-
Content count
347 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by gclshortt
-
http://suport.siriustrading.ro/02.DocArh/01.PLC/03.Modulare/05.MELSEC%20AnS,QnAS/01.Unitati%20centrale/01.AnS/AnS(J)HCPU%20-%20User's%20Manual%20IB(NA)-66779-N%20(01.11).pdf http://www.plctalk.net/qanda/showthread.php?t=17896 The above information may help you out. Regards, Garry
-
Another option would be to use a C200H-PRO27-E with a 3G2A5-AP003 and a 2 or 3-meter cable. https://accautomation.ca/purchase-find-parts/omron-c20k-c28k-c40k-c60k/#Peripheral This is still using the handheld but with the cable extension, it is better to work with it. Regards, Garry
-
http://www.plctalk.net/qanda/showthread.php?t=47460The above post mentions a similar application using a timer and a counter to get to minutes.Can you post the logic? Regards, Garry
-
What is the distance that you are communicating? Is it that you do not want to change the baud rate, or cannot change it? http://www.plctalk.net/qanda/showthread.php?t=53380 One other thing to do is to check the shield of your cable that you are using. It should only be connected to one end. This is usually the PLC side. Regards, Garry
-
https://accautomation.ca/omron-cp1h-counters/ The above thread may help you out. Regards, Garry
-
http://www.plctalk.net/qanda/showthread.php?t=98877 Since this is not a constant error, I would try the following: - Ensure that your communication cable separate from your power wiring. - If the problem still persists, then try lowering the communication baud rate for each device. Regards, Garry
-
http://www.barr-thorp.com/wp-content/uploads/2011/06/PacDrive-Controller-C400-C400-A8-Operating-Manual.pdf wd (watchdog indicator) Watchdog is a hardware module to monitor the controller. OFF - Normal operation ON - Fatal error; reset required, reboot system The above is from the manual above. This may help you out. Regards, Garry
-
https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf Look at section '10.3 Creating Programs for the Slave Station' of the above manual. I hope this will help you out. Regards, Garry
-
http://www.plctalk.net/qanda/showthread.php?t=3221 This thread may help you out. Regards, Garry
-
http://www.plctalk.net/qanda/showthread.php?t=62245 http://www.plctalk.net/qanda/showthread.php?t=32652 The above threads may help you out. Regards, Garry
-
https://www.myomron.com/index.php?action=kb&article=1639 The above link has the description for the Trend Graph: ' Trend Graph is linked to a data set and displays the values for analysis (coming soon) and User Alarms Viewer shows either current or historical information on alarms (see 'Introduction To NA Alarms' article). ' Regards, Garry
-
http://www.plctalk.net/qanda/showthread.php?t=113901 The above thread may help you out. Regards, Garry
-
This is not an Omron NJ series, but here is a series on the Omron CP1H. https://accautomation.ca/series/omron-plc-cp1h-series/ I hope this will help you out. Regards, Garry
-
Licensed runtime and 2 hours demo - screen refresh
gclshortt replied to Milosh's topic in CX-Supervisor
http://forums.mrplc.com/index.php?/topic/11888-cx-supervisor-hanging/ The above thread may help you out. Regards, Garry -
Hi Experts, the pulses counted in my flow meter are not the same with what it counts in my PLC.
gclshortt replied to Nyame Ephraim's topic in Allen Bradley / Rockwell Automation
With a 100msec pulse, I would just try a regular DC input for the signal and see what you get. Part numbers would help on the flow meter, PLC and high-speed counter card if applicable. Regards, Garry -
Failing Interposing Relays, and Varistors
gclshortt replied to gkingc6z06's topic in Control Panel Building
What you need to do is find out the inrush of the coils. I would contact the manufacturer or use their website to determine this value. The following information will help you to determine the inrush based on your equipment specifications. https://www.pacontrol.com/download/Solenoid%20Valves%20Engineering%20Information.pdf Once you have this rating, I would look for an interposing relay to handle the value. A Solid State could also be used. https://temcoindustrial.com/product-guides/contactors-and-overloads/solid-state-vs-electromechanical-relay Hope this helps you out. Regards, -
Novice question...IR internal relay adress in ladder diagrams
gclshortt replied to Trimjohan's topic in CX-Programmer
https://accautomation.ca/omron-cp1h-numbering-systems-and-addressing/ The above will explain the numbering systems in the Omron CP1H series. This would be similar to all of the PLC's in this CP1 Series. Here is a link to the entire CP1H Series. https://accautomation.ca/series/omron-plc-cp1h-series/ Hope this helps you out. Regards, Garry -
Using RTC To Shut off Motor
gclshortt replied to grubb's topic in Allen Bradley / Rockwell Automation
http://www.plctalk.net/qanda/showthread.php?t=70085 http://www.plctalk.net/qanda/showthread.php?t=70329 The above threads may help you out. Regards, Garry -
What is the accuracy you are looking to achieve? Depending on the PLC you can handle this a couple of ways. 1 - set the scan time and then count the number of scans. 2 - add the scan time every cycle Regards, Garry
-
https://accautomation.ca/series/horner-xl4-series/ The above is a series on the Horner XL4 PLC. It includes installing and using the CScape Software Package. This may help you out. Regards, Garry
-
Able to download to plc from one PC but not another
gclshortt replied to sanchezplc96's topic in Allen Bradley / Rockwell Automation
http://www.plctalk.net/qanda/showthread.php?t=120012 Answers posted at the above thread. Regards, Garry -
+1 gtsuport You must ensure that the processor that you are programming does not use this are for other items like DM Setup Area. Regards, Garry
-
Typically you would organize the data in the PLC and the HMI would display the data. Each time the machine starts, then capture the real-time data and store in a register. You can also do the same thing for when the machine stops. You would then need to index your register to store the next value(s). You will need to know how big of an area you are going to need in the PLC. It appears that you are only going to store events and not do any calculation on the data. Regards, Garry
-
The first thing that you will decide is exactly what you want and where? Example: Shift = 8 hours = 480 minutes = 28800 seconds Let's assume a one second unit of measure. ON Time for Shift = 20000 seconds (Register Location?) OFF Time for Shift = 8800 seconds (Register Location?) Once the basic information is stored per shift then calculation can be made for the shift. Uptime = 69.44% If you are looking just to log the events with time and date, then using the real-time clock would be beneficial. This can be done at specific intervals like every second or minute or just when the event occurs. Example Output Every Minute 03/13/19 09:30:00 - Machine ON - Parameters A, B, C - Widgets Made 03/13/19 09:31:00 - Machine ON - Parameters A, B, C - Widgets Made 03/13/19 09:32:00 - Machine ON - Parameters A, B, C - Widgets Made 03/13/19 09:33:00 - Machine ON - Parameters A, B, C - Widgets Made ETC. Example Output for Event of Machine ON 03/13/19 09:30:00 - Machine ON - Parameters A, B, C - Widgets Made 03/13/19 09:45:10 - Machine OFF - Parameters A, B, C - Widgets Made 03/13/19 09:47:33 - Machine ON - Parameters A, B, C - Widgets Made ETC. You must begin with the end in mind. This post may help you out. https://accautomation.ca/now-you-can-have-robust-data-logging-for-free-part-1/ Regards, Garry