Search the Community

Showing results for tags ' firmware revision 4.006 or later -1768-eweb compactlogix ethernet/ip web server module'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 218 results

  1. Good Day, I am seeing intermittent bUs (communication bus) errors on 3 VFD's simultaneously.  These are Yaskawa P1000's with CM092 Industrial Ethernet Cards. There are Stratix 5700 switches between the drives and the Controllogix 1756-L75 CPU.  Happens every day to every week -- intermittent. Reading parameter F6-98, it indicates a 'connection time out'.  I don't understand why I would receive this fault.  IGMP snooping and querier are enabled on all switches, if that matters. I do not have unicast checked but Yaskawa said that didn't matter.  Packet time is 100 milliseconds.  I welcome any input on what might cause this.  One Yaskawa tech said I should set speed to 100 Mbps (now set at 10 Mbps). Any help appreciated.
  2. Hi All  I'm struggling to a PLC using WAGO's e!cockpit software which I am new to.  In the network tab when I click to select "ETHERNET" from the "Scan Settings" area all that comes up is a drop down with "update selection" which does nothing.  As a result I cannot scan for the PLC's on my network. Has anyone got any ideas on this issue.  I'm running on windows 10, could that be a problem?     
  3. Fuel tank level automatic report

    Hello, I have a fuel level reading system in a 2000 gallon diesel tank. the system has a slc 5 05 of rockwell. I need to connect the system to a printer located in an office 300 meters away from the tank. can someone give me lights about the type of printer I need and what communication technology to use, preferably wireless. Thanks.
  4. Hello forum! I'm using AB Compactlogix 1769 L35E CPU energized by 1769-PA2 power supply which is also supplying to 1769-SDN DeviceNet scanner, both via backplane. Trying to build a simply DN network connecting the scanner to a Balluff BNI DNT-104-000-Z004, which is a 16 PNP digital input block, since is only input module I rely that no extra power supply will be required. The problem is that when connecting both scanner and input block via my DN thick cable (Balluff BCC07YY), the input module does not energize. In fact I got no voltage reading when measuring voltage between scanner V+ and V- terminals. I measured voltage at 1769-PA2 power supply DC output (which is not in use) and its providing 24VDC, also scanner is powered on so I do not think the problem could be power supply nor backplane. Scanner display shows 92 number, scanner manual says that 92 error is "no devicenet power" and has the following description: No network power detected on DeviceNet port. Provide network power. Make sure the module drop cable is providing the proper power to the DeviceNet port. Which I do not get, is not the power supply from 1769-PA2 via backplane enough?  Is not the scanner supposed to provide voltage to the network? I've no grounding connection connected to PE yet (just between devices GND terminals)... is that a problem for testing this small network? It will be done soon but now I'm waiting for cable material. Actually I'm online using Studio5000 and have 1769-SDN DeviceNet scanner device declared at the project, there is no warning nor major fault displayed from the software. Thanks for reading.
  5.   Hello, everybody.. i want to ask how to communicate the A1SJ71LP21 module with the QJ71LP21-25 module using fiber optic cable? can anybody help me to configuration that?    
  6. Hello.. I have hmi Proface GP-4301TW, USB type B cable and ethernet cable. I want to transfer the program to the hmi but I cant. When I turn on the power of hmi,  a series of test appears and finally it looks like the photo below and I cant enter the offline menu.. can anybody help me to solve the problem?
  7. I'm trying to understand the basics of using a serial to ethernet converter such as this Comtrol DM-EIP-2101, with Studio5000 code. Basically I have a weighing machine that only outputs data via RS-232 and I need to send that data to a PC that will process it through a Studio5000 program and have the data displayed on an HMI using FTview SE. Is it as simple as just connecting the serial and ethernet to the converter and it does all the work? Obviously checking ip addresses and firmware will need to be verified. The main thing I am unsure of is the process of passing the individual data packets from the machine to the Logix code on the PC,  things like what the weight of the item was, was it over weight or under, etc....  Would there be an AOI or tags built into the software for a machine like this Checkweigher? I've worked with much smaller items like Cognex Dataman cameras and I know you can just use their AOI that allows you to simply call a tag if you want to display information like if a scanned barcode was correct or whatever. If anyone has done something similar I'd appreciate any guidance. It can be difficult getting the information from the manufactures so I'm looking for answers anywhere I can. EDIT: I guess I should also clarify that only using one or the other (serial or E/IP) is not an option. It will be a serial connection from the Weighing machine to the converter and then Ethernet to the PC.
  8. Is there a way to monitor the Temperature of a Servo Motor on Allen Bradley Servo motors... MPL? PLC: CompactLogix 1769-L30ERM Drive: Kinetix 6500   Motors: MPL-B310P-MJ72AA, and  MPL-B560F-MJ72AA I would like to be able to monitor the temperature, and flash a warning screen on the HMI if the Motor gets too hot, or perhaps shut down the operation before the Motor overload trips. The drive and PLC are connected through Ethernet IP What I don’t know is if that Motor heatsink temperature information is available to the PLC.
  9. Hi All, I am new with PLCs. Currently I have a project that required me to send a 12 alphanumeric (2D code scanned) from multiple CP1Hs to NJ101. Then NJ101 will directly send the data into a SQL (haven't made yet). So basically, there are a few hurdle that I face. 1) How send data from CP1H to NJ101.  - I have tried using _CPU010_SendData from CP1H but I'm not sure how to do the ladder or what to use on sysmac (NJ101) side. Btw, I really not familiar with sysmac.  This is the first project that I use sysmac.  - I have read about TCP IP, Fins/UDP and Fins/TCP but I'm not familiar with those method. 2) How to confirm that NJ101 has received the data from CP1H 3) How to arrange the data received from CP1H into SQL - This one I have a sample program that I can follow from my colleague. 4) Setting up a dummy SQL server just for the sake of testing. - I don't have any idea on this. I anyone have an application or software that can used to test the database function, please let me know.   Your helps are greatly appreciated!   Thank you! Bob
  10. If you’re looking for a SCADA with extensive support for a wide range of PLCs and protocols, check out IntegraXor. It’s robust, feature-packed, and user friendly. The built-in web HMI lets you access your processes anywhere, anytime, on any device. Official Website
  11. All, I have been trying for days to find a way to control a yaskawa v1000 over Ethernet. I have been trying to use explicit messaging but I cannot find the instance class  etc in any of the yaskawa literature. All I can find is to use EDS files with RS5000 but I have a micrologix 1400 and I don't have that capability. If anyone has any recommendations let me know. Thank You, Liam M.     
  12. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  13. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  14. Hello I have a problem with dl-ep1 ethernet modul. I connected the module to a IL-1000 sensor amplifier. There is some problem with the communication. How should I adjust ? I made some pic about the trouble. The sensor is a IL-600 laser distance sensor. I dont know yet how can I get the actual value.  Anybody knows how to set this modul ? If I think correctly after the right setting, if I check the sensor output:0 then, I can see the actual value of the IL-600 sensor. But unfortunatelly this part also not so clear for me, because I can connect about 15 sensor this ethernet modul.  Thank you so much if anybody help.
  15. I have a cpu33 that I had issues with a bad battery and it loaded from memory card.  The version on the card was old so I decided to download the latest version from 2 days ago to it.  When I did, I lost communication through ethernet.   Can't connect through usb either.   The thing that baffles me is that I can ping the plc at the address and I get a reply.   Any help/suggestions would be greatly appreciated as I am not familiar with omron plc's at all.  Also on the display it cycles through Er HE 1P 07.
  16. Graphic Operational Controller

    Please give me the steps how to communicate GOC with Laptop using Ethernet and serial port I have using Codesys for Programming
  17. Hi everyone,  I am trying to use Kepware to communicate with my PLC setup which is the iQ-R Series R08PCPU.  I read the documentation which is available at https://www.kepware.com/getattachment/3daf1ac3-5c76-49ce-bbfe-f0fb1015f6cc/mitsubishi-ethernet-manual.pdf I read through the setup for Kepware and the setup procedure for iQ-R series but it still didn't work.  From the documentation, it said something about "using special ladder logic to enable ethernet communications is required.", I couldn't find anything about this online.  Here what I did in addition to the documentation: - Enabled IP Packet Transfer - Ping the PLC's IP Address which was successful Does anyone have any idea what I didn't do to establish that communication between Kepware and R08PCPU?  Thank you in advance. 
  18. I have a AB CompactLogix L43S with 1768 ENBT Ethernet/IP module. I would like to talk to a TCP/IP device (such as my laptop) from the PLC. How can I do this without using RSLinx? 
  19. I have a line that I'm integrating that requires the main machine (Q13UDVCPU) to communicate via the built in Ethernet port with 3 different up and downstream machines using FX3G controllers with FX3U-ENET modules.    We are using GX Works 2 software. So far I'm having no luck with the Mitsubishi documentation, or online.  Some (old) sources say it is not possible, I hope that is not the case. What I could really use is a working example program to look at and dissect.  But any help would be appreciated.
  20. Anyone know any free libary to communication with FX3u-enet-adp, please help me ? Note: I've used mx Component , it work very well but it is too expensive and I dont even know it can work in windows server 2012/2016 or not.  one more question, Is there otherway to make program run in other computer without install mx compoment, it is very huge to install in every client computer Thank for reading and sorry for my bad english  
  21. Communication error

    Hey Guys,    This is my first time on a forum like this! but i need a hand with something if someone could point me in the right direction.   I have a Powerflex 40 drive communicating over Ethernet/IP to a switch, That drive has four Powerflex 4's connected to it thru DSI connection. They seemed to be wired correctly and seem to be sound connections but when someone on the production hits an E-Stop it removes power from this bank of drives. (Which is standard here) . However, when they power back up i get an F081 Error (Comms lost) on the master drive and one slave. Also, the port light on the 20-comm-e(Powerflex 40) is faintly flashing about every 5 seconds and is the only light on. In this state, none of them communicate. However, when i unplug the DSI cable, the 20-comm-e powers back up to normal operation. I then plug the DSI back in and everything works fine.  Should i start replacing parts or is there some parameters/other wiring i could check?   Thanks guys.
  22. CompactLogix I/O Fault

    Hello, Back in December 2017, we replaced a customer's PLC-5 control system with a CompactLogix.  Everything was working fine until about a month ago, when they started having an I/O fault, Code 16 - I/O module connection failed on required module.  At first it was showing up on multiple modules, and also the end cap.  However, after a few more faults, it was only showing up on module 2.  We replaced that module and the faults stopped for about a week and then returned.  The module we replaced is a 1769-IA16. Any idea what may be causing this?  The customer insists nothing was done to the panel since the initial installation.  
  23. I recently had an issue where a system shipped to a customer's site with a mismatch between the IP address loaded into the CJ1W-ETN21 card and the node dials on the card itself.  We had been testing the settings of the card by pinging the address and had assumed if the node dials were wrong we would not be able to ping the card.  As we just found out that is not the case! Both our quality department and our customer's end user were able to ping the Ethernet card, but the end user could not establish FINS communications because the node dials were not correctly set. Is there a way to test that the dials are correctly set?    Thank you!!!
  24. Is it possible to add another AB Rockwell PLC to the network tree as a Generic Ethernet Module and use it as IO? Any idea where I would find information regarding assembly instance and size of I/O/C for AB Rockwell products? If possible, what are the pros and cons when compared to produce/consume and MSG instructions? Don't need to use it real world, just curious. Many thanks in advance.
  25. Delta PLC Analog Noise Reduction

    Hello All, I am Using Delta SE Series PLC and 06AD Module for Pressure Transmitter. But Analog input get fluctuate continuously. Is anybody have program for analog scaling.