CP1L and CP1H EasyModbus FB

Sign in to follow this  
Followers 0

1 Screenshot

About This File

Ideally suited to multiple Omron inverters connected on Modbus RTU network and where the Omron FB is too memory hungry.<br />Reads <u>upto</u> 16 registers from register 20 and writes to two registers (Fixed at 1 and 2). <br /><br />Set the serial port to Serial Gateway and set the baud rate to match the inverters. Inverter default is 81N. In the V1000 set H5-01 to the address. It must start at 1 and have no gaps.<br />The baudrate works upto 115200 (with V1000)<br /><br />Data format suits V1000 F7 E7. Don't use for V7 or J7.<br /><br />Data is only written on a change. The change is managed in the PLC NOT in the inverter. Data is read sequentially from node 1 to 'MaxNodes'.<br /><br />Not tested on CP1L-L (one serial port version). I think its Easy modbus addresses are different to two port versions.<br /><br />You can choose addresses within CIO only.<br /><br />Refer to any inverter manual for modbus addresses.

Edit: the CP1L 14/20 use port two EasyModbus addresses. I think you can select Port 2 but set port 1 to Serial Gateway. Can someone try this??


1 person likes this