viliux112
MrPLC Member-
Content count
5 -
Joined
-
Last visited
Posts posted by viliux112
-
-
problem has been solved. I was using wrong port on plc..
-
by the way,
i am using CP1W-CIF11 communication board.
-
settings on PLC Serial port 1:
Communication settings same as temp controller. Mode: Serial gateway.
On temperature controller mode: CompoWay/F. All settings is set by FB manual. But still, no luck to read or write registers on temp controller... i am using _e5xx200_ReadVariable and _e5xx400_WriteVariable FB's..
Any suggestions what i am doing wrong?
-
Hello,
is there a way, to edit E5CC-T temperature controller internal program, using CP1L-EM PLC, connected to temperature controller via rs-485 communication? I can't find any information about doing it. I know that i cat change these programs, using CX-Thermo, but that is not an option. I need to do that, using only PLC..
CX-Thermo program
in Other Omron Software
Posted
Hello,
I am working with e5cc-t programs, for heating application. I need to find a way, to start program, when temperature reaches set-point of first (no. 0) segment. I think that, there should be some kind of setting, but i cant found it..
I've done this with PLC, but this is not an solution for this application.
in conclusion: After program starts, it has to reach set point temp, and then hold temperature for certain time.