Search the Community

Showing results for tags ' comm. settings depending on hw used.) connect any mb client/master or server/slave device(s) to your clgx plc'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 72 results

  1. Device point error between Parameter and PLC

    Hello all, I am a beginner with PLCs programming. I have an issue on GX Developer programming software from Melsoft trying to program my Mitsubishi Q-series PLC. CPU is Q03UDCPU. When the program is written and I try to upload it to the PLC, with the write to PLC window, I check -Program -- MAIN and -Prameter -- PLC/Network/Remote, click EXECUTE and a message appears : "Device point that is set in parameter is not match the device point in PLC". I can't fix it. In Parameter - PLC Parameter - Q parameter setting (window) - I/O assignment tab : I have (see image). Whe I use CHECK button it says there is no error. The X41 input device is plugged on slot 1/00. I am making this folowing the instructions a PDF I found on the Mitsubishi electric's wesite : Q-series basic course (for GX Developer). Thanks for the help, A. S.
  2. If you’re looking for a SCADA with extensive support for a wide range of PLCs and protocols, check out IntegraXor. It’s robust, feature-packed, and user friendly. The built-in web HMI lets you access your processes anywhere, anytime, on any device. Official Website
  3. Hello I have a scenario that's been bugging me for some time now. The scenario consists of a Micrologix 1400 that I need to control it's output from modbus/tcp. In detail what I really need is to be able to manipulate the O0:0 through modbus/tcp. The PLC would be the master and I would be the slave that triggers the connection to the master. I'm using a Modbus-Client on my PC and that should be the slave. Any idea as to how I can manage that? Currently I can send data to the master but everything is "stored" on B10 and I have no idea how I could write directly on O0. Thanks a bunch guys. PS: I'm borderline noob. 
  4. Hey everyone! New member here, and this site has always been a big help!  I try to help other folks too, but a lot of guys are super quick on here.   I've got a problem using some obscure components. I inherited a sensor network at work that uses Panasonic S-Link and I need to read them from a Q-Series. Panasonic makes a module that slots into the Q Series called an SL-VMEL-Q that I have.   My question is:  Did I do everything correctly on my Mitsubishi side? I put it into the parameters as an intelligent module with 64 points and I put the correct address in for the start I/O. Is that all I have to do?  This is the first time I used a module that wasn't on the drop down list when you add one in GX Works 2.   I can read and write to the buffer memory, but I can't get the unit to send to or receive from the sensors. I think the problem is that there is no end unit on the S-Link line (I don't know if it's just a terminating resistor or what), but it previously worked without one, so I can't be certain.
  5. Omron CJ1m - bluetooth connect

    Hi, I write app to smartphone to communication omron CJ1m and Android. I want to connect devices by standard bluetooth. I plug in bluetooth adapter directly to omron RS232.  I want to ask you, how i can connect by FINS command. Bluetooth device baud rate is set 9600. If i connect to omron, i sent code: "AC01" and i sent how long as omron return me "AC01" ?? And what's next command i sent? If I want read CIO 10 i sent: "0101B000000A" ? and FCS and "*" ?? how i calculate FSC? Is it XOR my data sent? 
  6. Password Protected LS Master K

    I have a customer that has a LS Master K PLC, and he needs me to make some changes to the program. I am not the original program writer so I do not have the original program nor the password. And the company that originally made this program does not exist anymore. Does anyone have any suggestions on a software or a device that can help me either find the password or just bypass it. I need help ASAP Please!!!!! I saw there is a password breaker while i was googling, but the software cost $50, and it looked a little sketchy so I am kind of hesitant to trust 1 purchasing the software and 2 downloading it only my work laptop. Please help!!
  7. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem.
  8. Communication error

    Hey Guys,    This is my first time on a forum like this! but i need a hand with something if someone could point me in the right direction.   I have a Powerflex 40 drive communicating over Ethernet/IP to a switch, That drive has four Powerflex 4's connected to it thru DSI connection. They seemed to be wired correctly and seem to be sound connections but when someone on the production hits an E-Stop it removes power from this bank of drives. (Which is standard here) . However, when they power back up i get an F081 Error (Comms lost) on the master drive and one slave. Also, the port light on the 20-comm-e(Powerflex 40) is faintly flashing about every 5 seconds and is the only light on. In this state, none of them communicate. However, when i unplug the DSI cable, the 20-comm-e powers back up to normal operation. I then plug the DSI back in and everything works fine.  Should i start replacing parts or is there some parameters/other wiring i could check?   Thanks guys.
  9. Lets say i have a PLC, with a name PLC1 with IP/Subnet of 10.125.34.243/255.255.255.0 I have to communicate this PLC1 with 2 other PLC's, PLC2 and PLC3 PLC2 with IP/Subnet of 10.125.34.10/255.255.0.0 PLC3 with IP/Subnet of 10.125.46.10/255.255.0.0 I imagine that, all these three are in different subnets, and so there should be no communication at all, but when i tested it, PLC1 to talking to/from PLC2 and not PLC3.  anyone know the answer to this ? How does it talk to PLC2 with different subnet, but not PLC3 which is in different subnet as well. 
  10. mitsubishi nexgenie plc target settings View File This target setting files are used with codesys software for programming mitsubishi nexgeine PLC series,    Submitter lionheart86 Submitted 01/18/17 Category Demo Software
  11. ab

    The HMI server in area 'RNA://$Local/Spring_Insertion' refused to load it's project. The HMI server is not licened and cannot open a project with more than 5 displays
  12. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem. Thanks in Advance..
  13. channelconfiguration setup

    Dear Engineers, Please hep me to send and read data in ML1400 through rS485 communication. Regards, Prasanna +918970424843
  14. I need solution for master & slave configuration between 2 PLC Twido TWDLCAE40DRF. My final project is about a system for filling drink on a cup and do the packaging. the component of the project is the filling system (dropping cup, filling water, pressing the seal) and the packing (packing into a box and sealing the box). This project is using 2 PLC Twido TWDLCAE40DRF. My problem is how to configure one of them as the master and the other as the slave. I've read the manual book but it's hard to understand the instruction. if anyone can give a simplify explaination to me please reply this post or you can reach me at mail: tatangprayoga11@gmail.com  
  15. Hello I would like to connect 2 HMIGXU 5512 to my Modicon M221 is it possible please?
  16. Omron 3G3HV Problem

    Hello guys, I got a used Omron VFD from a friend. It was used in an industrial application. It works fine with the integrated panel. I would like to use it to run my drill press. I now try to control it by the so called 3 wire sequence (S1, S2, S3) for Start, Stop and forward/reverse. System does not work as expected, i. e. no reaction on the switches. I'm not sure if I have messed up the configuration of one of the n xxx parameters or if there is a HW problem. With SC open, there is no voltage at that pin (expecting 24Volts?!). Any thoughts? regards and thanks, Matthias   Current config: n001 = 4 n003 = 1 n004 = 0 n006 = F/R 052 = 0 n176 = rdy n177 = 1
  17. Hello All,   I am would like to know how to send a bit from an excel file to an omron PLC through CX-server in order to confirm that I have communication and the excel file is open.   At the moment I am reading data from the PLC on the Excel file no problem but I don't know how to do it on the other way.   I am attaching the code I have written and the excel file. So the idea is having a cell with a 1 and reading this value as a bit ON on the PLC.   Thank you very much in advance I really  appreciate it. :)    
  18. Hello All,   I am having some issues with Excel while communicating with the Omron PLC. The Excel file is getting the data from the PLC and the macro doing what I want to do, but I am getting the following error messages when opening the excel file.   I am attaching the pictures of the messages and the code where debug send me.   Thank you very much in advance
  19. Version 2.0.2

    221 downloads

    free HMI/SCADA program WebN Server 2.0 (freeware) * manual & program download site : http://www.netran.co.kr * Web-N Server 2.0 (freeware) - PLC interface demo video : https://youtu.be/MuOFMwK7Qqs* Android phone app download : https://play.google.com/store/apps/deta ... .en2&hl=en- Windows 7/8/8.1/10 x64, .NET frameworks 4.6 over  - Mult-Language (tool language, view page language)  - PC monitor, Web browser monitor, Smartphone monitor - (Design once and monitor on multiple instruments)   Unlimited number of tags    Unlimited monitoring time    1,024 concurrent connections    Unlimited upgrade    Unlimited connection of       equipment (PLC, DCS, DDC ..)    Unlimited app push message   No Software fee    No installation cost    No registration fee    No license fee    No cost to use    No upgrade cost    Free Redistributable      
  20. free HMI/SCADA program Web-N Server2.0 (freeware) View File Program download site : http://www.netran.co.kr   Web-N Server 2.0 - video for PLC interface demo : https://youtu.be/MuOFMwK7Qqs   - Windows 7/8/8.1/10 x64, .NET frameworks 4.⁠6 over - Mult-Language (tool language, view page language) - PC monitor, Web browser monitor, Smartphone monitor   (Design once and monitor on multiple instruments)   Unlimited number of tags Unlimited monitoring time 1,024 concurrent connections Unlimited upgrade Unlimited connection of equipment (PLC, DCS, DDC ..) Unlimited app push message   No Software fee No installation cost No registration fee No license fee No cost to use No upgrade cost Free Redistributable =============================================== Submitter webn Submitted 08/29/17 Category Free Utilities
  21. Rx3i to Balluff IO Master

    Wanting to write to Balluff Smart Lights via IO Link Master IP #BNI EIP-502-105-Z015.  I can find lots of literature on setting up the communication via E/IP in RSLogix 5000 but haven't located anything with Machine edition for writing the data over IP.  I am utilizing an Rx3i platform with IC695CPU315 and IC695ETM001 for network access
  22. Hi, I am doing a project with three Omron Cj2m cpu.  I dont know how to connect More than one Omron Cj2m Cpu Plc in a same network to communicate each other with a Internal Memory addresses. Can any one help me to understand?
  23. FT View Site Edition v.8

    I have been tasked with pointing our FT View application to a remote SQL server for all data logging.  I'm having some issues getting this to happen.  I've configured everything I can find in our test environment, but FT View still points to the local SQL Server instance.  There must be a setting I'm missing.   For instance, when i go to Tools -> Diagnostics Setup -> Destination Setup -> ODBC Database, and I point to the system DSN I've created pointing to the remote server (and even enter the correct remote credentials), when i create a table, it goes to the local sql server instance... I've restarted multiple times.   Any direction would be appreciated.
  24. Mitsubishi iQ-R Series

    Hi Has anyone got any real life experience with the new Mitsubishi iQ-R series?  I have been assigned a major capital project to replace our old ageing DCS system.  Our current PLC backbone is about 40x Q2ASHCPU, 10x Q06UDEHCPU and about 2xA2SCPU all linked up via Melsecnet/10 network with communication links into the DCS system via Modbus RTU utilising the QJ71MB91 modbus card. Due to the nature of my companies process and the limitations on plant downtime it is estimated this project could take up to 5 years to complete, with this in mind I am wanting to install a system that will not be obsolete (or unsupported) in a few years, hence, I am very interested in the new iQ-R series with it being Mitsubishi's latest and greatest.  However, recent communications with my local Mitsi rep is not filling me with confidence that the iQ-R series is not as well supported/developed as the Q series.  A major requirement during the development stages of this project is the new ability of the new processors to be able to talk to the old DCS up until a point where the DCS nodes will be completed removed and replaced with a modern SCADA package.  Hence, the requirement of a Modbus Slave card for the iQ-R (i.e. a QJ71MB91 equivalent) which I am told is in development, but has no fixed timescales.  Previous experience with Mitsubishi developments of cards is normally years not months. Any information anyone can provide on their experience of the iQ-R series would be greatly appreciated and if anyone knows if a Modbus Slave card is in development that would be useful.  I realise i could utilise the Q series extension rack with a iQ-R processor but this is not the route i want to go down. Thanks for any help and apologises for the war and peace. Cheers Matt
  25. In general, this control PLC program is written in GX Works. I did a simple visualization on TIA Portal v14 (WinCC RT Advanced) and I would like to now test it on Mitsubishi FX3U driver with ENET Module. I do not have much experience in this kind of thing, I'm still learning. I know that someone previously made a visualization in LabView and downloaded the tags from the PLC using NI OPC Server. Someone also did visualization in iFix and also downloaded tags through server opc. I do not know just how or what program to download tags in PLC so that I can no longer use it in visualization in TIA Portal. Unfortunately I still have a connection problem. The driver is connected to the router. From the connection options with RT Advanced I chose in the connections tab Mitsubishi and entered the appropriate IP. Still nothing. I do not know if the lack of a connection can be related to a virtual machine (VM Vare Workstation 12) on which I have TIA Portal installed. The driver pings but can not connect. I also tried using KEPServer EX to connect and unfortunately also failed. (I have information about the can not connect). Anyone know what program I should use? or had contact with such a problem? I attach a photo of communication from my station to more visualize the problem. Thanks