acpi

MrPLC Member
  • Content count

    161
  • Joined

  • Last visited

Community Reputation

9 Neutral

1 Follower

About acpi

  • Rank
    Sparky
  • Birthday 06/09/68

Profile Information

  • Gender Male
  • Location France
  • Country France

Recent Profile Visitors

3223 profile views
  1. Hi, You can try here : http://mei-msma.fr/crbst_43.html if it doesn't work, let me know by pm, I have others versions. JC
  2. Plc7-3

    Hi, Are you talking of a TSX 47 plc from Telemecanique programmed in PL7-3 ? If so there's no software that could be used in any Windows version. You must use PL7-3 software either under DOS or OS/2. An other alternative is to use a T407 console with the PL7-3 langage cartridge but it could be difficult to find one. JC
  3. Hi, Maybe you could make a FB with a loop. Here is an example to reset an array of bool. You just need and index and a bool as the conditon of the reset. JC
  4. Hi, 1) Forget Unity, your processor is PL7-Pro only. For Unity only processors reference that ended by a 4 (ie TSX572624) can be programmed with unity. 2) XIP driver is installed when you install PL7-Pro. XIP Driver is provided as well on the cd with PL7-Pro. To configure XIP driver have a look here : https://www.schneider-electric.fr/fr/faqs/FA17522/ Sorry it's in french, I didn't find something in english. But it's not so complicated. Anyway a quicker solution will be to find an RS485 cable to connect the TER plug, it's easier than in Ethernet with these processors. JC
  5. Error OBs

    You're right, some Schneider plcs system bits could be used to "emulate" some OB, but in this particular case it's not really interesting. With a Siemens Step7 Plc, if you address a memory area that doesn't exist, your plc will stop. If you add OB121 (that is not present by default when you create your project) it will not. It's really a totally different philosophy between Siemens and Schneider and it's not a good idea to try to do with a Schneider plc what you did with a Siemens. JC
  6. Error OBs

    Hi, OB means organization Block, it can't be compared with Schneider DFB. OB121 and OB122 are specials organization blocks that can be used to avoid to stop the processor when a programming error occurs (OB121) or I.O error (OB122). So don't look at this on Schneider Plcs, they don't exist so you don't need it :) JC  
  7. Question about chip PLC

    http://velocio.net/ace/ I never used it myself but it's cheap... JC
  8. SUCOS PS316 connection issue

    Hi, I worked with PS316 several years ago and if I remember well I had to use a software from Kithara to use the com port under Windows XP (http://kithara.com/en) This software was provided for free by Lauer. I don't remember very well how it worked but the fact is without this software I couldn't communicate with the PLC even with the protocoled original Klockner cable. Maybe you could look at it. JC
  9. Hi, I Checked on my side and you can use XBTL-900 too, it's a software designed for Windows 3.11 so it's a little bit more easy to use it than the DOS (100, 400) versions. Be aware that upload/download to the XBT are not easy cause there's only one com port and most of the time you have to change the port mode to RS232 instead of the RS485 used for the link to the PLC, this changes has to be made directly on the panel. JC
  10. Hi, If I remember well you need XBTL-900 that run under windows. Maybe you could use XBTL-400 or 100 but these ones are DOS only. The cable is a serial one, probably not a standard cable. I should have the drawing somewhere. Anyway this panel is completely osbolete and you should replace it as soon as possible. JC   PS: Here is a link to download the user guide, you'll probably find the informations you need : https://www.schneider-electric.com/en/download/document/0428830K01000/
  11. Hello, P57104 processor are Unity processors, they will be sold until 2026. If necessary the program can be easily adapted to a M340 or a M580 if the program is bigger. JC
  12. Morning, That simply means the battery inside the power supply module (behind the front cover)  is dead or close to be. If you have a memory cartridge inside the processor it's not a real problem, if not, that means that if you shut down the power your program will be lost. Take a picture of your plc with the leds state and I will give you a diag more accurate. JC
  13. Hi, It depends of the reference of your Premium, if it ends by a 3 (TSX P57 203 by example) you need the older PL7 Pro software. If it ends by a 4 (TSC P57 2634 by example) you need Unity software. Both use the same serial cable, TSXPCX1031 (RS232 version) or TSXCUSB485 + TSXCRJMD25 (usb version). Some processors have a buit in Ethernet connector or an additional Ethernet module that can be used to communicate with the plc. JC
  14. Morning, The best place for a T407 is in a museum, this tool is completely obsolete nowadays.  What you have to do is to find a virtual image of OS/2 with the XTEL workshop including basically PL7-2 software (for TSX17) and PL7-3 software for TSX 47, 67, 87 or 107. Then you need an RS232 to RS485 converter for the 17 and an RS232 to Current Loop converter for all the rest of the 7 series plcs.  As I said in another message the original converter used by Telemecanique was a Westermo MA-21. Once you have uploaded the programs you will be able either to print it or convert it to the new Schneider plcs as cHud said .   JC PS : Here is a drawing of the TSX 17 programming cable : http://www.schneider-electric.co.in/library/SCHNEIDER_ELECTRIC/SE_LOCAL/APS/5805_33AE/2.8E10.gif For all 7 series plcs except 17 using a generic converter : http://forum-automatisme.net/download/file.php?id=1263&mode=view
  15. TSX67

    Hi, You need PL7-3 software Under XTEL and an RS232 to Current loop converter. Ideally a Westermo MA-21 which was the converter used by Telemecanique. JC