MerlinKnight

MrPLC Member
  • Content count

    7
  • Joined

  • Last visited

Community Reputation

0 Neutral

About MerlinKnight

  • Rank
    Newbie

Contact Methods

  • ICQ 0
  1. I am looking for a way to record user logged in time. Wanting to see who logged in to acknowledge an alarm. Can the user logged in show up in the alarm screen.?
  2. RSLOGIX 5000 ethernet

    THANKS to all of you. I have alot of reading to do. THanks again, MerlinKnight
  3. RSLOGIX 5000 ethernet

    No i did not try the MSG. I'll try that and the consume/produce. If anyone has any examples it would be great. Thank You. Merlin Knight
  4. I have 2 rslogix 5000 that have a 1756-enet cards in their racks. They go to a switching hub. I want to pull data from 1 plc into another using the ethernet. Any directions on doing this would greatly be appreciated. Probably real easy, just can't think of it.
  5. Quantum CPU113-3

    Thank you Crossbow, I was not sure if i could do that or if it would take it. The help area for the plc program had shown the info above and that it. I did not understand why the bits were needed or how they worked. I'll try it. Thanks Again, Merlin Knight
  6. Hello, I am new to quantum but i have found this: Clock Register Values 4xxxx: Contains the following control information from the left: Bit 1: Set Clock Values Bit 2: Read Clock Values Bit 3: Done Bit 4: Error 4xxxx+1: Contains the day of the week (from 1 to 7). 4xxxx+2: Contains the month 4xxxx+3: Contains the day 4xxxx+4: Contains the year 4xxxx+5: Contains the hour (using the 24-hour clock). 4xxxx+6: Contains the minutes. 4xxxx+7: Contains seconds. But how does this work. Do i set bit 2 then read the modbus register. Do i set then reset bit 2 then read register. To set the clock do i put a # in the reg then set bit 1 then reset the bit the set bit 3 then reset. Don't know and can't find. Processor is running and i can't test . Thanks, Merlin Knight
  7. Modbus fault cp341

    HELP!!!, I am using a 315-2dp siemens processor. I have 2 of them and i have to communicated between them through a lease line. We are using 2 cp341's with modbus master and modbus slave drivers installed. I can transmit to the slave all day sending data without a fault code or error. When i try to read data from the slave i get OE32 fault after awhile of running. Merlin :