Search the Community

Showing results for tags ' firmware revision 5.007 or later -1756-eweb controllogix ethernet/ip web server module'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 273 results

  1. Is it possible to upgrade the firmware in an NJ controller?
  2. I'm using Controllogix L61 redundancy system as a slave with DCS using ethernet tcp/ip socket programming. The communication between master and slave will fail after a switchover. Kindly give solution for this. Thanks and regards, Rasu
  3. Hello, I need to make an ethernet communication Siemens S7-300 <> Omron G9SP. The HW of the Siemens that i us are CPU 315 2DP and CP 343-1 Lean. I did try to follow the Omron manuals Z922 and Z924, but faced with some problems. First of all in Z924 there is no complete HW configuration of Siemens (communication configuration is missing). Also, formats of messages differ in both manuals. Maybe there is an Simatic Step 7 project example, that i could open with Simatic Step 7 manager to do a deeper investigation, or maybe somebody has a lot more experience in this case? Thank you in advance.   WBR @rturas
  4. Hi everybody: I'm writing here because I have an Etherhet problem with my compactlogix 1769-L32E. I connect a crossover cable between my pC and the controller, then I run the BOOTDHCP server program . The BOOT DHCP window only shows the MAC of the PC, the controller´s MAC doesn't show even if i wait for more than 10 minutes I hope you can´t hel  
  5. Logix Designer tips

    Hi, I would like to know how to find a particular instruction in my ladder code. I'm on Logix designer. Thanks in advance  
  6. Good afternoon Mr.PLC forum members.   We recently had a fuse blow on the wiring between a 1756-OF6CI analog out card and a control valve (which we have no feedback for - only the 0-100% output). Took a little longer to troubleshoot since we have no feedback and we also don't monitor individual channel status of the card. For input cards (1756-IF8H or IF16H), it's easy enough to use the under-range/over-range or broken wire signal to troubleshoot a blown fuse or bad connection, and activate an alarm. I have been told by our local consultant-technician that there is an equivalent monitoring bit for output cards. Reading the instruction manual for the 1756-I/O cards, the fault channel bits do not seem to have this type of function for the 1756-OF6CI. The fault bits only seem to look at the requested output values, and at the connection between card and PLC itself as far as I can tell.  Am I missing something?   thanks for your help
  7. We're running KEPServerEx 4.5 with the AB drivers to interface with a Siemens WinCC HMI. All we've done is change the L61 processor with an L72 and then KEP shows the incorrect values for the tags. We stick the L61 back in and all is okay. The Device properties haven't changed as the L72 is part of the ControlLogix 5500 family. The IP address is the same as well as the project name, etc. I've checked the properties against the KEP manual and all is okay. The manuals I have don't mention editing a device in KEPServerEx. I feel we've missed something. :hmmm: Any thoughts?
  8. Hello All,   I am would like to know how to send a bit from an excel file to an omron PLC through CX-server in order to confirm that I have communication and the excel file is open.   At the moment I am reading data from the PLC on the Excel file no problem but I don't know how to do it on the other way.   I am attaching the code I have written and the excel file. So the idea is having a cell with a 1 and reading this value as a bit ON on the PLC.   Thank you very much in advance I really  appreciate it. :)    
  9. Hello All,   I am having some issues with Excel while communicating with the Omron PLC. The Excel file is getting the data from the PLC and the macro doing what I want to do, but I am getting the following error messages when opening the excel file.   I am attaching the pictures of the messages and the code where debug send me.   Thank you very much in advance
  10. Hi Everyone! I try to read Analog Data in PLC Master through Salve Module (ECT-21) but i dont see any data, with an Digital Module i can read and write, but with analogic module i can't do anything. The analog module works perfect, i have 4-20ma Simulator and work fine. Modules: PLC: NJ501-1300 Slave: ECT-21 Analog: ADO81-V1 Can u help me? Regads..
  11. Version 2.0.2

    328 downloads

    free HMI/SCADA program WebN Server 2.0 (freeware) * manual & program download site : http://www.netran.co.kr * Web-N Server 2.0 (freeware) - PLC interface demo video : https://youtu.be/MuOFMwK7Qqs* Android phone app download : https://play.google.com/store/apps/deta ... .en2&hl=en- Windows 7/8/8.1/10 x64, .NET frameworks 4.6 over  - Mult-Language (tool language, view page language)  - PC monitor, Web browser monitor, Smartphone monitor - (Design once and monitor on multiple instruments)   Unlimited number of tags    Unlimited monitoring time    1,024 concurrent connections    Unlimited upgrade    Unlimited connection of       equipment (PLC, DCS, DDC ..)    Unlimited app push message   No Software fee    No installation cost    No registration fee    No license fee    No cost to use    No upgrade cost    Free Redistributable      
  12. free HMI/SCADA program Web-N Server2.0 (freeware) View File Program download site : http://www.netran.co.kr   Web-N Server 2.0 - video for PLC interface demo : https://youtu.be/MuOFMwK7Qqs   - Windows 7/8/8.1/10 x64, .NET frameworks 4.⁠6 over - Mult-Language (tool language, view page language) - PC monitor, Web browser monitor, Smartphone monitor   (Design once and monitor on multiple instruments)   Unlimited number of tags Unlimited monitoring time 1,024 concurrent connections Unlimited upgrade Unlimited connection of equipment (PLC, DCS, DDC ..) Unlimited app push message   No Software fee No installation cost No registration fee No license fee No cost to use No upgrade cost Free Redistributable =============================================== Submitter webn Submitted 08/29/17 Category Free Utilities
  13. Hello,             I need to communicate Power meters ( GE Multilin EPM 5500P) to  GE Multilin EnerVista Software. The present communication system uses Ethernet for communication from LAN Switch to Computer. There are a few existing Power Meters which need to be connected to the  Network. The Meters having output ports as RS485. I need to use a convertor for that right. So when I contacted GE they told me to use GE Multilinet Serial to Ethernet Convertor. But due to the price and unavailability of the material I am thinking to use a universal convertor. Is that compatible for Multilin Devices?? and In Case of using a universal Convertor does we need any other drivers for that. Please Help Me.. Thanks In Advance  mnetman-a3.pdf multinet (1).pdf PM-GE.pdf
  14. Hi Everyone! Where are my experts? I am undertaking a project at work. The project contains analog style motor positioning circuits (operational amplifiers, integrators, and other PI elements). Not that this is relevant to the post yet ;) .It's my first PLC project ever! I am using the Schneider M258 with SoMachine 4.1 The PLC is talking to SoMachine via Ethernet (obviously I have a router between the PLC and my pc).I can Login and run the first POU I created. It's a simple And logic circuit for now. I have a co worker (c programmer) agreeing to help me pass data from my PLC to a browser screen. Although he's not familiar with PLC he's quite skilled writing code. He has wrote a Modbus protocol which allows him to interpret Modbus commands on his desktop.   1) Do I Need any special hardware to pass the data out of the PLC into the Router then into his browser. 2) As a trial can I send him MODBUS commands regarding my AND circuit? 3) How do I create such a command? 4) Is it possible for him to send me Modbus commands to change variables inside my program? 5) Are there web browser "plug-ins" for this idea? Thanks for reading and hopefully all of you can help me answer some of these questions.        
  15. Is CP1H with Ethernet option board (CP1W-CIF41) is capable to communicate More than one client? If yes what settings I need to be Done?  
  16. FX3U to FX3U via wifi

    Good day fellow PLC ninjas! I have a question/ concern which I would love your opinions on. We have 3 FX3U PLC’s+ENET cards. Two of the 3 PLC’s move around in an EMS trolley. The other is a ‘base station’ with a GOT2000 connected via Ethernet. Base PLC IP = 192.168.1.11 HMI IP = 192.168.1.31 Carrier 1 IP = 192.168.1.61 Carrier 2 IP = 192.168.1.62 I have programmed the base PLC to use Active communication; we are using fixed buffer communication to send and receive data to/ from the Carriers. The carriers are set up as Fullpassive ‘slaves’. This part works well and the update time changes (using a counter in the base station) from 1s to 100ms (because it enters a different work station).  My issue is the following: using a network sniffer (WireShark), I pick up plenty of re-transmits and sequence number errors coming from the base PLC’s ENET card. This is troublesome and causes delays when the update time is required to be fast (100ms). I am sending and receiving 10 words of data. The wifi seems stable, and there is minimal noise in the area. The power has been turned down and the antennas used are suited well for the application. The antennas are at a similar height to minimize possible loss of signal. I have LOS (line-of-sight) to the carriers at all times; to at least one of the antennas (I am using 802.11n). Has anyone picked up issues or found settings which can be used for comms over wifi? I can easily do this using a S7-1200 Siemens PLC and have done so using 12x S7-1200 clients and 2 AP’s with 1 base PLC. I have also successfully done this using 8xFX3U client with a System Q base PLC. My suspicion is that the delay in reading and writing to/ from the BFM in the ENET card is causing this. I am not sure that if I change to a FX5U will help. The communication cards on the Mitsubishi PLC’s seem very limited. Does anyone have any technical details on the access times between the CPU and communications cards’ BFM? Help is as always, appreciated.
  17. [Utilities] - NX-EIC202 Utility

    NX-EIC202 Utility View File A nice little utility created by PMCR that calculates the power consumption for NX I/O, provides the I/O layout for a given allocation, creates symbols for use in CX-Programmer and aliases for use with an RSLogix5000. Submitter Michael Walsh Submitted 09/22/16 Category Utilities
  18. Looking for some servo application help. Software: I have GX works 2, GT Designer, and GX Developer.  Hardware: PLC L06CPU-P, GOT2000 HMI, MR-J4-350B servo amps, HG-JR35JK motors, LD77MS2 Pulser I have (2) AC servos that will simply move an aluminum frame backwards and forwards using a FESTO belt mover and I have a servo gear reducer 20:1. I have a "simple motion module"and all of this hardware and software, plenty of time, and would really like to finish this project off. But this is my first servo and my first hmi project. I have some experience with Omron, Mitsubishi, and Allen-Bradley plc's, and consider myself novice at best. Any sample programs or help getting me started would be greatly appreciated!  
  19. Hi all. My experience is using Studio5000 / RSLogix5000 to program CompactLogix PLC's. I need to use a basic (cheap) PLC to get data from a Control Techniques Drive (about 9 DINT's for Speed, Torque, etc) and then display on a PanelView Plus 600. Its a bit extravagant to use even a basic CompactLogix for this, so I believe the most basic AB solution I can go for is the Micro820.In Studio5000, to add in CT Drive comms, I simply just add a Generic Ethernet Module and setup the IP address of the CT Drive and the Connection Parameters and that is pretty much it. I look in the Controller Tags and there is my DINT array that I can interrogate for the information. Very simple.Anybody any clue how to replicate this in Connected Components Workbench for the Micro820? I cant seem to fathom it out at all?Just to clarify, I am not doing any control of the Drive from the HMI or Micro820, merely displaying on the HMI parameters like speed, Torque, etc.Thanks.
  20. Hi, I have encountered an unexpected "PRI" LED indication of 1756-RM Series B module. When the affected redundancy module is set to primary, the status of the "PRI" LED indicator is blinking red. On the other hand, it is set to a solid red when the RM is set as secondary. I have read the manual and there are only two expected behavior for the "PRI" LED indicator, green if it is set as the primary and off if it is secondary. Does someone encountered this scenario already?   P.S. The RM does not have any minor/major faults when accessed. The status indicator indicates "PRIM" when the affected module is set as primary and "SYNC" when set as secondary. Manual switchover between controllers are done and was successful. Thanks in advance! Regards, RIValencia
  21. FT View Site Edition v.8

    I have been tasked with pointing our FT View application to a remote SQL server for all data logging.  I'm having some issues getting this to happen.  I've configured everything I can find in our test environment, but FT View still points to the local SQL Server instance.  There must be a setting I'm missing.   For instance, when i go to Tools -> Diagnostics Setup -> Destination Setup -> ODBC Database, and I point to the system DSN I've created pointing to the remote server (and even enter the correct remote credentials), when i create a table, it goes to the local sql server instance... I've restarted multiple times.   Any direction would be appreciated.
  22. Hello all, I am still fairly new to this forum and PLC's in general. I am trying to connect a EA9 touch panel via Ethernet to an Allen Bradley Micro Logix 1400 PLC. I am using Ethernet over serial because I need the serial connection to program while using the touch panel. I have given the Panel the IP Address 192.168.1.20 with a subnet mask 255.255.255.0 and I have given the PLC the IP address 192.168.1.10 with a subnet mask 255.255.255.0. The panel is not communicating with the PLC and I have very little knowledge on the subject, anyone's help would be greatly appreciated. The picture on the top is from the PLC and the picture on the bottom is from the C-More program for the panel.
  23. Hi guys. I have 1 cj2m cpu33 reciving 3bits of info from 3 other plcs (all similar type cj2m cpu 34-33) The problem is that 2 bits are ariving the third one is not. See the pictures i uploaded:   I do not know these instructions, in the other cases it was working. However i noticed that the output plc had a different adress with D950. I changed the adress to D804 as you can see on the pictures but still not reciving the data.  I guess i will have to configure somwhere else also. All i found (https://www.myomron.com/index.php?action=kb&article=1416) on internet that i have to open this datalink tool from the integrator. When i actually do that of course i just get an error: FATAL Error. Cannot read the file.   How can i make this work? Is the other way to constantly send this one bit with ethernet? Any sollutions, advices are welcome!
  24. Connecting PLC to ethernet

    Hello, Just recently bought a used CJ2M-CPU33 Omron PLC and I am trying to hook it up via ethernet. I keep getting an error F3. I figured it was because I didnt populate my I/O table so I did that and still no change. I have tried to connect to it via USB (which works fine) and then upload it a new IP address but no luck. Communication problems are my enemy and any help would be appriciated. Its a CJ2M CPU33 with a PA202 power supply. Analog in and out, digitial in and out cards. Thanks
  25. Hi guys,  I am sorry for posting same issue over and over but  I really want to get over with this one. The way PLC program setup and actual structure of rack is different.   Could it be a problem when I try send an email from ControlLogix by using MSG command? When I put 1,2 in the path field, It shows Au200_2 but it is supposed to be Au200_3. Any help would be appreciated. Thank you for your time  I really appreciate it.