Search the Community

Showing results for tags ' are: -1756-en2xx controllogix® ethernet/ip communication modules'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 470 results

  1. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  2. We recently obtained a new Vendor ID (VID) Number from ODVA, 1477 for the purposes of developing an EtherNet/IP scanner device.  When we try to use that number with the Allen-Bradley PLC & Studio 5000 Logix Designer, our data type REAL's are showing up in Studio 5000 as SINT's.  We have seen this mangling of data types before when using the Omron VID, 47 with the same Allen-Bradley PLC/EIP Scanner.  The data types are being misinterpreted, or mangled from REAL to SINT, e.g. the *.eds file defines 32 REALs for Input and 32 REALs for Output, but within Studio 5000 we see 128 SINTs each for Input and Output. It is as though the Allen-Bradley/Studio 5000 database does not have our Vendor ID.  When I change the *.eds file, Vendor ID Number from #1477 to #1 then we see the *.eds file being properly read and interpreted, e.g. 32 REALs for Input and Output show up as 32 REALs each.  Does anyone know what file we need to modify in Studio 5000 ???  We want to add our Vendor ID #1477 to that file. Hardware: EIP Scanner: Allen-Bradley Compact Logix L18ERM EIP Adapter: Delta Tau Power PMAC Motion Controller (EIP OpeNer Stack) Thanks in advance! See screenshots below. within Studio 5000, see screenshots
  3. Hello to all, I am new here, and I have a project with FX3U plc and CR 2DA 700 robot controller. Does anyone have some experience in establishing communication over FX 3U enet module and robot controller, I need to send and receive 5- 10 M registers and D integers. Thanks
  4. Hello everybody, I have network from : PC - 192.168.3.11 PLC - 192.168.3.250 I change this option in FX5U PLC in GX Works3 for Network Ethernet port --> Application Setting -> Security -Disable Direct connect with MELSOFT : Enable/disable -DO not respond CPU module search : Respond / not respond and I upload program to PLC. After upload program to PLC and restart it was impossible to connect again. I Have ping between PLC and PC, but could't write program. Always writes me Error <ES:0180840b> So to disable Security Option you should to do : 1. Open Works3 2. New Project (Choose your PLC - FX5U) 3. Online menu 4. Specify Destination Communication 5. Click twice in PLC module 6. Set Connect via hub (In my case i connect PC and PLC directly !) 7. Choose IP Address ( in my project : 192.168.3.250 , PC must be in same network 192.168.3.X) 8. Give OK 9. Connect Test. With steps I disable security options and it was enable to connect to PLC and Write data on it. I Hope that will help to other with same problem. Special thanks to : Piotr Tynor(Mitsubishi, Poland ) , Adam Syrek (Mitsubish, Poland ) , I. Ayvazova (Bulgaria) , K. Raykov (Bulgaria)
  5. Hi All, Networking guy here, looking for network experts on a AB PLC (1756-EN3TR/B v217021900) which seems to STOP ARPing for a device after 10 ARP's. The device is purposefully powered down, but when powered up, it can take minutes before the PLC sees it again. The PLC team says only changes in the PLC's logic are made. When an older backup is restored though, I do NOT see the issue somehow. 1) The devices that are powered down are back on the network and reachable within 10 seconds or so (ping). The initial thought was that they were not even on the network, but they are. Just that PLC shows a comms loss. 2) With the 'good code', the PLC, once the device is offine, keeps sending ARPs to find the device. The first one is a directed one, the subsequent ones are broadcasts. These broadcasts keep happening till the device is back online and is able to talk to the PLC again. 1st ARP after comms is lost: 474.423859     Rockwell_cf:a7:6c     Hilscher_2e:ea:08     ARP      60     Who has 192.17.150.208? Tell 192.17.150.30 Next and subsequent ARPs after the first one: 475.423471     Rockwell_cf:a7:6c     Broadcast             ARP      60     Who has 192.17.150.208? Tell 192.17.150.30 These ARPs keep happening every 1 second, till the device is online again. 3) With the bad code, the PLC, once the device is offline, sends only 10 ARP messages total and then stops sending ARPs altogethe . Then it takes 10 minutes* before it sends another one. If the device is backup online by that time, the PLC finds it right away. SO with these 2 different code bases, how is that a low level L2 protocol like ARP is impacted so much. The PLC team tells me that they have no idea and not set anything related to it. My question is where is the ARP network behaviour governed and how to change it? How can older code which supposedly only has changes in logic have different ARP behavior? * The 10 minutes interval might lead people to think it's a ARP timer and most likely it is, but then people usually ask about gratuious ARPS (garp) and I've verified that they make it through from the device to the PLC OK. If the device is offline for say a minute, the PLC mirrored port does indeed see the garps, yet at that point the PLC is no longer ARPing and regardless of that garp, it has to sit out the time till it sends a next ARP till it connects. Thus, I suspect the coming back to life process is governed by the PLC ARPing for it, and not by the detection of a garps. Thanks everyone!  
  6. Hello, I was hoping for some help in trying to read/write to a handful of bits in a CJ1M-CPU13 controller from a Compact GuardLogix. The CJ1M rack has a CJ1W-ETN21 card that is already communicating to a handful of Yaskawa drives. Is it possible for me to communicate with this controller from a CLX unit over ethernet? I don't believe an ETN21 card uses EIP but is there a way around this? Right now, I'm struggling to even find the IP address of the ETN21 card as the CX-Programmer file provided to me by the customer does not have the card in the IO configuration and I've never worked with Omron PLCs before. I found a CJ2M to CLX guide but it assumes communication over Ethernet IP and the ethernet port is native to the controller. Any help at all would be appreciated. Thanks!
  7. Grupa ProfAs Sp. z o. o. jest firmą doradczą, świadczącą usługi w szeroko rozumianej dziedzinie Human Resources. Specjalizujemy się w rekrutacjach na stanowiska specjalistyczne, średniego i wyższego szczebla. Wierzymy, że nasz Zespół złożony z profesjonalistów jest w stanie zapewnić perspektywiczne spojrzenie i najwyższą jakość wykonywanych usług. Aktualnie dla naszego Klienta - firmy z branży automatyki przemysłowej - poszukujemy osoby na stanowisko: Programista sterowników PLC Kraków / Piła / Poznań ZAKRES OBOWIĄZKÓW: Programowanie sterowników PLC Siemens Wykonywanie aplikacji dla systemów SCADA i HMI Dobór konfiguracji sprzętowych PLC Testowanie i uruchamianie maszyn u Klientów końcowych (delegacje krajowe i zagraniczne) Wykonywanie programistycznych prac serwisowych u obecnych Klientów Sporządzanie instrukcji obsługi maszyn   WYMAGANIA: Bardzo dobra znajomość sterowników PLC Siemens Umiejętność parametryzacji serwonapędów, falowników, etc. Znajomość paneli HMI oraz systemów SCADA Znajomość sprzętowa oraz programowa komunikacyjnych sieci przemysłowych ProfiBus, Profinet, Ethernet, DeviceNet, Modbus, etc. Znajomość zagadnień i komponentów automatyki (przetwornice, serwonapędy, obwody bezpieczeństwa, aparatura modułowa, itp) Mile widziana znajomość programowania innych sterowników: Allen-Bradley, Omron Prawo jazdy kat. B Komunikatywna znajomość języka angielskiego lub niemieckiego OFERUJEMY: Współpracę w oparciu o umowę o pracę Udział w profesjonalnych szkoleniach Korzystne warunki wynagrodzenia Rozwój w firmie z doświadczeniem na rynku międzynarodowym nr w rejestrze 14990 Osoby zainteresowane prosimy o przesyłanie CV na adres k.dominik@profas.com.pl lub kontakt telefoniczny pod nr tel. 881 700 778.
  8. I'm using Controllogix L61 redundancy system as a slave with DCS using ethernet tcp/ip socket programming. The communication between master and slave will fail after a switchover. Kindly give solution for this. Thanks and regards, Rasu
  9. Hello, I need to make an ethernet communication Siemens S7-300 <> Omron G9SP. The HW of the Siemens that i us are CPU 315 2DP and CP 343-1 Lean. I did try to follow the Omron manuals Z922 and Z924, but faced with some problems. First of all in Z924 there is no complete HW configuration of Siemens (communication configuration is missing). Also, formats of messages differ in both manuals. Maybe there is an Simatic Step 7 project example, that i could open with Simatic Step 7 manager to do a deeper investigation, or maybe somebody has a lot more experience in this case? Thank you in advance.   WBR @rturas
  10. Cimplicity 7,5

    Good Day There is a SCADA Cimplicity and controller Control logix 5561 AB. Communication between them is organized via Ethernet IP. It is necessary to transfer some tags from the Cimplicity to the controller Control Logix. How to do it better? Through Rslinx DDE OPC or write scripts in the Cimplicity? 
  11. I am using rslinx in my configuration with 2 devices: windows xp computer and an SLC 5/05 CPU.  The XP PC is running a program that relies on a file that is automatically dropped in a shared folder from a separate networked PC.  The file is deleted immediately from the shared folder.  The program on the XP PC uses rslinx to control the SLC 5/05 CPU to complete the operation.  The original XP PC hard drive failed and a new PC was installed with all the necessary software and services.  Ounce I completed the  setup, the process worked for 48 hours, then stuck in one operation (one file).  Now, I can restart rslinx and the software and the process will function normally, but stall, then get stuck on one file.  There are no files in the shared folder, rslinks has not lost connection.  The original router was replaced at the same time as the PC.  I am leaning towards rslinx storing the files somewhere and stalling/stopping the operation.  I can not find files anywhere.  Does the SLC 5/05 CPU store the files?  I'm lost.  Do you have any troubleshooting suggestions?  
  12. Hi everybody: I'm writing here because I have an Etherhet problem with my compactlogix 1769-L32E. I connect a crossover cable between my pC and the controller, then I run the BOOTDHCP server program . The BOOT DHCP window only shows the MAC of the PC, the controller´s MAC doesn't show even if i wait for more than 10 minutes I hope you can´t hel  
  13. Is it possible to communicate from a PC program to PLC program for reading inputs and setting outputs? How can it be made ? is it possible to do from TER connector or AUX connector , without special comm module?
  14. Hi, I would like to know how to find a particular instruction in my ladder code. I'm on Logix designer. Thanks in advance  
  15. Good afternoon Mr.PLC forum members.   We recently had a fuse blow on the wiring between a 1756-OF6CI analog out card and a control valve (which we have no feedback for - only the 0-100% output). Took a little longer to troubleshoot since we have no feedback and we also don't monitor individual channel status of the card. For input cards (1756-IF8H or IF16H), it's easy enough to use the under-range/over-range or broken wire signal to troubleshoot a blown fuse or bad connection, and activate an alarm. I have been told by our local consultant-technician that there is an equivalent monitoring bit for output cards. Reading the instruction manual for the 1756-I/O cards, the fault channel bits do not seem to have this type of function for the 1756-OF6CI. The fault bits only seem to look at the requested output values, and at the connection between card and PLC itself as far as I can tell.  Am I missing something?   thanks for your help
  16. We're running KEPServerEx 4.5 with the AB drivers to interface with a Siemens WinCC HMI. All we've done is change the L61 processor with an L72 and then KEP shows the incorrect values for the tags. We stick the L61 back in and all is okay. The Device properties haven't changed as the L72 is part of the ControlLogix 5500 family. The IP address is the same as well as the project name, etc. I've checked the properties against the KEP manual and all is okay. The manuals I have don't mention editing a device in KEPServerEx. I feel we've missed something. :hmmm: Any thoughts?
  17. Hello everyone, Is there any way to communicate with Mitsubishi Servo amplifier MR-J2S-350CP through RS232 ,I prefer to use 224XP because i already have it... thank you 
  18. Greetings everyone, I am using a VERY OLD laptop, Windows 98, the correct AB cable....and only used to download programs into equipment to restore in emergencies into AB 5/04.  I was able to connect to SLC 5/04 using RSLinx (used Auto-Config, all worked correctly) , and wanted to install a program from earlier version using RSLogix500.  It seemed to download correctly, the pop-up asked if I was sure I wanted to install new program, hit YES...then said it would change channel, pop up buttons were "ALLOW" or "DENY" (something like that). I hit "ALLOW". All seemed good until I plugged HMI back in....had a bunch of codes it didn't like, so I went to install back to original version.  When I went through the same procedure (mentioned above)....5/04 and laptop no longer wanted to communicate.  I assume it has something with allowing the channel change.  As you can tell, I know Jack Squat...I'm not a programmer (duh), but was handed a computer with instructions....and now the machine is down.  Any help with getting me in right direction is highly appreciated in advance.  I searched the forum, and wasn't able to find a solution... I suppose it has to do with an in-experienced, well intending human messing with stuff he shouldn't be messing with !!
  19. FX3U PLC WITH OPTIDRIVE E3

    Hi can anyone help me to undestand more about modbus RTU between fx3u with optidrive e3 ?? I'm using rj45 with fx3u 485adp-Mb for the connection. Then specially in making the ladder program in Gx Works 2. I'm stuck understand the command code there. I'm first time using this. Please help me. Thank you.
  20. Hello,             I need to communicate Power meters ( GE Multilin EPM 5500P) to  GE Multilin EnerVista Software. The present communication system uses Ethernet for communication from LAN Switch to Computer. There are a few existing Power Meters which need to be connected to the  Network. The Meters having output ports as RS485. I need to use a convertor for that right. So when I contacted GE they told me to use GE Multilinet Serial to Ethernet Convertor. But due to the price and unavailability of the material I am thinking to use a universal convertor. Is that compatible for Multilin Devices?? and In Case of using a universal Convertor does we need any other drivers for that. Please Help Me.. Thanks In Advance  mnetman-a3.pdf multinet (1).pdf PM-GE.pdf
  21. Hello   i have a versamax icu200udr064 and i want to connect it with simatic basic panel ktp 1200 dp  both support modbus rut but the problem is that i cant find GE communication driver on the tia portal by whom i program the HMI.  One more thing is that i found a communication driver for modbus rtu but the tags addresses are in the standard form for modbus, so is there any solution for this?  thanks a lot .  
  22. Hi Everyone! Where are my experts? I am undertaking a project at work. The project contains analog style motor positioning circuits (operational amplifiers, integrators, and other PI elements). Not that this is relevant to the post yet ;) .It's my first PLC project ever! I am using the Schneider M258 with SoMachine 4.1 The PLC is talking to SoMachine via Ethernet (obviously I have a router between the PLC and my pc).I can Login and run the first POU I created. It's a simple And logic circuit for now. I have a co worker (c programmer) agreeing to help me pass data from my PLC to a browser screen. Although he's not familiar with PLC he's quite skilled writing code. He has wrote a Modbus protocol which allows him to interpret Modbus commands on his desktop.   1) Do I Need any special hardware to pass the data out of the PLC into the Router then into his browser. 2) As a trial can I send him MODBUS commands regarding my AND circuit? 3) How do I create such a command? 4) Is it possible for him to send me Modbus commands to change variables inside my program? 5) Are there web browser "plug-ins" for this idea? Thanks for reading and hopefully all of you can help me answer some of these questions.        
  23. Hi, I'm trying to set up a TCP communication between a Q03UDECPU and a Beijer E110 panel  I've tried both TCP and UDP as "communication mode" in E-Designer. nothing seems to work.  What I'm I doing wrong Se attached files from E-designer and Gx IEC Developer
  24. Is CP1H with Ethernet option board (CP1W-CIF41) is capable to communicate More than one client? If yes what settings I need to be Done?  
  25. Hello I downloaded a .mer file on the Panel view 1000 but it shows errors on the display graphics. i have configured the Rslinx communication several times by selecting the rigt PLC in Design and Runtime mode. I am using Facotry Talk view 8.20 and creating 5.10 runtime file. Please advice. I was able to correctly download and use the HMI on a similar machine. I dont know what am I missing on this one.    Thanks Pratik Jain