Gambit

MrPLC Member
  • Content count

    1271
  • Joined

  • Last visited

Community Reputation

88 Excellent

3 Followers

About Gambit

  • Rank
    Propeller Head
  • Birthday 09/29/74

Profile Information

  • Gender Male
  • Location Amsterdam
  • Country Netherlands

Recent Profile Visitors

3947 profile views
  1. Ethercat, Smartwire dt, or Other

    As for field wiring i like CC-Link IE Field maybe not as popular as most but you can use star and line topology together as much as you like so you don't really need to take care. It's 1GBps uses standard CAT cables and you don't need switches.
  2. Re-Naming Program Files...

    Yep, but you only need to clear the memory if you run into memory problems. It's ok if the other file exists 
  3. Re-Naming Program Files...

    With Tree you mean thr tree in your software ? because there you will only have Station 1 But in the PLC it will contain both MAIN0 and STATION1. (It's just another file and not over written as it has a different name) As @Crossbowmentioned this does take memory in the PLC so it is better to clear the PLC (remove the old files)  before you download the new files. Juts look at it like a PC. if you copy a word document to your C drive but there is already a word document with the same name than it will overwrite that file. If it has another name then you will have two word documents.  Remember the PLC will only run the program files which are in the PLC parameters.  
  4. The problem with understanding FX5U and PID

    Can you make a screen capture with the monitored values so we can see the settings?
  5. Structured Ladder

    The structured program can't be downloaded into an FX3S only the PLC code. But you should be able to upload that and open it
  6. Re-Naming Program Files...

    It's the same like a harddrive if your file is called prog 1 on the drive and copy a new file call prog 2 then they both exist on the drive. In case of the PLC only the program(s) set in the parameters will be executed. 
  7. Re-Naming Program Files...

    You will have to rename them and write them to the PLC. These names are set in your PLC Parameters!!!. Also if you rename these files and download them to your system Q your files will not be overwritten as these have other names so they will still be on the system Q.  
  8. GT WORKS 2.96

    If you have registered your current version at the Mitsubishi site than you should be able to download the update. Otherwise contact the Mitsubishi Dealer in South Africa -  adroit http://www.adroit.co.za/
  9. Have you taken a look at chapter 24(High speed input/output functions)  of the iQ-F user manual application. It's in the e-manual viewer  
  10. GT WORKS 2.96

    Download the latest version
  11. mrj4

    Do you mean 12.1?
  12. Using Ethernet as I/O

    I think the Keyence vision system supports MC protocol. Than all you need to do is set up an ethernet port and set up the devices in the keyence
  13. GX Works2 & MX OPC Server 6.10 issue

    Sounds like you didn't configure any devices to your variables in GX Works 2
  14. GX works 3 RS2 function

    So your question is how to convert an integer value to a string? INT_TO_STRING(_E)
  15. Logical NOT not working

    A download or online change of the compiled program should be enough.  When it's a new program file you will have to download the parameter and reset the PLC as the PLC parameters have changed.