Search the Community

Showing results for tags 'Modbus TCP'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 140 results

  1. Has anyone connected a Swegon ventilation unit to QJ71MB91. At Swegon, Read Holding Registers is 03 and in GX 0500. 03 is not in GX. I can't make it work. modbuscomp.pdf
  2. Hi,  I have a problem with modbus communication. I set everything as shown in the pictures and I get a error 04. What is wrong ? program.bmp ustawienia.bmp
  3. RJ71C24

    Hi, I want to set communication between ABB CI853 Modbus Master module and Mitsubishi RJ71C24 module. I tried with predefined protocol (you need to set slave address, but ABB is master), also with non-procedural (with G_Output function block), but without success. I tried connect ABB with QJ71MB91, and it worked because you can then set slave address and a station number, and this can't be set with RJ71C24??? If someone had a similar problem, I'll be grateful for sharing a solution. Best regards
  4. Greetings, I'd like to know how I could configure 2 HMI Kinco with reference MT4434T. I have a PLC with modbus485, a PC with USB-RS485 conversor and 2 HMI Kinco. The PLC have 1 on modbus direction, PLC have 1 and I guess that HMIs  would be 3 and 4. When I work with PC +  PLC  + 1 HMI Kinco, everything its ok. When I tried to connect other Kinco HMI, the connection between all devices stuck. I'm tried many combinations on modbus configuration, station number but I cannot make the modbus net works. Thanks.
  5. Hello people, i need some help. I'm Trying to create a simple program that stores some input's such as Temperature,  Production and Velocity (amongst others) in a machine , so that later i can send them to labVIEW via MODBUS RTU, the problem is i can't send anyregister i want, there was an old program we saved from the PLC that does store them, but uses the registers 199, 519 and 999 (the program reads 50 registers and 20 registers respectively from each register. I then tried modyfing the old program due to my problem to communicate the new one, and out even modyfing the registers won't work,  i'm i missing something?, does the HE-XE102 Horner PLC have a specified number of registers that can be read or sent via MODBUS. Appreciate any answer you guys could give me, Thanks for your attention.
  6. Hello All, Please Help Me.. How I can to connect Omron CP1L-M + CP1W-Cif11 with Mitsubishi Inverter D700? Thank you. Omron modbus belum fix.cxp
  7. Connect PLC to Kepserver

    I have Delta 12SA2 PLC it has RS232 port and I have connected it to kepserver (by Modbus serial) and then factory IO Now my problem is that when I connect my PLC to kepserver the RS232 port becomes busy with the kepserver and not available in the ISPSoft and therefore I could not demonstrate factory io and my logic in run mode in the isp soft together like you do in your videos. My PLC don't have ethernet port but is there an option in kepserver or any way by which i can use the same serial port of the PLC in isp soft run mode and kepserver+factory io together so that I can simultaneously show the logic running in isp soft and application working in factory io to my students. I googled a lot and found some softwares which make virtual serial ports for a given serial port but they don't work and soon hang Please help me I am in a great need of it. Thanks in advance.
  8. MODBUS-RTU slave

    At this moment I was asked to change one CJ2M's program (in Ladder, and the PLC is the slave) in order to make a list of desired variables "readable" by the master (an host computer/ SCADA) wich is using the protocol MODBUS-RTU. I only have to work on the PLC' side and i only know the name of the variables and their corresponding address.I already read the "CS/CJ Serial Communication Unit Operation Manual" but i still have some doubts:- The only way to define my slave address is done by writing a code to put the value of the address on the corresponding bits of DM area? or can i define the address using some feature of CX-Programmer?- (A CJ1W-SCU41-V1 is already implemented in the field) on the slave'side i only have to make sure the variables are allocated on the right place, according to the master's commands and modbus' addresses, right?- I read something related to the frames sended by the slave as responses for each master's command, am I supposed to write some code to do this task or it is done automatically?- Imagine the master is using the "Read coils" command, in OMRON there are 4 memory area associated to this data model "Coil" by default it is associated to CIO area, can i switch in the slave to Holding area without problem?Sorry about my english and this extensive text. Thanks.
  9. Modbus TCP/IP iQ-R series

    Hi, I have R04CPU (iQ-R series) on one side and on the other side is QJ71MT91 (modbus tcp/ip module). Is it possible to make communication between them (QJ71MT91 is master and R04CPU is slave)? iQ-R series doesn't have Modbus TCP/IP module, but is it possible to set modbus tcp/ip on built-in ethernet port of R04CPU, and how? Best regards Luka
  10. FX3GA-60MT Modbus RS485 as Slave

    Can Mitsubishi FX3GA-60MT PLC be used as Modbus RS485 Slave? Any sample code or documentation would be very helpful. I am planning to communicate to Weintek HMI (Modbus RS485 master) to FX3GA-60MT PLC (Modbus RS485 Slave). Any other ideas would be nice. Thanks
  11. I am using PLC Modicon M221, I want to make communication between PLC Modicon M221 to OPC Kepware by modbus tcp/ip ethernet. In PLC, I use software somachine basic, I set digital input and digital output. And in OPC Kepware my address  00001, but when I switch turn On/Off in PLC, value in OPC Kepware doesnt change. Could you please correct me? Thank you   Bujang
  12. Hello! I am using S7-1200 PLC 1212C AC/DC with configured Modbus TCP Server. I can already read/write Inputs/Outputs (Coils) and Memory Words. However I'd like to read/write Memory BITS. Is it possible? If so, how? What addresses should I use in TIA portal? And which function codes on client side? Thanks in advance!
  13. Is it possible to use FX3U-485ADP-MB as a serial port to send and receive user defined string/data to and from a computer? I have a FX3U-32M PLC and two FX3U-485ADP-MB adapters. I have been using PLC with one adapter as Modbus Master. Now i want to use both adapters, where one will be Modbus Master as usual and the other I want to use to send and receive data to and from computer terminal (Example - Realterm). I have a third party 232/485 converter which works really well. Lets me just describe my requirement straight forward. I want to display process parameters on a windows computer based user interface (UI) and also set some variables in PLC from the same UI. The UI has access to serial ports of computer.
  14. Hallo, i want to connect PLC Omron CP1E to indicator weighing scale with modbusRTU connection and i have a CP1W-CIF11 module to connect indicator with CP1E. ,but I have no experience in RTU modbus communication in the PLC. How do i start?   *i just need output: 1. Coil (Reference No = 0. Output bits) for input switch with address 3 (Tare). 2.Input Status (Reference No = 1) for output lamp with address 17 (stable) 3.Input register (Reference No = 3) to read data with address 5 (gross weight) 4. holding register (Reference No = 4) to write comparison data with address 17(over) page 85 - 94 in attachment     ad4402_manual.pdf
  15. hello everyone,, I use the QD03UDV PLC and the modbus QJ71MT91 module, I want to test the module using modbus poll but it fails continuously, and when I upload the program to the LED notification PLC "COM.ERR." the module is ON ... but in GX Works2 I have no errors .. why is it like that, can someone help me?          
  16. CJ2M-CPU35 and LS drives

    Hello, I want to do communication between CJ2M-CPU35 and LS drives. I am new to Omron.I searched the manuals regarding protocol macro.but it's bit confusing for me.please send if anybody have the sample program and document so that I can do it.Please support. Also I need to communicate Citect SCADA with CJ2M-CPU35 on Ethernet, please send me the documents if you have. Thanks
  17. PLC as Modbus Slave

    Is there any function for Mitsubishi PLC to perform as a Modbus Slave?
  18. hello.   I've been trying to communicate this omron plc CP1L-EM30DT1-D, with a yaskawa inverter cimr-vu4a0004faa. but i can't figure out how to make de correct mov or configuration in de DM. i need to run/stop, change frequency.    some help, please. :) 485PRUEBA.cxp 485PRUEBA.opt
  19. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  20. 1769-SM2

    Hello. I have a communication problem between an L30ER and SM2 module. It gives me a message error 16#001e, extended err code: 16#0000_0002, Error Text :Embedded service resulted in error. I have a Lovato network analyzer connected to SM2 module via Modbus RTU, on channel 1. The setting in the MSG instruction are: Configuration:Service type - Custom, Message type - CIP generic, service code 4b, Class 33f, instance 0, attribute 0, Source CH1_REQ[0] - INT[10], CH1_RESP[0] - INT[10]; Communication: slot 4, port 2, channel 1,  Connected - not checked. baud rate is 9600, DSI/RTU is 5, format 8-N-1. the channel led from the SM2 module is flashing. I read the value at a 2s. The rung is: XIO.TON.EN+TON.2s.EN+MSG.EN. The Cable betweenSM2 and Net.Anal is a CAT5, pins 4(A) and 5(B) Maybe someone has a clue.
  21. Modbus Addressing in Weintek HMI

    Modbus addressing in Weintek HMI to poll data from Temperature sensor through RS485. In my system i have connected Temperature sensor to I/O Scanner has output in terms of RS-485 which directly connected to COM3 Port pin. No. 6 (as Negative) & 9 (as Positive) of HMI (Model No: MT8071iE) and HMI connected to PC via ETHERNET. I want to read temp on HMI screen via MODBUS protocol. So, can you please provide me instruction about addressing of MODBUS register in Easy-Builder Software so can read data of corresponding register. Because when i do compile i got an error like " Device no Response". I hope i will get reply from your side as Fast as possible to overcome this problem. Thank you.
  22. Hello I have a scenario that's been bugging me for some time now. The scenario consists of a Micrologix 1400 that I need to control it's output from modbus/tcp. In detail what I really need is to be able to manipulate the O0:0 through modbus/tcp. The PLC would be the master and I would be the slave that triggers the connection to the master. I'm using a Modbus-Client on my PC and that should be the slave. Any idea as to how I can manage that? Currently I can send data to the master but everything is "stored" on B10 and I have no idea how I could write directly on O0. Thanks a bunch guys. PS: I'm borderline noob. 
  23. hy everyone.. I want to communication inverter SJ700 to hmi mitsubishi GS2017 for read an code error in interface HMI? is it possible to communication between them?
  24. WRITE MULTIPLE REGISTER MODBUS

    Hallo my name is Danu, i have a CP1E wirh CP1W-CIF11 and connect to modbus RTU device, i have done with write single coil, write single register,  read single register and read multiple register. But i try to write multiple register,  the indicator of CP1W-CIF11 is off and if i check d memory its no data. I attached my cx programmer. Can you help me create write multiple register in cx programmer?  Thank you AD4402-modbus edit edit edit edit edit.cxp
  25. Hello everyone! Briefly introduction, I would like to communicate and test the following hardwares: 1- Omron CP1E (using an Option Port CP1W-CIF11) ; and 2- Arduino Nano using MAX485 RS485 transceiver. The CP1E will operate in "Modbus-RTU simple master" as illustrated in image 01. The arduino will be in slave mode address 1 and the library used is "SimpleModbus NG" ( https://github.com/angeloc/simplemodbusng/tree/master/SimpleModbusSlave ). Taking the sample in official manual ( https://industrial.omron.eu/en/services-support/technical-tools/downloads#cp1e ) , pages 248-253 in the "CP1E CPU Unit Software User's Manual" (Image 04) describes a sample communication to an "Inverter Slave". I want to use the Arduino Slave as the Inverter Slave just to be sure that all previous steps are correct. Therefore, I would like to know: 1- As illustrated in Image 02, Am I missing any resistors? 2- Should I connect the GND to the FG? 3- In this scenario, the DIP switch setup should be as illustrated in image 03? Only DIP4 is OFF. 4- Can I test it just forcing A641.00 and checking the DM Area Data, as shown in Image 05? The code used in it is the following: // Wiring: Arduino and MAX485 // RX0 - RO // TX1 - DI // D2 - DE/RE #include "SimpleModbusSlave.h" enum { REGISTER_0, REGISTER_1, REGISTER_2, REGISTER_3, REGISTER_4, REGISTER_5, REGISTER_6, REGISTER_7, REGISTER_8, TOTAL_REGS_SIZE }; unsigned int holdingRegs[TOTAL_REGS_SIZE] = { 0, 1, 2, 3, 4, 5, 6, 7, 8 }; void setup() { modbus_configure(&Serial, 9600, SERIAL_8N1, 1, 2, TOTAL_REGS_SIZE, holdingRegs); } void loop() { modbus_update(); }   Any answer can be helpful. Thank you for your time!   Regards, Jose.