Search the Community

Showing results for tags 'address register range'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 54 results

  1. We have an iQ-r R08cpu that will not display some labels or addresses.  The PLC and the machine it controls run as expected.  However, when we read from the PLC, some of the labels and addresses are not shown.  Although it runs as expected, we are hesitant to make any changes or write to the PLC. There is a screenshot attached.  Any advice or solutions for this?
  2. Hi folks, I'm trying to communicate with an old CompactLogix L35E via Ethernet. I have already establish communication via DF1 Serial port and was able to go online but I Do not know the IP address to communicate via Ethernet. Can someone please tell me how I could determine the IP Address or create a new one ? This Controller was remove from a working machine. Any help will be highly appreciated. Thanks, Anthony.  
  3. hallo all, I want to ask if I click "read PLC Data" the "points" will appear, I use the QY18A output module that uses 8 points but there is no choice, the smallest is only 16 points.  so I can't put 148 in the "start XY" column ... will it affect the I / O address in the program?
  4. Hi, totally new to PLC's .. Just trying to do a university assignment I've connected a DTC1000 to Fatek PLC Port 2 - RS485 I want to know in which register I can find the measured temperature. A friend said you should add 400000 to the converted from hex to dec number which is mentioned in DTC manual. http://www.deltronic.su/userdata/files/dtc_manual_eng.pdf But I'm not sure which value should be used in manual and is 400000 the number to add (and where it has come from!) If I can just find the register, I can do the rest (just a bunch of normally open and close and  .. Thanks
  5. Lets say i have a PLC, with a name PLC1 with IP/Subnet of 10.125.34.243/255.255.255.0 I have to communicate this PLC1 with 2 other PLC's, PLC2 and PLC3 PLC2 with IP/Subnet of 10.125.34.10/255.255.0.0 PLC3 with IP/Subnet of 10.125.46.10/255.255.0.0 I imagine that, all these three are in different subnets, and so there should be no communication at all, but when i tested it, PLC1 to talking to/from PLC2 and not PLC3.  anyone know the answer to this ? How does it talk to PLC2 with different subnet, but not PLC3 which is in different subnet as well. 
  6. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  7. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  8. CX-Supervisor 3.4.1

    Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
  9. Double address - Alarm

    Hello, I would like to see your logical opinion about this situation and in which part of system where I need to find solution - software or in the physical field. Subject: Twelve old system based on Mitsubishi PLC AnS series, Profibus Here is pneumatic transport, with 5 lines, each line have a shredder and discharge valve. A few months ago, when line 1 works , display shows line 2 and vice versa, it was first problem, but the system was still working. From the last week system doesn't work. On the display appear line 3 in works, but system can not started. Alarm shows Double address (perhaps two valves have some address), Alarm still appear after reset and even all lines are turned off. What is your opinion where to find proble (PLC, I/O moduls, cables,...)  
  10. Compare not working

    We have this logic (on a CP1E) the desired outcome is as follows: When a bad part is detected, force the operator to index the machine 6 times, using a holding register to prevent a power cycle from resetting the count. once 6 cycles are recorded output that the bad parts are removed AND reset the count to zero.   What has actually happened so far: the count has gone to 6 and not reset. I have used CX Programmer to set the H0 value to zero but the compare still says it's equal (to 6)   I have read everything i can get my hands on regarding holding registers and compare functions and i can't see what is wrong. I have no formal training on this so i'm sure it's something simple. can anyone point me in the right direction?   Thanks guys    
  11. Hello everyone. I m new on site. I need to an example program (done and running properly) that bit shift register. I will design a bottle filling machine. I dont know how to use these logics.  hardware dosent matter.   thanks for your interest
  12. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  13. Dear all, I'm first time using M580 (hotstandby). Now finish the configuration, but the problem is how to write the address for Digital Input, Digital Output, Analog Input, and RTD module in elementary variable ? I try to put name DDI_1 and the address is same with M340 topology like %I2.1.0.1.1  and for digital input but got message after build : {Elementary Variables}    :     The instance is located on an address that isn't configured. :     DDI_1 Thank you for your advice regards  
  14. Dear all Please identify me i am having one Issue in my PLC.When I changed the IP of my plc then suddenly its showing error ERH its mean IP address wrong but  My CPU setting is same like previous means unit no=0, x16^0=0 ,Node=x16^0=1  and IP is 192.168.0.15 Mask add.255.255.255.0. but when I, transfer to PLC (in Program Mode) its not transferred(Failed to Transfer) please rectify me where I am doing wrong.
  15. I READ IN THE MANUAL FOR THE CJ2M-CPU34 THAT IT IS POSSIBLE TO CHANGE THE IP ADDRESS BY WRITING TO D30098 AND D30099 (MY DEVICE IS UNIT 0).  I TRIED TO DO THIS ON A TEST PLC BUT AM NOT HAVING ANY LUCK... I WROTE MY IP ADDRESS #C0A8 TO D30098 AND #0E30 TO D30099 (IP ADDRESS 192.168.14.48) WITH THE CPU IN PROGRAM MODE, I SET THE RESET BIT (A501.00) TO TURN ON ON THE TRAILING EDGE OF THE FIRST SCAN BIT, I CAN TELL THE CARD RESETS BECAUSE I AM CONNECTED VIA ETHERNET AND I GET DISCONNECTED, BUT THE IP ADDRESS DOES NOT CHANGE.  IS THERE ANY WAY TO CHANGE THE IP ADDRESS WITHOUT CX-PROGRAMMER?  I NEED TO GET A SOLUTION TO MY CUSTOMER TONIGHT AND MY SUPERVISORS DO NOT WANT TO RELEASE OUR DEVELOPMENT CODE TO THE END USER.   THANK YOU!!!
  16. I have Omron CP1H PLC and using Ethernet Option board to communicate through Ethernet. When I connect PLC to 2 Computer it starts malfunctioning and values in register get fluctuate. while I connect single HMI it works fine. Kindly give solution if anyone know. 
  17. Hi everybody. I'm just getting started with GX Works 3 and I feel a bit lost. If I have an external help file for my function blocks, how do I register this in the program? I can't find it anywhere when I double-click the fb library or in the e-manual Viewer. The file format is .CHM and I have imported this to GXW2 earlier.   /Niklas
  18. Hai i want to know how to save and retain the values of the program even in Emergency power off the PLC and on again? can any one help me?
  19. hi.  i want to make some program that work with indirect adress. example, i make program with many much type. I make with Got-1000 mitsubishi.   can you bring me some example? i am sorry, my english is Bad
  20. HI Everyone,  Recently i have bought a plc fx3ge and gt2000 hmi .the problem is that whenever i use a device address d280.b1 in hmi .i am not able to use the same address in gx works for plc (LD D280.1).can anyone help me with this problem.   
  21. Hello All! I am having difficulties mapping register values. In the TURCK register there are 24 unique register bytes corresponding to different value registers (8bit x 24). These 24(8bit) bytes were mapped into RSLOGIX 5000 as 12(16bit) INT words ....INT[12] .. This means there are 2 bytes (2 unique register values) inside each INT word. WHAT I NEED TO ACHIEVE: 1. (BLUE outline in drawing) Write/Map a value of "32" into byte 7 of the TURCK register so effectively starting at  INT[5].8 in RSLOGIX           Drawing1-Model.pdf This will enable the value of CNT1 (encoder count) to be registered in bytes 8-11... 2.  (PINK outline in drawing) READ/MAP the values registered in bytes8,9,10 and 11(4x8bits) into a SINGLE 32bit INT value which will tell me the CNT1 value of my encoder. I am having problems when ever I try to COP a value of 32 (no matter what kind of array it's sourced from) into INT[5].8 & I haven't tried to map/read the values of bytes 8-11 CAN SOMEONE PLEASE HELP EXPLAIN HOW TO ACHIEVE THIS?! Thanks for your input EVERYONE! :D Drawing1-Model.pdf
  22. E1151 New Display Register

    Hi all, I wonder if anyone can help me. I have 4 test rigs setup with E1151 HMIs and FX3U PLCs (with two ADCs and one DAC).  They are running pretty well, and the HMI changes block fine when using Jump to Block, but when I try to get the PLC to change the HMI's block using the New Display Reg it becomes very temperamental. For automatic testing I want the PLC to prompt the HMI to change block, so I set it up with a PLC register, then set the HMI to use this register for the New display reg.  When I turn the PLC and HMI on I can run through the test, and at the end it changes screen perfectly.  However if I run the test again the HMI appears to "forget" to change screen.  I have checked the new display register and It lists the correct screen, but the HMI doesn't change. So far I have tried adding "SCRR" too the command list to use short recipe names (saw this on a previous post), and tried reducing the amount to data transfer between the HMI and PLC to see if it was a latency issue, but neither have worked. Has anyone else witnessed problems like this?
  23. CPU 948R

    We have Redundant S5- CPU948R we have the requirement of knowing input address for FUM signals(Open & close signals).. Also how can we identify which cpu is acting as main CPU and which one is Standby. We look forward to a solution. Kindly advice us.
  24. IR register operation

    Hello, Can I add an offset value to IR register? for example, MOVR D0, IR0 and I have an offset value stored in D1, for example, &100, could I add the offset of D1 into IR0, to get IR0 pointing to D100? I know I can just do MOVR D100, IR0, but for purpose of versatility, I want an offset to be added in such a way. Thanks in advance. Xing
  25. Hello, we have 6 encoders and 2 of them lose their mac address every time power goes out. The other encoders find their Mac address by themselves. Can anyone help me with this issue? Thanks for reading. Have a great day.