Search the Community

Showing results for tags 'analog programming'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 94 results

  1. Direct Logic 05 Ethernet

    I have a control that I want to use a Direct logic 05 plc in.  It is a really simple program but it is going into a plant that has a main control panel that runs the plant.  I dont know the brand of the plc in the main control.  They want to be able to send me a command from their plc to the direct logic to turn on my unit.  I suppose that would mean a simple set instruction to my plc.  I also have a couple alarm conditions that I want to send them.  For example if water pressure is to low I would put my unit in the alarm mode and send them a low water signal.  If the chemical is low likewise,   I dont have a clue how to do this in my program.  Can anyone give me some examples in direct logic plc program for making this happen??? Thank you Thank you Thank you. MikeC
  2. Hi. We are struggling a bit with the analog IO on the EIC202 coupler. Have tried tag sets, and gotten the digital IO to work without problems, but not the analog. Any tips here? We are using 2x NX102 with 1x ID4442, 1x OD4256,  and 2x EIC202 with 1x ID4442, 1x OD4256, 1x AD2603, 1x DA2603 on each, for a redundancy-system. Software is Sysmac Studio. EIP connection.  
  3. Codesys

    Hello - I stumbled across some mention of Codesys and was curious if anyone here uses it. Pros/cons? prefer it over other programming software. Have it downloading currently (since you can download a free variation of the application) but it looks quite interesting. Also - what PLC hardware is programmed with it? Did not see that mentioned on their website when I was browsing through.
  4. 1746-INT4 Used for Position

    Hello, My apologies in advance if this is in the wrong place. I am working on a press that is using a 1746-INT4 to look at the position of the ram.  The press is using an LDT as the sensor reading back to the INT4. It obviously works. The press runs everyday.  I'm wondering if there would be a reason to use this instead of just a voltage or current analog card?   Thank you in advance for the replies.
  5. VFD Analog output to LOGO!

    Hullo neighbors,  We've got a LOGO! 0BA8 configured to use I8 as an analog input, and the goal is to read the current operating speed of an ABB ACS310 VFD. (we want our PLC to be able to react to any changes in speed from the VFD) Problem is, nobody can figure out how to hook up the analog output from the VFD to the analog input on the PLC. Have tried going from AO -> I8 and have also tried adding a connection from the LOGO! input neutral back to the GND... nothing works.  Attached is the terminal diagram for both devices with our poor attempts labeled. Any insights?  
  6. Small and newly started Controls Company available to provide service in the following areas: Controls Design Panel Building PLC and HMI programming Commissioning Services 15+ years in controls and automation ranging from automotive to material handling.   Experienced with Rockwell and OMRON Can ship panels to anywhere in the world from Canada Will design and or build your panels to your specs and according to CEC and NEC regulations. Can commission your machines on site. www.ashtoncontrols.ca    
  7. Hello! I am new at PLC programming. I am using TM221CE16R PLC with TM3AI8 analog input module and SoMachine Basic v1.6. I am trying to scale analog input value. I am using 4-20 mA pressure sensor. I managed my wiring so that I get raw values in SoMachine Basic. But I don't know how to scale these values to usable values. My sensor works in range 0 - 16 bar. What is best way to get values? Is it PID function block or multioperand function block using equations to get range 0 - 16? I will appreciate your help.   Thanks in advance!
  8. I am new to Automation Direct software and how the programs are written. Can anyone explain how they handle the analog outputs? My processor does not support the IBox that makes life easier, so I am having to do it the old hard way. I understand most of the logic of how its done for sending data to one channel but I don't understand how the channel selecting works. Can someone give me a programming example or explain how that works? I am looking at the online manual that Automation Direct provides for you for the analog module but I am having a difficult time trying to wrap my brain around how they do their analog stuff ><
  9. MELSEC FX2N 48m plc PID programming

    I am new for gx devloper,I want 4 to 20 ma value to scale with 0 to 5000 and out put with PID. Plz help me.
  10. Hello - I've recently started my adventure into PLC programming and I've found this site to be very helpful. I took on a project that requires control of a cylinder - the short and skinny is that the cylinder will have to provide position feedback and stroke to various set lengths determined by position of a selector switch. So - If position 1 is selected, the cylinder will stroke 20"inches. If Position 2 is selected, cylinder will stroke to 25"inches - so on and so on.   My questions is how to best go about this process. I may be having a brain-block and not viewing this clearly, but something is not clicking for me and wanted some advice. Planned on using Allen-Bradley's Micro850 PLC (had one on the shelf, and CCW software is free so why not). Thanks
  11. Hello I have a scenario that's been bugging me for some time now. The scenario consists of a Micrologix 1400 that I need to control it's output from modbus/tcp. In detail what I really need is to be able to manipulate the O0:0 through modbus/tcp. The PLC would be the master and I would be the slave that triggers the connection to the master. I'm using a Modbus-Client on my PC and that should be the slave. Any idea as to how I can manage that? Currently I can send data to the master but everything is "stored" on B10 and I have no idea how I could write directly on O0. Thanks a bunch guys. PS: I'm borderline noob. 
  12. Mad42 analog setup

    I am trying to setup a MAD42 analog card up in a cpu33 omron controller.   I need input 1&2 setup for 0 to 10 volt and can't get it to work. Any help is appreciated. 
  13. B&R SWPIC-3 PROSYS programming

    I'm looking for the SWPIC-3 PROSYS programming software from the C PLC English version programming system. I am also looking for BRKAOL5-1 Centronics / online converter Online operation through the PC parallel interface. Any help would be appreciated.
  14. I am new to PlC programming . Plz can anyone guide me for ladder programming for FX5U -4LC Temperature controller with autotune parameters . Plus i want to use a PT-100 for the same . Plz help me out.
  15. Hello all. I have been working with an SLC 5/04 system, which houses various Digital and Analog INs and OUTs, up to Slot 29. I am currently mainly working with Slot 25, an Analog Input: 1746-NI16I. This is a system which has already been set up and has been running for the best part of 8-10 years. This particular card has had some spare inputs, one of which I am trying to connect to. In the Advanced Configuration, only a few Channels are actually "Enabled", and each channel is pretty much slightly different from another in terms of Input Type, Filter Frequency and Data Format. I am trying to set up Input 14, which is Channel 15, to "Enable" it, 4-20mA Input Type, Filter Frequency of 6 Hz and Data Format of either Raw/Proportional or Engineering Units. Now, after I have made my choices, I click apply, and then OK. I am then confronted by a pop-up which states: "Configuration Rung and Data Integer Data File Number: 25 Integer Data Element: 100 Rung to be inserted: XIC S2:1/15 COP #N25:100 #O0:25.0 24 At Program File Number: 4 82" I have the options of OK or Cancel. If I click OK, I now have LAD 4, Rung 82 Highlighted. This First Scan Bit and COP function were already here, but does that mean I have now altered what is being written to "#O:25.0"? I now Download the Changes. However, after all this, I am not getting any Analog input reading coming in from the Live PLC. What is this COP function? What does it do? How do I properly set up this Analog Card?   Thanks for your time, -Jame
  16. Hello. Can anyone tell me if there is a function for this in gxworks2? I want to even a jumpy analog signal. I am aware there is a MEAN-function, but that needs me to feed an array of buffered analog values to it. Which I am not familiar with how to do. Cheers
  17. Hi, I have some trouble with a CJ2M-CPU33. My client did a backup to memory card earlier today, and after this we did some changes through remote link. Now the client wanted to restore the previous backup to the PLC and has done so, but the system would not function correctly. After going online on the PLC it seems like the PLC is stuck in "Stop/Programming Mode". When trying to change to "Monitor" or "Run" mode a dialog comes up containing the following message: "Failed to change the operating mode. The operating mode may be still changing in the PLC."  - All the dip switches are set to off after restoring backup - The PLC has been rebooted  - I have downloaded the application again through CX-programmer  - Verified that the PLC is set to start up in "Monitor mode" But nothing helps. The same message comes up when trying to change the operating mode.  Hoping anyone can help to resolve this issue as it is very critical for us and the client. In advance, thanks for any tips or help received. Best regards Stian
  18. GS2107 BASE SCREEN

    I am new with GS2107 WTBD, please anyone tell how to set the following initial things: Base screen overlap window1 overlap window2  superimpose window1 superimpose window2 Dialog Window Just want to make any new program for HMI, but not able to proceed without above settings.  
  19. Delta PLC Analog Noise Reduction

    Hello All, I am Using Delta SE Series PLC and 06AD Module for Pressure Transmitter. But Analog input get fluctuate continuously. Is anybody have program for analog scaling.
  20. ANALOGIC BIPOLAR OUTPUT - HELP

    Hello everyone,   I'm a student who recently started programming, and I could really use some help.  I have a CPU-31 CJ2M OMRON PLC and a ADO41-v1 analogic card. I need help programming an analogic scale with a bipolar signal -10V to +10V to then control a drive, which will then control the motor. If anyone could help me out of give me some examples I'd be really thankfull.   Thanks!
  21. 1746-NO8V configuration

    Looking for a little help.  Replaced a 1746-NO8V analog card that hadn't been working for years and the new card is giving a Configuration Error (Module LED flashes twice, all 8 outputs are flashing 12 times).  I have 2 other of the same cards in the same rack that have been working for a very long time and still working that seem to be configured the same way.  Is there any way to know what is wrong with my configuration.  or maybe my new card is just bad???  I have not yet swapped one of my working cards with the new card, have considered but really think I'm missing something.
  22. PLC Training

    Hi Everyone We are setting up a initial training in PLC programming for technicians, I got some experience with SIEMENS S7 but this seems to be an expensive choice, we would like to opt for a budget PLC but at the same time would like a user friendly software for teaching......I would like to have views of users of other PLC brands such as OMRON, MITSUBISHI or even Schneider??? thanks Jay
  23. SMC pressure sensor

    Hi! Allen bradley PLC RS Logix 5000 I have a problem with a SMC pressure sensor (ISE30A if I remember correctly). When I monitoring the raw data from the ananlog module, I get about -7710 value, when the smc display shows about 0. There are another SMC pressure sensors too, and if the sensors displays shows 0 then the values what I get form the analog module is about 0 too, so the others work properly. But this one don't.  I already check the wiring. I have no clue waths the problem. Any idea from anybody? Thank you for your help.
  24. Micrologix 1400 Float TAG

    Hello,  I have a micrologix 1400 plc connected to a length measurement gauge. The gauge sends an analog value to the plc to an analog input. I convert the value into a dimension and send it to F8:0. but I need this value in three different steps in the program. Since i just have one element of float (F8:0) is there anyway i can store the value in a different location or create more floating point tags eg. F8:1. F8:2 ?    Thank You   
  25. Analog Wiring

    I need to connect a analog amplifier with the analog input 0-10V on my Siemens 1200 PLC (located inside the same cabinet as plc, about 40 cm between). do i need a shelded cable? or just RK0,75mm2? do i use any special color on 0-10V?