. I've tried Putty, hyper-terminal and a standalone Station manager terminal from GE but nothing works.Anyone know whether I'm missing something?
  20. Q series Built-In Ethernet problem

    Hi ~ Thank you for helping me I use the Q03UDVCPU this time. I set a TPC MC Protocol 3000 port on the Built-in Ethernet to give PC to connection. The ethernet cable configuration is the PLC CPU link to Switch and link to PC. The problem is that when the PC is connected to the PLC, I use the Ethernet diagnostic of Work 2, you can see that the port 3000 is occupying by PC. There is no problem here, but when I remove the ethernet cable the PC, this 3000 port should be cleared, but the IP still occupying this 3000 port, until I remove the PLC CPU ethernet cable, it is the same result, and my PC can no longer be reconnect. Since the ethernet cable are all removed, the connection status should be updated, I don't understand why it is still occupying. Does anyone know the answer? Thank you so much!
  21. DeviceNet problem CJ2M-CPU31

    Hi, I am trying to set up a remote IO exercise using CJ2M-CPU31/CJ1W-DRM21-> GRT1-DRT with little success. Started with setting up Comms, making Routing table, downloading Routing table, Connecting to DeviceNet in lower left window in CX-Integrator, Devicenet appears in the project and  DRM in the right window. From then anything I try to do with the DRM responds with communication error. I got no NS leds, E2 in the DRM and flashing TS on the GRT. I have done the same thing with a CS1 and a CJ1M-CPU11-ETN with almost no problems. Only difference being that with CJ2M I had to start Integrator first, same results with Ethernet, Ethernet FINS/TCP and Direct online USB. The DRMs/DRTs are donated second hand units, so might have some inherited settings? Any suggestions? Geir Update: Actually had two problems, one of the IO-slices in the GRT was faulty and blocked communication. CX-Integrator only seem to work with CJ2M in Auto online USB or USB (Toolbus). Geir
  22. Omron NX102 / NX1P2 cannot trigger MOXA ioLogik E1212 Outputs through Ethernet/IP connection, But I can read the Inputs Status All the time.   Just CANNOT trigger the Outputs signal through Omron PLC. Moxa claim that they can use AB PLC trigger E1212 outputs and no problem at all, but now OMRON PLC cannot.   Steps I am doing... Define the custom Data Type Structure. Create a variables with custom data type. Mapping with MOXA eds file setting. Inputs - 67 bytes, Outputs - 1 bytes. I had Install the MOXA EDS file I do contact MOXA Support channel, they claim that Omron PLC  not response to port 2222 . Can anybody help ? because same Omron PLC using for test also tested with other EIP device with no problem at all. I have no idea which party are problem now... T.T  
  23. Fatek Ethernet PLC Module online

    Dear All,  Anybody can help me in communication between Fatek 20MAR2 & CBEH2A. The jumpers setting are JP1 is on left two pins (No password protected) & JP3 is on right two pins (forced boot operation mode). The Ethernet cable i used is type b T568. Fatek Ethernet module config software detecting module successfully (shown in attached pic) but on online PLC via ethernet cable its showing connection failed.   please help   thanks in advance
  24. Hi. I am new for omron , I want to use CJ2M CPU 34 + CJ1W-SCU32 connect to E5CC temperature controller with RS-485 , I'm no sure it will work or not.  Is it possible or not? The manual E5CC No details for SCU32 Sorry I'm not good english. Thank you.
  25. Hi to all, I have two queries about CJ2M-CPU13. 1) Can i use the in built serial port (RS232C) to the GUI or HMI? 2) Can i use the in built serial port (RS232C) to connect two CJ2M-CPU13s? I have only limited experience and knowledge in the PLC. I would like to see a step by step instruction video or tutorial notes.  If any of you any information pls share and help me.   Appreciate all help and thanks.