Milosh

MrPLC Member
  • Content count

    52
  • Joined

  • Last visited

Community Reputation

0 Neutral

About Milosh

  • Rank
    Sparky

Profile Information

  • Country Yugoslavia
  1. Need Manual for CS1W-CTS21 SSI Interface

    Hi, thanks to all. No this module CS1W-CTS21 not CJ1W... Also I have instruction sheet for CS1W module, and there is section about DIP switches...
  2. Need Manual for CS1W-CTS21 SSI Interface

    Sorry look at the CS1W-CTS21 sheet... Thanks
  3. Need Manual for CS1W-CTS21 SSI Interface

    Hi all. I need info how to set encoder resoluiton with DM words. In manual m+12 word is used to set resoultion, but if I want to set 10 databits, what I need to do. Example: I thinking about MOV instruction #10 to DM20112. Also if I need 24 bit resolution MOV #24 to DM20112. Before that I should to set  DIP switches 1...4 to ON. Thanks in advance...
  4. AD081 change settings via DM parameters

    Yeah, it's easy for binary values.   But how to know the values for Input1 input range setting, It's occupied 2 bits, which values corresponds to which ranges?
  5. Hi all Is there any document which describe how we can set let's say analog input module via DM adresses.  Which values of DM adddress corresponds  to enable analog input, to set input range, to set mean value processing etc. Example: If i want to enable conversion on all inputs I shold to se #FF in DM20000. But is there any doc. which explains which address and which values we should to use for  enabling, range etc. This is also interesting for some other modules, like CTS021... Thanks, Miloš    
  6. Hi all. I have task to change old cx-supervisor project v1.x which was worked on 1280x1024 resolution monitor. Now I need to upgrade to version 3.5, with monitor resoultion 1920x1080. I see in runtime settings->screen size option rescale checked, but my screens stay the same... Is there easy way to rescale screen and objects on screen to bigger resolution?! Thanks in advance, Miloš
  7. What is the difference between these two bacplanes? Can we mount cpu to io expansion backplane?
  8. Cpu position in rack ?

    Hi all Is there any problem if CPU is put like this (from right to left) slot 1 - PA209R slot 2 - ID231 slot 3 - ID231 slot 4 - OD231 slot 5 - OD 231 slot 6 - CS1H-CPU64H   On CPU is program logic (with all configurations). CPU have different rack informations. I need to put it on rack (above) and upload program code to PC.    
  9. Is there any problem if cx supervisor installed on the same machine with cx programmer and cx desiner? Some driver problems, etc. What is your expressions?   Best regards, Miloš
  10. Upload from CS1H PLC?

    I should to connect with direct (auto) mode?
  11. Upload project from NS5-SQ10

    Is that cable same as connecting to Omron PLC CS series? Should I need to do something on the PT before transfering? Or on the Cx-Designer?
  12. Upload from CS1H PLC?

    Hi all. I want to know what is the procedure to upload project from PLC model CS1H? Does the PLC goes to stop mode if I start uploading? Best regards, Miloš  
  13. Upload project from NS5-SQ10

    Hi all, Can someone explain how to upload project from NS5 HMI? 1. Which cable to use and which software? I tried with crossover rs232 cable to port A, but can't upload project? 2. Is it better to use USB cable? 3. Do I need to change something on DIP switches on HMI device?   Best regards, Miloš
  14. Change title bar of pop-up screen

    Thanks for reply. Yes, that is one solution, but in that case I don't have posibility to move pop-up screen around the base screen.
  15. Change title bar of pop-up screen

    Close button on title bar is all grayed, and like that, is not have good visibility. I hope that I can change it to standard red button with white X.