Search the Community

Showing results for tags 'compactlogix'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 40 results

  1. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  2. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  3. CompactLogix I/O Fault

    Hello, Back in December 2017, we replaced a customer's PLC-5 control system with a CompactLogix.  Everything was working fine until about a month ago, when they started having an I/O fault, Code 16 - I/O module connection failed on required module.  At first it was showing up on multiple modules, and also the end cap.  However, after a few more faults, it was only showing up on module 2.  We replaced that module and the faults stopped for about a week and then returned.  The module we replaced is a 1769-IA16. Any idea what may be causing this?  The customer insists nothing was done to the panel since the initial installation.  
  4. Hi guys, I am trying to connect AB compactlogix 1769-L30ER through Ethernet cable to my laptop. I use Rslinx version 3.9 When I enter IP address it can find the CPU without any problem but it does not show the I/O. When I check the driver diagnostic, it says: Can't set port type to 288: no harmony object for this Ethernet I should mention that my OS is windows 7 and I turned off firewall as well. So, what does it mean and how I can get rid of this message? Thanks
  5. We have an auto-clave unit purchased at auction roughly 4 years ago.   CompactLogix L32e and PanelView Plus 1000.  All has been working for us until last week.  Suddenly, the program seems to freeze up after around 30 seconds.  I can still touch the panelview and the touches are registered, (the mouse icon moves) but the program does not respond and I can tell the program is frozen because the clock which displays seconds stops counting. When i boot into safe mode (clicking white box on boot) the system does not seem to freeze at all.  I am able to navigate those menus w/o issue.  We don't have any of the software to connect to the PLC.  I understand this is a somewhat broad issue, but does anyone have any idease where i can start in troubleshooting this? or is their any further info i can provide which would be helpful?
  6. Anyone have any suggestions on the best way to pass a little bit of data between a SLC 5/03 controller and a compactlogix? The current problem I'm working through is the SLC 5/03 does not support Ethernet (only RS232 and DH485). So now I'm trying to find a solution.   Thanks,
  7. Read/Write Access DB

    I am fairly new on this forum & PLC's, usually i read and get tips from here.I use a RsLogix 5000 PLC software. I am currently working on a project at home that requires me to read from a Access DB. What type of Instruction or method do i go about, initially reading from Access? I know Excel is possible It's an existing system. Add on functionality/feature. I am using a barcode scanner that will link up to a Access DB to verify the barcode is legit and send this info to a different system via PLC/EthernetThe access DB is used because its a older system, it uses that. So it is possible? and guessing from what your stating, its is more involved to get the system working eventually?PLC = A&B 1769-L23-QB1 CompactLogix Controller I am using FactoryTalk View Studio as HMI, do not have SCADA.I have a control logix chassis. Thank you in advance...
  8. WeinTek to AB PLC Issues

    I am connecting a WeinTek eMT3105P to a CompactLogix L2 series PLC via the WeinTek Rockwell PLC (CompactLogix) - Free Tags driver and I cannot for the life of me get the thing to connect. I have all my tags imported and have played around with all the settings in the manuals I can find. Any help/advice would be greatly appreciated. I know my IP addresses are correct and if I connect my cable directly from the HMI to the PLC I still get the "PLC no response" message 
  9. Hello, I was hoping for some help in trying to read/write to a handful of bits in a CJ1M-CPU13 controller from a Compact GuardLogix. The CJ1M rack has a CJ1W-ETN21 card that is already communicating to a handful of Yaskawa drives. Is it possible for me to communicate with this controller from a CLX unit over ethernet? I don't believe an ETN21 card uses EIP but is there a way around this? Right now, I'm struggling to even find the IP address of the ETN21 card as the CX-Programmer file provided to me by the customer does not have the card in the IO configuration and I've never worked with Omron PLCs before. I found a CJ2M to CLX guide but it assumes communication over Ethernet IP and the ethernet port is native to the controller. Any help at all would be appreciated. Thanks!
  10. Hi everybody: I'm writing here because I have an Etherhet problem with my compactlogix 1769-L32E. I connect a crossover cable between my pC and the controller, then I run the BOOTDHCP server program . The BOOT DHCP window only shows the MAC of the PC, the controller´s MAC doesn't show even if i wait for more than 10 minutes I hope you can´t hel  
  11. Remote Access to CompactLogix PLC

    Can the PlC be accessed remotely. If I hook the CompactLogix L32E up to the internet WAN, would it be possible for an engineer to access and make changes to the program remotely?? Or does it have to be done onsite through the LAN.
  12. We've purchased an Autoclave at auction with CompactLogix L32e and PanelView Plus 1000.  With the help of some forum members and a local engineering company we have the machine finally working! I'm looking for some advise as to how to train users for standerd operation.  For example:  Their is a toggle switch on the front which powers on everything (PanelView, processer, switch, etc).  We close at 5pm each night.. Should we Power down the machine each night, or leave it on? Another user mentioned a battery and I was a bit confused with the manual. With the machine off, Is the PLC only holding the program because of the battery?? I have backups of the following.. (.acd, .apa, .mer) files.  I also have created a Disc Image of the Internal Flash card on the PanelView.  Is their anything else I should have a backup of? Their is a CF card in the PLC.  It has a folder called "Logix" and one called "System Volume Information"  In the Logix folder is  a CurrentApp folder with a .bin and .p5k file.  Does anyone know what exactly these are doing?? Any other advise is greatly appreciated.  Thanks so much for your time.
  13. Is there a way to monitor the Temperature of a Servo Motor on Allen Bradley Servo motors... MPL? PLC: CompactLogix 1769-L30ERM Drive: Kinetix 6500   Motors: MPL-B310P-MJ72AA, and  MPL-B560F-MJ72AA I would like to be able to monitor the temperature, and flash a warning screen on the HMI if the Motor gets too hot, or perhaps shut down the operation before the Motor overload trips. The drive and PLC are connected through Ethernet IP What I don’t know is if that Motor heatsink temperature information is available to the PLC.
  14. Good morning i want to know how i can recognize into the compactlogix 1769-L24 ER the micro 850 (2080-LC50-24QBB), because i want to communicate this two devices with MSG, i already i can see these two equipments into RSlinx but when i start Studio 5000 i don't know whick module i have to use it to recognize the micro 850, please help me
  15. Hi Everybody, I would like to get the Connections from an AB CompactLogix L32 with CIP. I can see these connections on the web interface. According to the CIP Vol1 v3.3 documentation I have created a reqest in java which requests the first instace of the  Connection Manager Object with Get_Connection_Data service. I captured the sent and the received packets with wireshark. I would like to ask the following: 1.) Is this the correct way to request the connections from the PLC with CIP? 2.) The response says that "Service not supported", is it possible that the PLC does not support this service or there is problem with the request? 3.) Is there any other way to get the connections (I/O and Message) from the PLC with a CIP reqest? Thanks for the answers in advance.
  16. Hello guys, Newbie on this site. I am looking for a run time free Allen Bradley .NET driver. Basically a library (.dll) that implements communication protocols to Allen Bradley PLC's ( CIP, Ethernet/IP, etc.). Can someone point me in the right direction please ?.
  17. GOT1000&CompactLogix Tags

    Hello Im new using HMI got1000, Im trying to connect using Ethernet this HMI to a compactlogix, i already imported the tags, but i can't use any of them, because the gtworks3 says "you have to map the tags for set a device", i dont know what means map the tags, some one can help me please?
  18. I have a compactLogix L24.  It is connected to a network switch.  I also have an ethernet servo driver (KM AKD) attached to the same switch. The CL L24 IP address is 192.168.150.1 The Servo Driver is 192.168.150.3 In RSLogix 5000, I added an ethernet module.  I put in the IP address for the servo driver.  When I go online, I just get a connection error (Code16#0204).   I can talk to the servo driver using my PC on the same network (192.168.150.13), but the CompactLogix won't talk to it.  Do I need to install an external ethernet module to make this work, or can I use the existing ethernet ports on the L24? I'm stumped.
  19. Hey guys, this is probably a stupid question so I apologize if it is, but I have a PanelView Plus 6 700 and a CompactLogix L36ERM on one of my machines at my plant.  We have several different molds that run in this machine, so we have 5-7 different PLC programs that can possibly run in this processor, depending on which mold is in.  I'm planning to go to a single program with recipes, but I haven't had the time to set that up yet.  So we use the PanelView for troubleshooting, and adjusting process paramters.  On the main screen in the PanelView I have the time/date and also the program name.  What I have been doing is just creating a string tag in RSLogix 5000 that is the program/processor name (we use the same name for the processor and program) and then on my PanelView I just create a string display that looks at the string tag name in the processor.  That way anytime a mold is changed over and the PLC program is downloaded, the PanelView displays the correct program/processor name.   Now this is all fine and dandy and works as long as if a new program is created, we remember to change the string tag to the name of the new program, we often run new sample parts and what we do is rename an existing program that has similar logic and save it as a new program name.  The problem comes up because if somebody copies an existing program and makes a new one, the string tag is still going to say the name of the old PLC program.  Now if we only had one or two or even 5 machines, it would be simple enough to just remember to change that string tag.  Our, or I should say MY problem is that we have approximately 40ish machines in our plant, and I can't always remember to change that string tag every time we create a new program.  I should say that I have been, but there are times that I may forget. My question is this, is there any way that in FactoryTalk View ME Studio to have a string display the name of the processor or the name of the PLC program automatically without having to manually enter the name into the string tag that I created in RSLogix 5000?  Like is there a system tag somewhere that has the name of the processor or the name of the program?   That was way more explaining then probably necessary.  It's early and I've had way too much coffee haha.   Thanks guys.
  20. 1769-ASCII Setup Help

    All, I have a 1769-L24ER-QBFC1B processor with a 1769-ASCII card that I am trying to get working on the bench. I have a standard serial cable hooked up from Channel 0 of the ASCII card to the COM1 port of my computer. All I'm trying to do at this point is a simple bare-bones hello world program with a terminal (termite or putty) so that I can verify my setup and understand how it works before I try to implement it on the plant floor. I have the card set up in alternating mode and am using the pre-canned program found starting on page 35 of the user manual(1769-um012) .This is my first time using the ASCII card I am familiar with the CompactLogix processors and the RSLogix Suite. Any insight you can give would be greatly appreciated. Thanks, Lucas
  21. Rs Logix 5000 simulator

    From what I can tell, there is no built-in PLC simulator within RS Logix 5000, and I have to download a separate package that requires another licence to be paid for?   Is that really the case??
  22. CompactLogix strings.

    How do I add a constant string to a CompactLogix PLC and RSLogix5000? How do I copy one string to another? I have found links to using the COP instruction, which is fair enough, but the source parameter needs a tag and not a literal. How do I get a value into the tag? Can I really only do it when online? I'm new to Allen Bradley, and finding string usage to be very confusing so far.  
  23. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  24. Excel Add-in for Allen-Bradley Data Logging

    Version 3.9.0.0

    324 downloads

    ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2016 spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Allen-Bradley ControlLogix, CompactLogix, MicroLogix, Micro800, PLC5, and SLC500 communications. No OPC, DDE, external drivers, or programming required.  
  25. View File Excel Add-in for Allen-Bradley Data Logging ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2016 spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Allen-Bradley ControlLogix, CompactLogix, MicroLogix, Micro800, PLC5, and SLC500 communications. No OPC, DDE, external drivers, or programming required.   Submitter Automated Solutions Submitted 03/01/16 Category Demo Software