Search the Community

Showing results for tags 'cp1l rs232'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 68 results

  1. HMI CONNECT TO NON PLC WITH RS232

    HELLO, i want to ask. Can HMI connect to Non PLC device(example: zebra printer,Barcode Scanner or Weighing scale) using rs232 ? if can, can you suggest me what type of HMI that can connect to Non PLC device Using rs232 communication? thank you, have a nice day....
  2. I have OMRON CP1E PLC and I want to read memory address of PLC via serial communication. I want to use ESP8266 OR ARDIUNO OR PC Hyperterminal Please help me in any direction. How I should proceed?  
  3. Hi   I'm beginner from plc programing, I  need to sent data (D0000-D0010) to PC through Host link mode . i just sent data from PC to PLC with command serial port is work only like below PLC_Serial.println("@00SC0252*");//sent to monitoring mode PLC_Serial.println(CalcFCS("@00KSHR 004500"));//set H45.00 to hight PLC_Serial.println("@00SC0352*")//sent to run mode but  PLC to PC i don't know how to do . Could you advise me ? Thank you.
  4. About InverterRefresh

    Hı guys,  I will design new project  but I dont know that how can ı use  FB  at the   attachmend files ı wanna send   speed  referances  for 23 motors with rs 485  I will not use   start and stop  function  for ınverters with modbus   ıt  will be doing   probably  only speeds of the motors     1 )  Plc CP1EN40S DT1D     2)   hmı : nb7 twb0        3  ınverter s  :  V1000   VZABOP4BAA how can ı use registers numbers of the ınverters so ı need simple program    thanks for  everythings [767]InverterRefresh.zip
  5. Omron CJ1m - bluetooth connect

    Hi, I write app to smartphone to communication omron CJ1m and Android. I want to connect devices by standard bluetooth. I plug in bluetooth adapter directly to omron RS232.  I want to ask you, how i can connect by FINS command. Bluetooth device baud rate is set 9600. If i connect to omron, i sent code: "AC01" and i sent how long as omron return me "AC01" ?? And what's next command i sent? If I want read CIO 10 i sent: "0101B000000A" ? and FCS and "*" ?? how i calculate FSC? Is it XOR my data sent? 
  6. CP1L-EL TCP/IP with VideoJet Printer

    Hello, My previous topic was want to establish communication CP1E --> Videojeet Printer using RS232 serial cable. this project test SUCCESS. by the way distance from printer and PLC was very far almost 500meter. so printer technical team request to use tcp communication using cat5e cable. Problem: 1. I'm using TCP communication protocol that need me to have open,send,receive,close port. 2. Communication testing with PC Hyper Terminal --> OK but HT need in waiting call mode, i don't know why. 3. Using printer no result show. how i'm suppose to know communication already establish? 4. Communication setting on PLC Setting-Built in Enthernet need to add other communication device.? here i'm share some programs to give more understanding. Thanksm TCP with printer.cxp
  7. I using easymodbus library to connect and read data from 3 PLCs CP1L but it run unstablely, sometime it disconnect and i cant re-connect PLC, it give error time out when i try to reconnect when it happen, i restart PLC and everything back to work. Someone please help me. I am new with modbus and omron
  8. PC send data to PLC

    Hello, i'm newbie for plc. i want to ask about PC/computer send data to PLC CP1E with serial communication (RS232). my wiring cable is: PC                         PLC 2                             2 3                             3 5                             9 4&6    7&8                               4&5 and if i send data from PC to PLC, my indicator in COMM is blinking. i think the cable have no problem. but if i send data from PC to PLC, the memory is not same as what i send and whatever i send data, the memory didn't change. i will attach my ladder diagram. what should i do?    New folder.rar
  9. i am new in plc programming . i know the basics difference between the rs232, rs422, rs485. but i am little bit confused in it. so i have the following question regarding these terms. 1.  can these protocols communicate with each other i mean rs232 can communicate with rs422 or rs485 and same. 2. my plc has port rs422  but i can connect it with my laptop serial port which is rs232 ? 3. what are the main important points that kept in mind during communication or cross communications.   any help will be greatly appreciated.
  10. Greetings everyone. I'm new here. Hoping to get help to operate the Omron V400-R2 barcode to the Mitsubishi QJ71C24N so that they can communicate the two devices with the correct method. PLC: Mitsubishi: Q03UDVCPU; barcode: Omron V400-R2; serial communication module: QJ71C24N. I use RS 232 communication cable, I have tried using predefined protocol and non protocol procedures but still can't communicate the two devices. I really appreciate your help.
  11. Compare data RS232

    Halo, my name is Riandanu, I connect PLC Omron CP1E to weighing scale, and its done. i think i dont have problem between PLC and weighing scale. And i want to ask about, how to compare value from weighing scale ?  example : from the picture you can see value of weighing scale is " ST,+00160.66  g", and i want to compare it with 180 or 150 to give output on to lamp. Thankyou Riandanu       PLC to ek-i.cxp
  12. CP1E RS232 communication to my weighing

    hello, i want to connect CP1E to EK300i (weighing scale) with RS232 communication. i attach file of datasheet ek300i, wiring CP1E to ek300i and my cx programmer. if i push send data on ek300i, com LED indicator in CP1E is on. and i dont know why my cx programmer can't change data of memory with data from ek300i? what should i do?   ek300i.pdf CP1E to EK300i rs232 communication (belum dicoba).cxp CP1E to EK300i rs232 communication (belum dicoba).opt wiring rs232 ek300i to CP1E (belum dicoba).txt
  13. Hi, First as i know we can communication in MODBUS RTU as summary below 1.FX series, FX3U-485ADP-MB + ADPRW instruction  2.Q series, QJ71C24 <Serial interface module>+ Pre-defined protocol  3.Q series, QJ71MB91<Modbus interface module Three thing upper, i think it will ok   The question is  1> FX series, Cloud we use < Serial communication only not Modbus adapter> + RS instruction to do Modbus and How to do that.                              2>Can I write modbus rtu over RS-232 interface of the CPU module Q01UCPU and how
  14. I need to add 3 encoders to my project. Currently my PLC Inputs are full. I am using high speed counters 0.00 and 0.001 to monitor a motor RPM with an encoder. I now wish to add 3 encoders to monitor position of (3) other linear axis controlled by stand alone (Zeta 6104) stepper drives. I have 3 open outputs on this PLC but all inputs are used. What are my hardware options to add additional encoders to allow me to track and correct the 3 additional axis. My first thought was to add another CP1L and use PLC1 0.00, 001 for ENC1, PLC1 0.002, 0.003 for ENC2, PLC2 0.00, 001 for ENC3, PLC2 0.002, 0.003 for ENC4. I thought this would allow me to use additional I/O from the second PLC but I am not sure if this is even possible. Is it possible to connect 2 PLCs this way? I will need additional I/O to send to these stepper drives to make the corrections. Do I need to add an expansion unit to the existing PLC and 2 additional high speed counter modules? The encoders are all Omron E6C2-CWZ6C. I would appreciate any advise on options to add these encoders and help point me in the right direction. Thanks in advance to any help.
  15. CP1E-N30DT with Hyperterminal PC

    Dear Expert, i'm issue to do communication CP1E with PC via RS232. im try to use plc for sending information and receive by hyperterminal pc. after googling some information there have multiway to success. by the way until now cannot settle. please expert share completed setup that's work: 1. communication cable from PLC - PC (my information use pin (2,3,9 jumper 4&5) - (2,3,5 jumper 7&8) 2. sample program that works (im using TXD & RXD with memory D1000 to keep data) 3. connection cable to PC using MOXA Serial to USB converter. 4. plc serial setting (default: 9600,7,N,1,Host link) my target to give instruction to printer to start print. printer need ACSII code. if this communication success i'm will convert all data to ACSII by ACSII convert function.   thanks,
  16. I recently purchased the SIEMENS CONNECTION KIT (6ES6400-1PC00-0AA0) with its corresponding serial cable to connect to a MICROMASTER 440. I connect my RS232-USB cable to the serial cable. But I can not connect in any way! What do I do wrong? 1. In the micromaster 440 I put the following USS configuration parameters (USS = serial communication):    p2010 = 6    p2011 = 0    p2012 = 2    p2013 = 127 2. I put the DIP of the Connection Kit (Ref. 6ES6400-1PC00-0AA0)  1 ON, 2 OFF, as indicated in the manual.    I connect the connection kit module with its serial cable to my RS232-USB cable. And I connect the USB to my PC. 3. Open "Set PG / PC interface" and select PC COM-Port.USS.1 4. I go to the properties and I am selected COM1 without problems. 5. But I do the transmission speed test and can not find anything. 6. Also in the diagnosis of PC COM-Port.USS.1 I do the test and can not find anything. Supposedly my RS232 cable is correct (I have tried several tests). And the configuration of the COM port in "device manager" also looks correct. What am I doing wrong?? Zhanks!
  17. SCPI Communication

    Has anyone been able to set up back and forth communication with a device that uses SCPI? I have a D2-260 and 5 Kikusui power supplies. The PLC already utilizes a RS485 Modbus network and also has an Ethernet connection. The power supplies only have a RS232 connection and uses SCPI commands. I have searched the web over and there are Modbus to ASCII converters but how to make it where to catch the response in a register for the PLC to find? I am open to anything, 5 small PLCs to there is no possible means to do this. Any direction would greatly be appreciated!
  18. CP1L connected with scanner symbol DS-4308 reading 2D data matrix,  with RS-232 on board CP1W-CIF01 Hi all, need some help because I can't read the information. Let me explain, I have a PLC, " CP1L-L14DR-D " with a RS-232 option borad " CP1W-CIF01 " , a scanner Symbol DS-4308, and I'm trying to read a data matrix 2d barcode (I don't know if that matters). so I build a cable with the next configuration, (one side male and the other female) PORT CONFIG PIN OUT SCANNER CABLE RJ-50 TO RS-232 PINOUT Maybe I'm missing a connection? a bridge? power supply ? ground?   in the program, I only have this to check the communication,       When my reception flag complete (A392.06), my instruction RXD is going to execcute, reading in D1500 the data. if is any error in communication (A392.04) or overflow (A392.07), my port is going to restart (A526.00) (ignore w0.03) with the followign config: (9600, 7,2,E, RS-232C, End code: Received Bytes 3       and I'm reading only, data on D1500 and D1501, and the data makes no sense.   with the configuration of End Code: CR, LF,          can't make it work, I read nothing. and if I change the END CODE: Received bytes to 4,      don't work. and my flag A392.04 go to ON.   PLC HAS 4 PIN SWITCH, ALL ARE OFF The configuration on the scanner is setting to default and then config to RS-232 Standard.   So, what I'm missing?  bad connections? plc don't support? scanner config? program?      
  19. SUPERVISION OF A CHAIN

    I have 6 PLCs CPM2A and 4 PLCs CP1LM I'm going to network them to do the supervision and data acquisition from each PLC and connects them to a pc via an ethernet port So what are the hardware and software used?
  20.  Hello    I need to sent data between PLC CP1L-M30 and  Hyberterminal with serial port (RS232C port 1) ,but there isn't data show up . something is wrong? Could you advise me? my ladder as below  
  21. PLC TO HMI

    Hi I am a beginner within PLC, I have attended high school and will attend an oral and practical test in January. To become a "licensed" automatician. Total 4.5 years of school and practice. (NORWAY) I have programmed a little omron before, but not with HMI I'm having trouble getting plc to communicate with HMI. I get CX-Designer to communicate with both PLC and HMI.   Hardware: CP1L-EL20DT1-D     NS5-SQ11B-V2     W4S1-03B     Omron 3-port basic ethernet switch 3x Ethernet Cat.6 patch cable   Thanks for reply
  22. Hi, In the attachment there is my code.  Setup is set correctly, because when I send data from PC to PLC everything works (data is read and LED Comm blinks), The problem is with TXD. After startup A392.05 is ON when I execute rung no LED blink either no data comes to PC and  A392.05 become OFF until f.e A526.00 set to ON Any idea why data is not send from PLC?  HMM  
  23. My issue is trying to receive data from a Datalogic PM9500 barcode scanner onto a Siemens ET200S (IM151-8 PN/DP) CPU using a serial interface card (6ES7 131-4BD01-0AB0) with the ASCII Protocol. The software that I'm using to program the PLC is TIA Portal V14. I made use of the built-in function block S_RCV to try and receive the data into a data block that I have created. I connected the Datalogic's base charger unit directly into the PLC's SI module. (I cut the DB9 plug off) So, Pin 5 (RXD) of the SI module is connected to the Tx wire (Brown) of the scanner, the Tx is also connected, as well as the ground, to the SI module, however, I only require the Rx. There is no flow control. Upon scanning a barcode, the Rx LED on the SI card flashes, indicating that something was received. I have tested the scanner using a terminal program called "Hercules", and I am receiving what I should be when I scan something. The parameters such as Parity, Stop Bits, and Baud Rate, etc, of the scanner corresponds to that of the SI module as well. I paramatized the S_RCV block as follows: 1.) EN_R is always ON. 2.) R is defaulted to the instance DB that was created with the function block's tag.  3.) LADDR  is set to "100" as that is the start address of my SI Module as defined in the device configuration. 4.) DB_NO is set to "2" as it is the number of the data block I created for storing the received data.  5.) DBB_NO is set to "0", which I understand to be the data blocks offset start point from where to start inputting the data. The rest of the NDR, ERROR, LEN, and STATUS outputs of the function block are also defaulted to the instance DB tags. I only want to see if I'm receiving the data from the barcode scanner into the datablock. I created an array of bytes and I also tried with characters  from 0 to 30 to store the data. As I mentioned, the problem comes when I'm trying to scan something, the RX LED on the SI module pulses, but when I monitor for any changes in the Function Block, as well as for any changes in the Datablock itself, nothing happens at all.  I don't know what If I'm missing something, this has been bugging me for some time now, I'm quite new to the whole programming scene, I would appreciate any help I could, get also I've attached the project file too. =)   Yumi_Panel.zap14
  24. hello, Maybe somebody know how need send only hex numbers via rs232 in the external device? I tried to use SEND_RECV_MSG function block, but unsuccessful, because send ASCII code. Need send 16#AE number, but I don't have any idea how need do it. I am waiting your advice.
  25. So, hello all. I'm new in Omron PLC. Using: CP1L-EM controll + CP1W-TS102 (x3) Problem: I need to regulate the valve with motor drive. You can meet the same in heating system for control the temperature of water. Logic is simple,  - low temperature? - open valve step-by-step - high temperature? - close the value step-by-step I always use PWM regulation, but in Omron PWM only for encoder (srsly, i don't need 10k impulses during short period of time, i need just several impulses during the time) So, i decided to use TPO. The input calue for TPO is output value from PIDAT. (W451 manual, description of TPO function, example) What's the problem?  1. I need to make difference time between impulses.  Look here: I have 55 C temperature of the water, but i need 80 C, so i need impules for 8-10 sec duration, but when the temper close to 75-79 degress i need the impuls 1-2 sec duration. And, as i read, TPO cant do this, right? Just constant duration in 1 TPO instruction, or use several TPO instruction. Other situation, i have 80 degree Celsius, but i need 50 C, so i need to close the valve.  But i have only 1 TPO! So i need to check the difference beetwen SP (set point of temperature) and PV (process value) and if it hegative - go to PIDAT #1, which connected with TPO #1 and close the valve (SP-PV need to be around 0) If i have positive value (SP-PV) i need to go to PIDAT #2 wich connected with TPO #2.....  Srsly? I cant make the measure between -100 .... 100 for 1 TPO function and use 2 digital output?  I know that 0...10v regulation is better, but i have that i have =)   Sincerely, p001p